<div dir="ltr">Hi Daric,<div><br></div><div>Thanks for your quick response. I updated the heating tab with your suggested temperature setting, but still has no space heat provided and the same unmet heat hours. This system does not include any reheat coil nor zone level VAV box. Only rooftop units with VFD. The cooling parts have no unmet cool hours, but the heating parts are very odd. </div><div><br></div><div>Jing</div></div><br><div class="gmail_quote"><div dir="ltr">On Tue, Nov 13, 2018 at 3:32 PM Daric Adair <<a href="mailto:Daric.Adair@hendersonengineers.com">Daric.Adair@hendersonengineers.com</a>> wrote:<br></div><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
<div lang="EN-US" link="#0563C1" vlink="#954F72">
<div class="m_-6703254255761223734WordSection1">
<p class="MsoNormal">Jing;<u></u><u></u></p>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal"><span style="color:#44546a">First thing that jumps out at me is that there is no Heating Discharge Air Tempertaures or Reheat Temperatures set on the System>Heating Tab (last image you shared). For a VAV System I’d expect these values to
be something like: Zone Max Temp: 90F Hot Deck Max Leaving Temperature 60F and Reheat Delta T: 35F.
<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#44546a"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="color:#44546a"><u></u> <u></u></span></p>
<p class="MsoNormal">Thanks,<u></u><u></u></p>
<p class="MsoNormal" style="background:white"><b><span style="font-family:"Arial",sans-serif;color:#383a35;text-transform:uppercase">DARIC R ADAIR</span></b><span style="font-size:7.0pt;font-family:"Arial",sans-serif;color:#383a35;text-transform:uppercase">
PE, CEM, BEMP </span><span style="font-size:9.0pt;font-family:"Arial",sans-serif;color:#383a35"><br>
Mechanical Engineer, Energy Analyst <br>
<br>
</span><b><span style="font-size:9.0pt;font-family:"Arial",sans-serif;color:#008c15;text-transform:uppercase">Henderson Engineers</span></b><span style="font-size:9.0pt;font-family:"Arial",sans-serif;color:#383a35"><br>
<a href="mailto:daric.adair@hendersonengineers.com" target="_blank"><span style="color:#383a35">daric.adair@hendersonengineers.com</span></a><br>
<br>
</span><b><span style="font-size:7.0pt;font-family:"Arial",sans-serif;color:#383a35;text-transform:uppercase">Licensed in</span></b><span style="font-size:7.0pt;font-family:"Arial",sans-serif;color:#383a35;text-transform:uppercase"> KS</span><span style="font-size:9.0pt;font-family:"Arial",sans-serif;color:#383a35"><u></u><u></u></span></p>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal"><b>From:</b> Jing Hong <<a href="mailto:hongjing.shirley@gmail.com" target="_blank">hongjing.shirley@gmail.com</a>> <br>
<b>Sent:</b> Tuesday, November 13, 2018 3:16 PM<br>
<b>To:</b> <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a>; <a href="mailto:equest-users@onebuilding.org" target="_blank">equest-users@onebuilding.org</a><br>
<b>Subject:</b> [Equest-users] Heating is not on for System Type Pkgd Var Vol, and 4380 under heated hours<u></u><u></u></p>
<p class="MsoNormal"><u></u> <u></u></p>
<div>
<p class="MsoNormal">Dear All,<u></u><u></u></p>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
<div>
<p class="MsoNormal">My model is located in Mexico and three zones are equipped with VFD. So I selected Pkgd Var Vol + Heat pump for these three zones and set the system up by the design cooling and heating capabilities. Currently, the SS-R shows 4380 under
heated hours for each of the zones. And no space heat is provided for any of the zones. Does anyone know the possible reasons for this phenomenon?<u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"> I've done several solutions by searching:<u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:12.0pt;font-family:"Arial",sans-serif;color:black">- Increased Throttling Range</span> <u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:12.0pt;font-family:"Arial",sans-serif;color:black">- Night Cycle Control --> Set to "Cycle on Any"</span><u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"> <span style="font-size:12.0pt;font-family:"Arial",sans-serif;color:black">- Fan Control and Placement - Set to" Hourly Report Schedule" </span><u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
<div>
<div>
<p class="MsoNormal"><img border="0" width="451" height="280" style="width:4.6979in;height:2.9166in" id="m_-6703254255761223734_x0000_i1025" src="cid:image001.png@01D47B66.0FB5CB80" alt="image.png"><u></u><u></u></p>
</div>
</div>
<div>
<div>
<p class="MsoNormal"><img border="0" width="452" height="280" style="width:4.7083in;height:2.9166in" id="m_-6703254255761223734_x0000_i1026" src="cid:image002.png@01D47B66.0FB5CB80" alt="image.png"><u></u><u></u></p>
</div>
</div>
<div>
<div>
<p class="MsoNormal"><img border="0" width="452" height="280" style="width:4.7083in;height:2.9166in" id="m_-6703254255761223734_x0000_i1027" src="cid:image003.png@01D47B66.0FB5CB80" alt="image.png"><u></u><u></u></p>
</div>
</div>
<div>
<div>
<p class="MsoNormal"><img border="0" width="452" height="281" style="width:4.7083in;height:2.927in" id="m_-6703254255761223734_x0000_i1028" src="cid:image004.png@01D47B66.0FB5CB80" alt="image.png"><u></u><u></u></p>
</div>
</div>
<div>
<div>
<p class="MsoNormal"><img border="0" width="452" height="278" style="width:4.7083in;height:2.8958in" id="m_-6703254255761223734_x0000_i1031" src="cid:image005.png@01D47B66.0FB5CB80" alt="image.png"><u></u><u></u></p>
</div>
</div>
<div>
<p class="MsoNormal">Thank you!<u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
<div>
<p class="MsoNormal">Jing<u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
</div>
</div>
<br>
<hr>
<font face="Arial" color="Gray" size="1"><br>
This email and any files transmitted with it are confidential and are intended solely for the use of the individual or entity to whom they are addressed. This communication represents the originator's personal views and opinions, which do not necessarily reflect
those of Henderson Engineers, Inc. If you are not the original recipient or the person responsible for delivering the email to the intended recipient, be advised that you have received this email in error, and that any use, dissemination, forwarding, printing,
or copying of this email is strictly prohibited. If you received this email in error, please immediately notify <a href="mailto:administrator@hendersonengineers.com" target="_blank">administrator@hendersonengineers.com</a>.<br>
</font>
</div>
</blockquote></div>