Hey Daric,

I'm on the same page with David.  Space Loads export includes annual totals for equipment/plug loads and for lighting at a SPACE resolution, but there's no way to immediately calculate FLEH for a given annual schedule I'm aware of.

Short of loading/managing/manipulating schedules with an exterior spreadsheet (hint hint), I think the best advice I can give is to highlight a day schedule, swap to spreadsheet view, and copy that table (or the specific rows you want) into excel.  From there you have to determine how many days per year each day type applies to the schedule(s) of interest, then it's just some summing and multiplying to arrive at your answer.

~Nick

[cid:image001.png at 01D3BC39.84240FF0]
Nick Caton, P.E., BEMP
  Senior Energy Engineer
  Regional Energy Engineering Manager
  Energy and Sustainability Services
  Schneider Electric

D  913.564.6361
M  785.410.3317
F  913.564.6380
E  nicholas.caton at schneider-electric.com<mailto:nicholas.caton at schneider-electric.com>

15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States

[cid:image002.png at 01D3BC39.84240FF0]



From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of David Reddy via Equest-users
Sent: Thursday, March 15, 2018 1:22 AM
To: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] eQuest Generated EFLH


Daric,

The space loads report (via File -> Export File ->) has schedule values for select space internal loads starting in col AC, but I believe if you have more than one schedule for a given end-use, this summary is not correct, or represents a weighted-average.  I don't use this often, so can't recall the behavior when there is more than one schedule defined for a particular end-use.  This is the only EFLH summary I'm aware of, and I believe it is an eQUEST function, not DOE-2.2.

-David

On 3/14/2018 2:27 PM, Daric Adair via Equest-users wrote:
Does anyone know if there is a report or means from eQuest to generate the EFLH (equivalent full load hours) for each schedule?
Colleague of mine believes VistualDOE was able to complete and hoping there is a comparable tool/report.

Thanks in advance.



Thanks,
DARIC R ADAIR PE, CEM, BEMP
Mechanical Engineer, Energy Analyst

Henderson Engineers
8345 Lenexa Drive, Suite 300  |  Lenexa, KS 66214
Tel (913) 742-5530
daric.adair at hendersonengineers.com<mailto:daric.adair at hendersonengineers.com>

hendersonengineers.com<http://www.hendersonengineers.com/>

Licensed in KS

Sending me large files? Please use Henderson File Share<https://apps.hendersonengineers.com/FileShare/Upload?to=daric.adair@hendersonengineers.com> | TX ID #F-001236


________________________________

This email and any files transmitted with it are confidential and are intended solely for the use of the individual or entity to whom they are addressed. This communication represents the originator's personal views and opinions, which do not necessarily reflect those of Henderson Engineers, Inc. If you are not the original recipient or the person responsible for delivering the email to the intended recipient, be advised that you have received this email in error, and that any use, dissemination, forwarding, printing, or copying of this email is strictly prohibited. If you received this email in error, please immediately notify administrator at hendersonengineers.com<mailto:administrator at hendersonengineers.com>.




_______________________________________________

Equest-users mailing list

http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org

To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>


______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180315/842c8341/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 255 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180315/842c8341/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 8477 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180315/842c8341/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: oledata.mso
Type: application/octet-stream
Size: 7134 bytes
Desc: oledata.mso
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180315/842c8341/attachment.obj>


More information about the Equest-users mailing list