<div dir="ltr">Thank you Daric and John!!!!!<div>Choosing Package VAV is the trigger for the error. I changed it to PVVVT and it worked! With minimal unmet hours. You guys saved my life. LOL. I have tried everything I googled out these days. </div><div><br></div><div>Thank you!!!</div><div><br></div><div>Jing</div></div><br><div class="gmail_quote"><div dir="ltr">On Tue, Nov 13, 2018 at 4:06 PM Daric Adair <<a href="mailto:Daric.Adair@hendersonengineers.com">Daric.Adair@hendersonengineers.com</a>> wrote:<br></div><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
<div lang="EN-US" link="blue" vlink="purple">
<div class="m_5260614291614191496WordSection1">
<p class="MsoNormal">Jing;<u></u><u></u></p>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal">John Aulbach is right on.<u></u><u></u></p>
<p class="MsoNormal">This may be an issue of modeling vs reality then. With a ‘Packaged VAV’ eQuest believes that there are VAV boxes downstream, so it will put out cold air to provide cooling and depend on the VAV Boxes to reheat and prevent over-cooling.
<u></u><u></u></p>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal">You may want to try a PVVVT system since that requires specifying a control zone, and that will allow the System to provide hot/cold air based on the control zone. The other 2 zones will be slaved along to them, providing either heating
or cooling – whatever the control zone dictates it needs. But it doesn’t require VAV boxes (as your system doesn’t have them)<u></u><u></u></p>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal"><span style="color:#44546a">The Thermostat Control should not enable/disable/prevent heat. A Single Max VAV system uses ‘Proportional’ and a Dual Max VAV System needs ‘Reverse Acting’. Proportional just allows eQuest to provide CFM up to
the max durring cooling and turn down to the minimim ratio as coolng load ecrease and then jump to the minimum heating ratio (if a dual min box. If single min box, then the min ratio and min-heatig-ratio will be the same). Reverse acting just means that as
the heating load increases, the box can allow more airflow up to the Heating Maximum Airflow (making it a dual max box.)<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#44546a"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="color:#44546a">The main issue may be the incorrect system type in eQuest vs the actual system type that is attempting to be modeled.<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#44546a"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="color:#44546a"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="color:#44546a"><u></u> <u></u></span></p>
<p class="MsoNormal">Thanks,<u></u><u></u></p>
<p class="MsoNormal" style="background:white"><b><span style="font-family:"Arial",sans-serif;color:#383a35;text-transform:uppercase">DARIC R ADAIR</span></b><span style="font-size:7.0pt;font-family:"Arial",sans-serif;color:#383a35;text-transform:uppercase">
PE, CEM, BEMP </span><span style="font-size:9.0pt;font-family:"Arial",sans-serif;color:#383a35"><br>
Mechanical Engineer, Energy Analyst <br>
<br>
</span><b><span style="font-size:9.0pt;font-family:"Arial",sans-serif;color:#008c15;text-transform:uppercase">Henderson Engineers</span></b><span style="font-size:9.0pt;font-family:"Arial",sans-serif;color:#383a35"><br>
<br>
<a href="mailto:daric.adair@hendersonengineers.com" target="_blank"><span style="color:#383a35">daric.adair@hendersonengineers.com</span></a><br>
<br>
</span><b><span style="font-size:7.0pt;font-family:"Arial",sans-serif;color:#383a35;text-transform:uppercase">Licensed in</span></b><span style="font-size:7.0pt;font-family:"Arial",sans-serif;color:#383a35;text-transform:uppercase"> KS</span><span style="font-size:9.0pt;font-family:"Arial",sans-serif;color:#383a35"><u></u><u></u></span></p>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal"><b>From:</b> John Aulbach <<a href="mailto:jra_sac@yahoo.com" target="_blank">jra_sac@yahoo.com</a>> <br>
<b>Sent:</b> Tuesday, November 13, 2018 4:01 PM<br>
<b>To:</b> Jing Hong <<a href="mailto:hongjing.shirley@gmail.com" target="_blank">hongjing.shirley@gmail.com</a>>; Jing Hong via Equest-users <<a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a>>; <a href="mailto:mbusman04@gmail.com" target="_blank">mbusman04@gmail.com</a><br>
<b>Cc:</b> <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a>; Daric Adair <<a href="mailto:daric.Adair@hendersonengineers.com" target="_blank">daric.Adair@hendersonengineers.com</a>>; <a href="mailto:equest-users@onebuilding.org" target="_blank">equest-users@onebuilding.org</a><br>
<b>Subject:</b> Re: [Equest-users] Heating is not on for System Type Pkgd Va<u></u><u></u></p>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal" style="margin-bottom:12.0pt">reheat You need a reheat coil for VAV !!!<u></u><u></u></p>
<div id="m_5260614291614191496ymail_android_signature">
<p class="MsoNormal"><a href="https://go.onelink.me/107872968?pid=InProduct&c=Global_Internal_YGrowth_AndroidEmailSig__AndroidUsers&af_wl=ym&af_sub1=Internal&af_sub2=Global_YGrowth&af_sub3=EmailSignature" target="_blank">Sent from Yahoo Mail on Android</a><u></u><u></u></p>
</div>
<p class="MsoNormal"><u></u> <u></u></p>
<blockquote style="margin-left:0in;margin-right:0in;margin-bottom:15.0pt">
<div>
<div>
<p class="MsoNormal"><span style="font-family:Roboto;color:#6d00f6">On Tue, Nov 13, 2018 at 1:59 PM, Jing Hong via Equest-users<u></u><u></u></span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-family:Roboto;color:#6d00f6"><<a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a>> wrote:<u></u><u></u></span></p>
</div>
</div>
<div style="border:none;border-left:solid #6d00f6 1.0pt;padding:0in 0in 0in 15.0pt;margin-top:7.5pt">
<p class="MsoNormal">_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">
EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><u></u><u></u></p>
</div>
</blockquote>
</div>
<br>
<hr>
<font face="Arial" color="Gray" size="1"><br>
This email and any files transmitted with it are confidential and are intended solely for the use of the individual or entity to whom they are addressed. This communication represents the originator's personal views and opinions, which do not necessarily reflect
those of Henderson Engineers, Inc. If you are not the original recipient or the person responsible for delivering the email to the intended recipient, be advised that you have received this email in error, and that any use, dissemination, forwarding, printing,
or copying of this email is strictly prohibited. If you received this email in error, please immediately notify <a href="mailto:administrator@hendersonengineers.com" target="_blank">administrator@hendersonengineers.com</a>.<br>
</font>
</div>
</blockquote></div>