[Equest-users] Shading of windows
Joe Huang
yjhuang at whiteboxtechnologies.com
Tue Sep 25 12:53:59 PDT 2018
Ah, a question that I can easily answer!
A building-shade is tied geometrically to a building, while a fixed
shade is not, i.e., it's tied geometrically to the global coordinate
system. As an example, one should model the shading cast by neighboring
structures as fixed shades, and model the shading of building elements
like overhangs and fins as building shades. This distinction is handy
when one wants to rotate a building model on a given site.
Joe
Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 108D
Moraga CA 94556
yjhuang at whiteboxtechnologies.com
www.whiteboxtechnologies.com
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
On 9/25/2018 2:10 PM, Jones, Christopher via Equest-users wrote:
>
> You can model fins at the end of each window or offset one way or the
> other from the end of windows. If you have multiple fins across a
> window, you have to use Building Shades or Fixed Shades. I am never
> sure the difference between Building and Fixed Shades.
>
> The DOE2.2 manuals are very handy:
>
> http://doe2.com/download/doe-22/
>
> *Christopher R Jones, P.Eng.*
>
> T+ 1 416-644-0252
>
> *From:* Equest-users
> [mailto:equest-users-bounces at lists.onebuilding.org] *On Behalf Of
> *Akshat Kabra via Equest-users
> *Sent:* Tuesday, September 25, 2018 1:53 PM
> *To:* equest-users at lists.onebuilding.org
> *Subject:* [Equest-users] Shading of windows
>
> Hi,
>
> I have modelled the building in design development wizard.
>
> Is it possible to have series of fins over the window area with equal
> space without changing geometry.(Since I have customised the glazing
> unit).
>
> I have attach the image for the reference.
>
>
> ------------------------------------------------------------------------
>
>
> NOTICE: This communication and any attachments ("this message") may
> contain information which is privileged, confidential, proprietary or
> otherwise subject to restricted disclosure under applicable law. This
> message is for the sole use of the intended recipient(s). Any
> unauthorized use, disclosure, viewing, copying, alteration,
> dissemination or distribution of, or reliance on, this message is
> strictly prohibited. If you have received this message in error, or
> you are not an authorized or intended recipient, please notify the
> sender immediately by replying to this message, delete this message
> and all copies from your e-mail system and destroy any printed copies.
> You are receiving this communication because you are listed as a
> current WSP contact. Should you have any questions regarding WSP's
> electronic communications policy, please consult our Anti-Spam
> Commitment at www.wsp.com/casl <http://www.wsp.com/casl>. For any
> concern or if you believe you should not be receiving this message,
> please forward this message to caslcompliance at wsp.com
> <mailto:caslcompliance at wsp.com> so that we can promptly address your
> request. Note that not all messages sent by WSP qualify as commercial
> electronic messages.
>
> AVIS : Ce message, incluant tout fichier l'accompagnant (« le message
> »), peut contenir des renseignements ou de l'information privilégiés,
> confidentiels, propriétaires ou à divulgation restreinte en vertu de
> la loi. Ce message est destiné à l'usage exclusif du/des
> destinataire(s) voulu(s). Toute utilisation non permise, divulgation,
> lecture, reproduction, modification, diffusion ou distribution est
> interdite. Si vous avez reçu ce message par erreur, ou que vous n'êtes
> pas un destinataire autorisé ou voulu, veuillez en aviser l'expéditeur
> immédiatement et détruire le message et toute copie électronique ou
> imprimée. Vous recevez cette communication car vous faites partie des
> contacts de WSP. Si vous avez des questions concernant la politique de
> communications électroniques de WSP, veuillez consulter notre
> Engagement anti-pourriel au www.wsp.com/lcap
> <http://www.wsp.com/lcap>. Pour toute question ou si vous croyez que
> vous ne devriez pas recevoir ce message, prière de le transférer au
> conformitelcap at wsp.com <mailto:conformitelcap at wsp.com> afin que nous
> puissions rapidement traiter votre demande. Notez que ce ne sont pas
> tous les messages transmis par WSP qui constituent des messages
> electroniques commerciaux.
>
>
>
> -LAEmHhHzdJzBlTWfa4Hgs7pbKl
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180925/473342de/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 1860 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180925/473342de/attachment.png>
More information about the Equest-users
mailing list