[Equest-users] Modeling Ashrae - System 8 in equest - Fan in the parallel box
Sharad Kumar
sharadcapricious at gmail.com
Fri Aug 2 03:43:33 PDT 2019
Hi Konstantina,
As per me you are correct in finding the Fan power for system type-8 which
comes as 0.35 W/ cfm. as per G 3.1.3.14.
The thing that you are required to have is the same kind of input in the
Airside system fan power parameters.
As an example following snapshot has been provided.
[image: image.png]
Hope this might help.
*Thanks and Regards*,
Sharad.Kumar
Freelancer
India
*From:* Equest-users <equest-users-bounces at lists.onebuilding.org> *On
Behalf Of *Konstantina Kalliakoudi via Equest-users
*Sent:* Tuesday, July 30, 2019 8:44 AM
*To:* equest-users at lists.onebuilding.org
*Subject:* [Equest-users] Modeling Ashrae - System 8 in equest - Fan in the
parallel box
CAUTION: EXTERNAL SENDER
Dear equest users,
According G3.1.3.14 for system 8 the fan parallel box shall be modeled with
0.35 W/cfm fan power.
I was wondering where this paramater can be insered in equest.
In the following screenshot I have input the power of the supply fan.
[image: image.png]
Thank you very much.
Best regards
Konstantina Kalliakoudi
Mechanical Engineer Μ.Sc.
www.khmoe.gr
<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.khmoe.gr%2F&data=02%7C01%7CNicholas.Caton%40se.com%7C80eeb87eb1024add726908d714f07a79%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C637000895394432188&sdata=Vw2BEgGFn1p5%2BhXju0ZynmRaHRPGpkcxSNFWkA2CJAc%3D&reserved=0>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190802/f862e867/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.png
Type: image/png
Size: 79003 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190802/f862e867/attachment.png>
More information about the Equest-users
mailing list