[Equest-users] Heating is not on for System Type Pkgd Va
Jing Hong
hongjing.shirley at gmail.com
Tue Nov 13 14:20:59 PST 2018
Thank you Daric and John!!!!!
Choosing Package VAV is the trigger for the error. I changed it to PVVVT
and it worked! With minimal unmet hours. You guys saved my life. LOL. I
have tried everything I googled out these days.
Thank you!!!
Jing
On Tue, Nov 13, 2018 at 4:06 PM Daric Adair <
Daric.Adair at hendersonengineers.com> wrote:
> Jing;
>
>
>
> John Aulbach is right on.
>
> This may be an issue of modeling vs reality then. With a ‘Packaged VAV’
> eQuest believes that there are VAV boxes downstream, so it will put out
> cold air to provide cooling and depend on the VAV Boxes to reheat and
> prevent over-cooling.
>
>
>
> You may want to try a PVVVT system since that requires specifying a
> control zone, and that will allow the System to provide hot/cold air based
> on the control zone. The other 2 zones will be slaved along to them,
> providing either heating or cooling – whatever the control zone dictates it
> needs. But it doesn’t require VAV boxes (as your system doesn’t have them)
>
>
>
> The Thermostat Control should not enable/disable/prevent heat. A Single
> Max VAV system uses ‘Proportional’ and a Dual Max VAV System needs ‘Reverse
> Acting’. Proportional just allows eQuest to provide CFM up to the max
> durring cooling and turn down to the minimim ratio as coolng load ecrease
> and then jump to the minimum heating ratio (if a dual min box. If single
> min box, then the min ratio and min-heatig-ratio will be the same). Reverse
> acting just means that as the heating load increases, the box can allow
> more airflow up to the Heating Maximum Airflow (making it a dual max box.)
>
>
>
> The main issue may be the incorrect system type in eQuest vs the actual
> system type that is attempting to be modeled.
>
>
>
>
>
>
>
> Thanks,
>
> *DARIC R ADAIR* PE, CEM, BEMP
> Mechanical Engineer, Energy Analyst
>
> *Henderson Engineers*
>
> daric.adair at hendersonengineers.com
>
> *Licensed in* KS
>
>
>
> *From:* John Aulbach <jra_sac at yahoo.com>
> *Sent:* Tuesday, November 13, 2018 4:01 PM
> *To:* Jing Hong <hongjing.shirley at gmail.com>; Jing Hong via Equest-users <
> equest-users at lists.onebuilding.org>; mbusman04 at gmail.com
> *Cc:* equest-users at lists.onebuilding.org; Daric Adair <
> daric.Adair at hendersonengineers.com>; equest-users at onebuilding.org
> *Subject:* Re: [Equest-users] Heating is not on for System Type Pkgd Va
>
>
>
> reheat You need a reheat coil for VAV !!!
>
> Sent from Yahoo Mail on Android
> <https://go.onelink.me/107872968?pid=InProduct&c=Global_Internal_YGrowth_AndroidEmailSig__AndroidUsers&af_wl=ym&af_sub1=Internal&af_sub2=Global_YGrowth&af_sub3=EmailSignature>
>
>
>
> On Tue, Nov 13, 2018 at 1:59 PM, Jing Hong via Equest-users
>
> <equest-users at lists.onebuilding.org> wrote:
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
> ------------------------------
>
> This email and any files transmitted with it are confidential and are
> intended solely for the use of the individual or entity to whom they are
> addressed. This communication represents the originator's personal views
> and opinions, which do not necessarily reflect those of Henderson
> Engineers, Inc. If you are not the original recipient or the person
> responsible for delivering the email to the intended recipient, be advised
> that you have received this email in error, and that any use,
> dissemination, forwarding, printing, or copying of this email is strictly
> prohibited. If you received this email in error, please immediately notify
> administrator at hendersonengineers.com.
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20181113/5c1a7fcd/attachment-0001.html>
More information about the Equest-users
mailing list