[Equest-users] Loop to Loop Heat Pump Error
Bishop, Bill
bbishop at pathfinder-ea.com
Wed Mar 7 06:22:48 PST 2018
Pasha,
Like Nick, I had no problem getting the model to run using 3.65 build 7174 in DOE2.2 mode.
It also runs in 3.64 build 7130, once I remove the line “HVACDefaulted = 1” from the pd2 file.
A couple suggestions:
- Go to the Miscellaneous tab of the chiller and Restore Default to the four Heat Exchanger inputs. The error message you sent makes me think these have non-default values.
- Copy the .pd2 and .inp files you sent into a new folder and try opening it again.
Regards,
~Bill
William Bishop, PE, BEMP, BEAP, CEM, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer
[cid:image007.jpg at 01D3B5F6.0C4754E0] [cid:image008.jpg at 01D3B5F6.0C4754E0]
134 South Fitzhugh Street Rochester, NY 14608
T: (585) 698-1956 F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com> www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
[http://png-5.findicons.com/files/icons/977/rrze/720/globe.png]Carbon Fee and Dividend - simple, effective, and market-based.
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of David Eldridge via Equest-users
Sent: Tuesday, March 06, 2018 10:34 PM
To: PKConsulting <pasha.pkconsulting at gmail.com>; Nicholas Caton <Nicholas.Caton at schneider-electric.com>
Cc: equest-users at onebuilding.org
Subject: Re: [Equest-users] Loop to Loop Heat Pump Error
Hopefully Nick’s software version control works. If not, maybe you can track down those keywords in the BDL(?) file – I forget – the file with the compiled syntax, where the INP doesn’t echo back fields with default values?
David
David S. Eldridge, Jr., P.E., LEED AP BD+C, BEMP, BEAP, HBDP
Grumman/Butkus Associates
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of PKConsulting via Equest-users
Sent: Tuesday, March 06, 2018 6:53 PM
To: Nicholas Caton <Nicholas.Caton at schneider-electric.com<mailto:Nicholas.Caton at schneider-electric.com>>
Cc: equest-users at onebuilding.org<mailto:equest-users at onebuilding.org>
Subject: Re: [Equest-users] Loop to Loop Heat Pump Error
Thanks David, at this point I just don’t know. I looked through the .inp file too and couldn’t find those keywords either. That is when I turned to the group for more help.
I’m completely stumped on this one...
Pasha
Ph: 308-763-1593
On Mar 6, 2018, at 4:10 PM, Nicholas Caton <Nicholas.Caton at schneider-electric.com<mailto:Nicholas.Caton at schneider-electric.com>> wrote:
Would it bug you to learn this loads and simulates without error on my end?
Gut check: are you being deliberate to open and simulate with the “release testing” build 7174?
~Nick
<image001.png>
Nick Caton, P.E., BEMP
Senior Energy Engineer
Regional Energy Engineering Manager
Energy and Sustainability Services
Schneider Electric
D 913.564.6361
M 785.410.3317
F 913.564.6380
E nicholas.caton at schneider-electric.com<mailto:nicholas.caton at schneider-electric.com>
15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States
<image002.png>
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Pasha Korber-Gonzalez via Equest-users
Sent: Tuesday, March 06, 2018 3:11 PM
To: eQUEST Users List <equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>>
Subject: [Equest-users] Loop to Loop Heat Pump Error
Hi All,
does anyone have any experience with modeling the Loop to Loop Heat Pump chiller? I'm getting the following error in my file, and right now I am auto-sizing everything just to test it to get the file to run. I cannot locate/find where the Qhx Design, SupFlow, SupTi, SupTo key words are linked too. The heat-Exchanger: HRC-T1 is the name of my LtLHP Chiller that I input on the loops.
I've looked through the DOE-2 documents for LtLHP chiller and I can't find where this error is occurring so that I can fix it. Any insight you can offer will be appreciated.
I've also attached my .pd2 & .inp files if anyone is inclined to look at them. Thanks in advance for sharing your thoughts and your brains with me!
***ERROR***********************************************************************
Heat-Exchanger: HRC-T1 has
inconsistent design parameters:
QhxDesign SupFlow SupTi SupTo
3541040. 708. 85.0 95.0
DemFlow DemTi DemTo
708. 85.0 75.0
Pasha
Ph: 308-763-1593
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180307/0f1ff9fa/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image007.jpg
Type: image/jpeg
Size: 1517 bytes
Desc: image007.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180307/0f1ff9fa/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image008.jpg
Type: image/jpeg
Size: 1647 bytes
Desc: image008.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180307/0f1ff9fa/attachment-0001.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image009.png
Type: image/png
Size: 3856 bytes
Desc: image009.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180307/0f1ff9fa/attachment.png>
More information about the Equest-users
mailing list