Jing Hong
hongjing.shirley at gmail.com
Tue Nov 13 13:49:39 PST 2018
Hi Daric,
Thanks for your quick response. I updated the heating tab with
your suggested temperature setting, but still has no space heat provided
and the same unmet heat hours. This system does not include any reheat coil
nor zone level VAV box. Only rooftop units with VFD. The cooling parts have
no unmet cool hours, but the heating parts are very odd.
Jing
On Tue, Nov 13, 2018 at 3:32 PM Daric Adair <
Daric.Adair at hendersonengineers.com> wrote:
> Jing;
>
>
>
> First thing that jumps out at me is that there is no Heating Discharge Air
> Tempertaures or Reheat Temperatures set on the System>Heating Tab (last
> image you shared). For a VAV System I’d expect these values to be something
> like: Zone Max Temp: 90F Hot Deck Max Leaving Temperature 60F and Reheat
> Delta T: 35F.
>
>
>
>
>
> Thanks,
>
> *DARIC R ADAIR* PE, CEM, BEMP
> Mechanical Engineer, Energy Analyst
>
> *Henderson Engineers*
> daric.adair at hendersonengineers.com
>
> *Licensed in* KS
>
>
>
> *From:* Jing Hong <hongjing.shirley at gmail.com>
> *Sent:* Tuesday, November 13, 2018 3:16 PM
> *To:* equest-users at lists.onebuilding.org; equest-users at onebuilding.org
> *Subject:* [Equest-users] Heating is not on for System Type Pkgd Var Vol,
> and 4380 under heated hours
>
>
>
> Dear All,
>
>
>
> My model is located in Mexico and three zones are equipped with VFD. So I
> selected Pkgd Var Vol + Heat pump for these three zones and set the system
> up by the design cooling and heating capabilities. Currently, the SS-R
> shows 4380 under heated hours for each of the zones. And no space heat is
> provided for any of the zones. Does anyone know the possible reasons for
> this phenomenon?
>
> I've done several solutions by searching:
>
> - Increased Throttling Range
>
> - Night Cycle Control --> Set to "Cycle on Any"
>
> - Fan Control and Placement - Set to" Hourly Report Schedule"
>
>
>
> [image: image.png]
>
> [image: image.png]
>
> [image: image.png]
>
> [image: image.png]
>
> [image: image.png]
>
> Thank you!
>
>
>
> Jing
>
>
>
> ------------------------------
>
> This email and any files transmitted with it are confidential and are
> intended solely for the use of the individual or entity to whom they are
> addressed. This communication represents the originator's personal views
> and opinions, which do not necessarily reflect those of Henderson
> Engineers, Inc. If you are not the original recipient or the person
> responsible for delivering the email to the intended recipient, be advised
> that you have received this email in error, and that any use,
> dissemination, forwarding, printing, or copying of this email is strictly
> prohibited. If you received this email in error, please immediately notify
> administrator at hendersonengineers.com.
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20181113/d99c7404/attachment-0001.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 62889 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20181113/d99c7404/attachment-0006.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 50882 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20181113/d99c7404/attachment-0007.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 43429 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20181113/d99c7404/attachment-0008.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 58706 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20181113/d99c7404/attachment-0009.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.png
Type: image/png
Size: 63529 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20181113/d99c7404/attachment-0010.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 43429 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20181113/d99c7404/attachment-0011.png>
More information about the Equest-users
mailing list