[Equest-users] Hourly space temperatura after cooling

Brian Fountain bfountain at greensim.com
Fri Mar 22 09:55:49 PDT 2019


SS-R will tell you what zone is throwing unmet hours.

SS-F will show you which month the unmet hours are occuring in for that/ 
those zone(s) and the corresponding max and min temperatures.

SS-O shows you the time of day when it occurs.

In SS-O, this is the space temperature after heating and cooling is 
applied for hours when the fan schedule is on.

 From there, you may wish to create an hourly report on the zone 
temperatures or unit supply temperatures and airflows.

Other items to check:
- fan, heating and cooling schedule
- night ventilation control -- cycle on any?  - stay off (in which night 
setback temperatures may not be met)
- throttling range
- thermostat action (reverse action?  proportional?)

155 hours is not very many to worry about.

Brian



On 22/03/2019 9:51 a.m., Integral Mechanical Engineering Designs via 
Equest-users wrote:
>
> Hi all,
>
> If I open the BEPS Building Energy Performance, there are 155 unmet 
> hours. I would like to get the temperature values throughout the year 
> after cooling, but the only related option that I can see is the SS-O 
> Space Temperature Summary where the temperatures above the set point 
> are much more than the unmet hours. It seems that is the report of the 
> space before cooling.
>
> How could I get the space temperature after cooling to have relation 
> with the unmet hours?
>
>
> Kind Regards,
>
> Paul Caicedo
>
> Mechanical Engineering Consultant
>
> __
>
> *IntegralMECH*
>
>
> <http://www.avg.com/email-signature?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient> 
> 	Virus-free. www.avg.com 
> <http://www.avg.com/email-signature?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient> 
>
>
> <#DAB4FAD8-2DD7-40BB-A1B8-4E2AA1F9FDF2>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190322/07fc602e/attachment-0001.htm>


More information about the Equest-users mailing list