[Equest-users] Heating is not on for System Type Pkgd Var Vol, and 4380 under heated hours
Jing Hong
hongjing.shirley at gmail.com
Tue Nov 13 13:59:14 PST 2018
Michael,
Thanks for your response. I think you are correct that the Thermostat type
should be Reverse Action for VAV. I changed the thermostat type to
"Reverse Action" accordingly, but the space heat is still ZERO.
Jing
On Tue, Nov 13, 2018 at 3:41 PM Michael Busman <mbusman04 at gmail.com> wrote:
> Jing,
>
> It's been a while but I'm remembering back to my days using VisualDOE.
> You might want to check how your thermostat is defined. To get heating to
> simulate properly with a VAV system, the thermostat needs to be defined as
> reverse acting. Take a look at this.
>
> My best,
>
> Mike Busman CEM
> Retired Senior Energy Engineer
>
> On Tue, Nov 13, 2018 at 1:32 PM Daric Adair via Equest-users <
> equest-users at lists.onebuilding.org> wrote:
>
>> Jing;
>>
>>
>>
>> First thing that jumps out at me is that there is no Heating Discharge
>> Air Tempertaures or Reheat Temperatures set on the System>Heating Tab (last
>> image you shared). For a VAV System I’d expect these values to be something
>> like: Zone Max Temp: 90F Hot Deck Max Leaving Temperature 60F and Reheat
>> Delta T: 35F.
>>
>>
>>
>>
>>
>> Thanks,
>>
>> *DARIC R ADAIR* PE, CEM, BEMP
>> Mechanical Engineer, Energy Analyst
>>
>> *Henderson Engineers*
>> daric.adair at hendersonengineers.com
>>
>> *Licensed in* KS
>>
>>
>>
>> *From:* Jing Hong <hongjing.shirley at gmail.com>
>> *Sent:* Tuesday, November 13, 2018 3:16 PM
>> *To:* equest-users at lists.onebuilding.org; equest-users at onebuilding.org
>> *Subject:* [Equest-users] Heating is not on for System Type Pkgd Var
>> Vol, and 4380 under heated hours
>>
>>
>>
>> Dear All,
>>
>>
>>
>> My model is located in Mexico and three zones are equipped with VFD. So I
>> selected Pkgd Var Vol + Heat pump for these three zones and set the system
>> up by the design cooling and heating capabilities. Currently, the SS-R
>> shows 4380 under heated hours for each of the zones. And no space heat is
>> provided for any of the zones. Does anyone know the possible reasons for
>> this phenomenon?
>>
>> I've done several solutions by searching:
>>
>> - Increased Throttling Range
>>
>> - Night Cycle Control --> Set to "Cycle on Any"
>>
>> - Fan Control and Placement - Set to" Hourly Report Schedule"
>>
>>
>>
>> [image: image.png]
>>
>> [image: image.png]
>>
>> [image: image.png]
>>
>> [image: image.png]
>>
>> [image: image.png]
>>
>> Thank you!
>>
>>
>>
>> Jing
>>
>>
>>
>> ------------------------------
>>
>> This email and any files transmitted with it are confidential and are
>> intended solely for the use of the individual or entity to whom they are
>> addressed. This communication represents the originator's personal views
>> and opinions, which do not necessarily reflect those of Henderson
>> Engineers, Inc. If you are not the original recipient or the person
>> responsible for delivering the email to the intended recipient, be advised
>> that you have received this email in error, and that any use,
>> dissemination, forwarding, printing, or copying of this email is strictly
>> prohibited. If you received this email in error, please immediately notify
>> administrator at hendersonengineers.com.
>> _______________________________________________
>> Equest-users mailing list
>> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>> To unsubscribe from this mailing list send a blank message to
>> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20181113/b0b169a7/attachment-0003.htm>
More information about the Equest-users
mailing list