[Equest-users] Shading of windows
Nicholas Caton
Nicholas.Caton at schneider-electric.com
Tue Sep 25 12:56:39 PDT 2018
This sounds a little like a “how should I..” question that may be best answered with a “should you?”
If I wanted this to be pretty, I would do something that based on your screenshot would be pretty complicated & time-intensive using building shades. It would involve a good long while in the text editor, copying/pasting my efforts and carefully renaming what looks like tens to hundreds of components to hopefully realize my artistic vision…
But the engineer in me has 2 alternative suggestions which won’t achieve the aesthetic ideal but could get you to the finish line quicker:
1. Build on the efforts of those who came before us, and distill your repeating sidefins into a shading coefficient: https://aceee.org/files/proceedings/1992/data/papers/SS92_Panel1_Paper20.pdf
* Note that considering the screenshot you shared, your building façade orientations don’t appear to align neatly with cardinal directions. You’ll need to interpolate the provided coefficients for orientations other than N, S, E, W.
* This will result in a set of glass properties unique to each orientation in your model.
2. Do something like the following exercise, then revise the geometries & ideally step back to and utilize the DD wizards to time-efficiently tailor to your actual situation:
* Adjust a window to be 2 ft wide x 5 ft tall
* Give it a single left sidefin with a depth of 1.0 ft
* Give the sidefin a horizontal dimension of -1.0 ft. This should put the sidefin squarely along the centerline of the glazing. The window and sidefin should now look like a capital “T” in plan view.
* Give the window a multiplier of 10.
* Zero out the windows’ framing depth, and define/adjust glass properties to reflect the net properties of the framing/glass situation.
* Now we have modeled a 20ft x 5ft window band with vertical fins spaced 2ft on-center. It just doesn’t look quite so impactful.
Hope these thoughts may be helpful to you or others!
~Nick
[cid:image001.png at 01D454DD.77AC1960]
Nick Caton, P.E., BEMP
Senior Energy Engineer
Regional Energy Engineering Manager
Energy and Sustainability Services
Schneider Electric
D 913.564.6361
M 785.410.3317
F 913.564.6380
E nicholas.caton at schneider-electric.com<mailto:nicholas.caton at schneider-electric.com>
15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States
[cid:image003.png at 01D454DD.77AC1960]
From: Equest-users <equest-users-bounces at lists.onebuilding.org> On Behalf Of Jones, Christopher via Equest-users
Sent: Tuesday, September 25, 2018 2:10 PM
To: Akshat Kabra <akshatspin at gmail.com>
Cc: equest-users at onebuilding.org
Subject: Re: [Equest-users] Shading of windows
[External email: Use caution with links and attachments]
________________________________
You can model fins at the end of each window or offset one way or the other from the end of windows. If you have multiple fins across a window, you have to use Building Shades or Fixed Shades. I am never sure the difference between Building and Fixed Shades.
The DOE2.2 manuals are very handy:
http://doe2.com/download/doe-22/<https://emea01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fdoe2.com%2Fdownload%2Fdoe-22%2F&data=02%7C01%7Cnicholas.caton%40schneider-electric.com%7C8aea183ff69e470177a808d6231a9d7d%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C636734994554164633&sdata=ChFrZvWTkoR8uvYolUjkUNGtyQ77WyZQZABkV9itoS8%3D&reserved=0>
Christopher R Jones, P.Eng.
T+ 1 416-644-0252
[cid:image004.png at 01D454DD.77AC1960]
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Akshat Kabra via Equest-users
Sent: Tuesday, September 25, 2018 1:53 PM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] Shading of windows
Hi,
I have modelled the building in design development wizard.
Is it possible to have series of fins over the window area with equal space without changing geometry.(Since I have customised the glazing unit).
I have attach the image for the reference.
________________________________
NOTICE: This communication and any attachments ("this message") may contain information which is privileged, confidential, proprietary or otherwise subject to restricted disclosure under applicable law. This message is for the sole use of the intended recipient(s). Any unauthorized use, disclosure, viewing, copying, alteration, dissemination or distribution of, or reliance on, this message is strictly prohibited. If you have received this message in error, or you are not an authorized or intended recipient, please notify the sender immediately by replying to this message, delete this message and all copies from your e-mail system and destroy any printed copies. You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSP's electronic communications policy, please consult our Anti-Spam Commitment at www.wsp.com/casl<https://emea01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.wsp.com%2Fcasl&data=02%7C01%7Cnicholas.caton%40schneider-electric.com%7C8aea183ff69e470177a808d6231a9d7d%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C636734994554174646&sdata=vdHcQPuQxcLS9lfZ8Pfojtdn8h%2FPHo0q6hMM15FmQsE%3D&reserved=0>. For any concern or if you believe you should not be receiving this message, please forward this message to caslcompliance at wsp.com<mailto:caslcompliance at wsp.com> so that we can promptly address your request. Note that not all messages sent by WSP qualify as commercial electronic messages.
AVIS : Ce message, incluant tout fichier l'accompagnant (« le message »), peut contenir des renseignements ou de l'information privilégiés, confidentiels, propriétaires ou à divulgation restreinte en vertu de la loi. Ce message est destiné à l'usage exclusif du/des destinataire(s) voulu(s). Toute utilisation non permise, divulgation, lecture, reproduction, modification, diffusion ou distribution est interdite. Si vous avez reçu ce message par erreur, ou que vous n'êtes pas un destinataire autorisé ou voulu, veuillez en aviser l'expéditeur immédiatement et détruire le message et toute copie électronique ou imprimée. Vous recevez cette communication car vous faites partie des contacts de WSP. Si vous avez des questions concernant la politique de communications électroniques de WSP, veuillez consulter notre Engagement anti-pourriel au www.wsp.com/lcap<https://emea01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.wsp.com%2Flcap&data=02%7C01%7Cnicholas.caton%40schneider-electric.com%7C8aea183ff69e470177a808d6231a9d7d%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C636734994554184650&sdata=7cquLA3trsCN%2F8GhZwKEaUqQuP1KSipp9Gkr1KkvJlg%3D&reserved=0>. Pour toute question ou si vous croyez que vous ne devriez pas recevoir ce message, prière de le transférer au conformitelcap at wsp.com<mailto:conformitelcap at wsp.com> afin que nous puissions rapidement traiter votre demande. Notez que ce ne sont pas tous les messages transmis par WSP qui constituent des messages electroniques commerciaux.
-LAEmHhHzdJzBlTWfa4Hgs7pbKl
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180925/b404e3c7/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 255 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180925/b404e3c7/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 8477 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180925/b404e3c7/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 1860 bytes
Desc: image004.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180925/b404e3c7/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: oledata.mso
Type: application/octet-stream
Size: 7135 bytes
Desc: oledata.mso
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180925/b404e3c7/attachment.obj>
More information about the Equest-users
mailing list