[Equest-users] Heating is not on for System Type Pkgd Var Vol, and 4380 under heated hours

Michael Busman mbusman04 at gmail.com
Tue Nov 13 13:41:09 PST 2018


Jing,

It's been a while but I'm remembering back to my days using VisualDOE.  You
might want to check how your thermostat is defined.  To get heating to
simulate properly with a VAV system, the thermostat needs to be defined as
reverse acting.  Take a look at this.

My best,

Mike Busman CEM
Retired Senior Energy Engineer

On Tue, Nov 13, 2018 at 1:32 PM Daric Adair via Equest-users <
equest-users at lists.onebuilding.org> wrote:

> Jing;
>
>
>
> First thing that jumps out at me is that there is no Heating Discharge Air
> Tempertaures or Reheat Temperatures set on the System>Heating Tab (last
> image you shared). For a VAV System I’d expect these values to be something
> like: Zone Max Temp: 90F Hot Deck Max Leaving Temperature 60F and Reheat
> Delta T: 35F.
>
>
>
>
>
> Thanks,
>
> *DARIC R ADAIR* PE, CEM, BEMP
> Mechanical Engineer, Energy Analyst
>
> *Henderson Engineers*
> daric.adair at hendersonengineers.com
>
> *Licensed in* KS
>
>
>
> *From:* Jing Hong <hongjing.shirley at gmail.com>
> *Sent:* Tuesday, November 13, 2018 3:16 PM
> *To:* equest-users at lists.onebuilding.org; equest-users at onebuilding.org
> *Subject:* [Equest-users] Heating is not on for System Type Pkgd Var Vol,
> and 4380 under heated hours
>
>
>
> Dear All,
>
>
>
> My model is located in Mexico and three zones are equipped with VFD. So I
> selected Pkgd Var Vol + Heat pump for these three zones and set the system
> up by the design cooling and heating capabilities. Currently, the SS-R
> shows 4380 under heated hours for each of the zones. And no space heat is
> provided for any of the zones. Does anyone know the possible reasons for
> this phenomenon?
>
>  I've done several solutions by searching:
>
> - Increased Throttling Range
>
> - Night Cycle Control --> Set to "Cycle on Any"
>
>  - Fan Control and Placement - Set to" Hourly Report Schedule"
>
>
>
> [image: image.png]
>
> [image: image.png]
>
> [image: image.png]
>
> [image: image.png]
>
> [image: image.png]
>
> Thank you!
>
>
>
> Jing
>
>
>
> ------------------------------
>
> This email and any files transmitted with it are confidential and are
> intended solely for the use of the individual or entity to whom they are
> addressed. This communication represents the originator's personal views
> and opinions, which do not necessarily reflect those of Henderson
> Engineers, Inc. If you are not the original recipient or the person
> responsible for delivering the email to the intended recipient, be advised
> that you have received this email in error, and that any use,
> dissemination, forwarding, printing, or copying of this email is strictly
> prohibited. If you received this email in error, please immediately notify
> administrator at hendersonengineers.com.
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20181113/eeb30ab2/attachment-0005.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 62889 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20181113/eeb30ab2/attachment-0054.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 50882 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20181113/eeb30ab2/attachment-0055.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 43429 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20181113/eeb30ab2/attachment-0056.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 58706 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20181113/eeb30ab2/attachment-0057.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.png
Type: image/png
Size: 63529 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20181113/eeb30ab2/attachment-0058.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 62889 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20181113/eeb30ab2/attachment-0059.png>


More information about the Equest-users mailing list