[Equest-users] What does Space Heat include?
Jing Hong
hongjing.shirley at gmail.com
Wed Jan 3 11:45:05 PST 2018
Thank you Nick!
I've fixed the problem by setting the cooling and heating design season.
Jing
On Tue, Jan 2, 2018 at 5:15 PM, Nicholas Caton <
Nicholas.Caton at schneider-electric.com> wrote:
> The last three pages of this document may prove a helpful starting place
> for “what’s included in XXX end use category” questions.
>
> From there:
>
>
>
> It’s hard for anyone to do better than just guess at what might be the
> source from what you’ve provided… reheat/baseboard/pilot lights… it might
> not be zone-thermostat schedule driven heating.
>
>
>
> On the aside, have you explored whether you have any zones still dropping
> to 40F that could be a source (subjectively warm climates can still have
> brisk evenings)? You can remove all calls for heat by defaulting away the
> heating schedule assignment, but pay mind to how close to freezing you go –
> your mechanical designer may not be so comfortable with the results!
>
>
>
> Hope that’s helpful,
>
>
>
> ~Nick
>
>
>
> *Nick Caton, P.E., BEMP*
>
> Senior Energy Engineer
> Regional Energy Engineering Manager
>
> Energy and Sustainability Services
> Schneider Electric
>
> D 913.564.6361 <(913)%20564-6361>
> M 785.410.3317 <(785)%20410-3317>
> F 913.564.6380 <(913)%20564-6380>
> E nicholas.caton at schneider-electric.com
>
> 15200 Santa Fe Trail Drive
> <https://maps.google.com/?q=15200+Santa+Fe+Trail+Drive+%0D+Suite+204+%0D+Lenexa,+KS+66219+%0D+United+States&entry=gmail&source=g>
> Suite 204
> Lenexa, KS 66219
> United States
>
>
>
>
>
> *From:* Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] *On
> Behalf Of *Jing Hong via Equest-users
> *Sent:* Tuesday, December 26, 2017 9:08 AM
> *To:* equest-users at lists.onebuilding.org; equest-users at onebuilding.org
> *Subject:* [Equest-users] What does Space Heat include?
>
>
>
> Dear all,
>
>
>
> Happy Holiday!
>
>
>
> I have a question: What does Space Heat include in eQuest? I set a heating
> design temp very low, like 40 F for a ventilation only condition, but still
> get 0.01 x10^6 Btu Space Heat in June and Aug for Climate zone 3B. That
> does not make any sense. I tried several ways to detect where that space
> heat comes from in June, but could not figure out.
>
> Here is the background of my model: It is in climate zone 3B. The baseline
> is DX+Furnace (ASHRAE). I have four schedules to control temperature:
> Cooling (75F), Heating(72F), Ventilation for cooling season(100F),
> ventilation for heating season(40F). I setup 100F and 40F to avoid turning
> the cooling and heating mode on for the rooms requesting ventilation only.
>
>
>
> Please let me know if I did something wrong for my model. Thank you!
>
>
>
> Jing
> --
>
> PhD Candidate, LEED AP BD+C
>
>
>
> School of Architecture and Urban Planning
>
> University of Wisconsin-Milwaukee
>
>
>
>
> ______________________________________________________________________
> This email has been scanned by the Symantec Email Security.cloud service.
> ______________________________________________________________________
>
--
PhD Candidate, LEED AP BD+C
School of Architecture and Urban Planning
University of Wisconsin-Milwaukee
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180103/2cb66cdd/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 255 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180103/2cb66cdd/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 27460 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180103/2cb66cdd/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 8477 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180103/2cb66cdd/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 49392 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180103/2cb66cdd/attachment-0003.png>
More information about the Equest-users
mailing list