[Equest-users] Increassed cooling consumption with DCV Modeling

Harshal Gupta harshal8899 at gmail.com
Thu Jan 10 22:50:31 PST 2019


Hello Energy Modelers,

This is regarding to increased cooling consumption while modelling DCV in eQUEST.I have prepared a hourly analysis on a single zone modeled without and with DCV, hourly result is attached.

Modeling Inputs

  1.  Project Location : Bangalore India (moderate climate).
  2.  Occupancy profile : 90% in office hours and 50% in lunch hours
  3.  Minimum air schedule is modeled in air side and minimum control is set to DCV reset down.

The outcomes are summarize below:

                                                         =Without DCV-With DCV  Remarks
                Difference in supply air flow (btu)     2,98,886        Reduced
Difference in latent (btu)      0       No change
Difference in total tonnage (TR)        -1,764  Increased
Difference in fresh air (CFM)   8,51,210        Reduced
Difference in vent fan consumption (kW) 32      Reduced

Queries :

  1.  Supply flow air and vent fan consumption is reduced, why their is an increment total cooling consumption.
  2.  Why their is no change in Total SPACE latent heat load from LOADS (Btu/hr).
  3.  What should be the correct way to model this and get efficiency.



Warm Regards
Harshal Gupta
Energy Analyst
LEED AP<https://www.usgbc.org/organizations/environmental-design-solutions-eds?view=employees> || IGBC AP<https://igbc.in/igbc/redirectHtml.htm?redVal=showIgbcApnosign> <http://www.grihaindia.org/index.php?option=com_fabrik&view=list&listid=31&t=griha_community&Itemid=0&resetfilters=0> || GRIHA CP<http://www.grihaindia.org/index.php?option=com_fabrik&view=list&listid=31&t=griha_community&Itemid=0&resetfilters=0>
 [cid:96544101-c417-4e46-b22e-12b0ce86db48]        [1504090917380_igbc-logo-big.jpg]     [1504090994828_GROHA]

<http://www.grihaindia.org/index.php?option=com_fabrik&view=list&listid=31&t=griha_community&Itemid=0&resetfilters=0>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190111/caee3870/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Outlook-hh1tsvib.png
Type: image/png
Size: 2018 bytes
Desc: Outlook-hh1tsvib.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190111/caee3870/attachment-0006.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Outlook-1504090917.jpg
Type: image/jpeg
Size: 2502 bytes
Desc: Outlook-1504090917.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190111/caee3870/attachment-0003.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Outlook-1504090994.png
Type: image/png
Size: 2971 bytes
Desc: Outlook-1504090994.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190111/caee3870/attachment-0007.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: 20190102_R115 DCV Analysis_R1.xlsx
Type: application/vnd.openxmlformats-officedocument.spreadsheetml.sheet
Size: 1715905 bytes
Desc: 20190102_R115 DCV Analysis_R1.xlsx
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190111/caee3870/attachment-0003.xlsx>


More information about the Equest-users mailing list