[Equest-users] Slab on Grade Floor Heat Loss

Joe Huang yjhuang at whiteboxtechnologies.com
Mon Feb 5 22:01:44 PST 2018


Christopher,

You're exactly right. It probably takes the building several years to warm up the ground 
beneath the foundation to a long-term steady-state.

When I was doing thousands of foundation simulations for the Building Foundation Design 
Handbook (Labs, Carmody, Sterling, Shen, Huang, and Parker, Underground Space Center, 
University of Minnesota 1988),  Lester Shen and I discussed whether to initialize the 
simulations with or without the building. We ended up deciding to initialize without a 
building, i.e., for an empty site, on the logic that the results would be more 
representative for new construction.  However, if you're trying to calibrate your model 
for an existing building, you might want to initialize for ten years to pick up the fact 
that the building warms up the ground over time.  Even initializing for bare ground took 
about five years.  We solved the runtime issue by doing four years at a monthly time step, 
one year at a daily time step, before finally doing the run.  Worked out fine.

Joe

Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 205A
Moraga CA 94556
yjhuang at whiteboxtechnologies.com
http://weather.whiteboxtechnologies.com for simulation-ready weather data
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"

On 2/5/2018 11:54 AM, Jones, Christopher wrote:
>
> It seems to me that the centre of building underslab temperature gradient would change 
> over time. When the building is first turned on, the underslab may be close to the 
> average deep ground temperature. Depending on soil type, with the room temperature 
> approximately constant, I would expect that underslab soil temperature to warm up?
>
> I haven’t been able to find a paper addressing the subject.
>
> **
>
> *Christopher R. Jones*, P.Eng.
>
> Technical Specialist
>
> Sustainability & Energy
>
> T +1 416-644-0252
>
> 2300 Yonge Street, Suite 2300
>
> Toronto, ON M4P 1E4 Canada
>
> wsp.com
>
> __
>
> **
>
> /Please consider the environment before printing.../
>
> *From:*Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] *On Behalf Of 
> *Joe Huang via Equest-users
> *Sent:* Friday, February 02, 2018 4:55 PM
> *To:* equest-users at lists.onebuilding.org
> *Subject:* Re: [Equest-users] Slab on Grade Floor Heat Loss
>
> The use of F2 factors for foundation heat flows has always been flawed.   The simplest 
> explanation for the F2 factor is that it's the effective U-value per perimeter length.   
> This formulation assumes that there are no heat loses through the foundation away from 
> the perimeter, which is simply not true (think of the case in Minnesota where the 
> constant deep ground temperatures is between 55 and 60 F).  The other problem is the 
> delta-T used to derive the F2 factor is not clearly defined.  All the studies I've seen 
> (albeit  all these are from 30 years  ago or more) derived  them against the outdoor air 
> temperature, or more exactly, Tin - Tair.   This then opens up the question whether in 
> DOE-2 the slab  should be modeled as an exterior wall or an underground wall?   The 
> third problem  is that by treating the slab as a monolithic surface, it lumps the heat 
> flow characteristics along the perimeter with those of the slab core , which differ in 
> both magnitude and time  lag.
>
> When I last had a project on ground heat flows 17  years ago,  I proposed a simplified 
> method where the foundation was divided into three regions  (perimeter  1' ,  near 
> perimeter 1-4', and core >4' deep),  each with 3 conductances  to the daily average air 
> temperature , average air temperature over the past three weeks,  and the deep ground 
> temperature.  This method was implemented in an enhanced version of DOE-2.1E, and from 
> what I hear, adopted  into California Title-24.   If anyone is interested  to read the 
> report, just send me an e-mail.
> <#yiv9572653599Picture_x0020_4>
>
> The good news for everyone here is that there is now a RTAR/WS  (ASHRAE terminology for 
> a RFP) being circulated  in TC 4.7 (Energy Calculations)  that aims to develop a better 
> simplified ground model to replace the F2 factors. Stay tuned but be forewarned that it 
> takes ASHRAE at least a year to approve  a project and another half year to pick a 
> contractor, so don't expect any products for another 3 years.
>
> Joe
>
> Moraga CA 94556
> yjhuang at whiteboxtechnologies.com <mailto:yjhuang at whiteboxtechnologies.com>
> http://weather.whiteboxtechnologies.com  for simulation-ready weather data
> (o) (925)388-0265
> (c) (510)928-2683
> "building energy simulations at your fingertips"
>
> On 2/2/2018 12:26 PM, Paul Diglio via Equest-users wrote:
>
>     Thanks Bill, you are always such a big help.  That is what I thought, but just
>     wanted to run it by the forum.
>
>     Thanks to you too Nathan.
>
>     Paul Diglio
>
>     ------------------------------------------------------------------------------------------
>
>     *From:*"Bishop, Bill" <bbishop at pathfinder-ea.com> <mailto:bbishop at pathfinder-ea.com>
>     *To:* Nathan Miller <nathanm at rushingco.com> <mailto:nathanm at rushingco.com>; Paul
>     Diglio <paul.diglio at sbcglobal.net> <mailto:paul.diglio at sbcglobal.net>;
>     "equest-users at onebuilding.org" <mailto:equest-users at onebuilding.org>
>     <equest-users at onebuilding.org> <mailto:equest-users at onebuilding.org>
>     *Sent:* Friday, February 2, 2018 3:13 PM
>     *Subject:* RE: [Equest-users] Slab on Grade Floor Heat Loss
>
>     Paul,
>
>     Your reviewer may have thought that if the slab was showing up as an “exterior
>     surface” (such as on the LV-D report) than the model was simulating heat transfer
>     between the zones and the outside air through the slab. But eQUEST/DOE-2 simulates
>     heat transfer across underground surfaces differently, as described in the
>     UNDERGROUND-WALL and UNDERGROUND-FLOOR section of the DOE-2 help documentation. The
>     main difference is that ground temperature is used instead of the OA temperature as
>     the outside temperature. The monthly ground temperature is taken from the weather
>     file, or can be entered as SITE-PARAMETERS:GROUND-T.
>
>     The eQUEST wizard creates custom constructions for each underground surface based on
>     inputs for Exterior/Cavity Insulation and Perimeter Floor Insulation. Underground
>     floors are given constructions with low U-factor (high R-value) consistent with the
>     lower heat transfer that would be expected.
>
>     Regards,
>
>     ~Bill
>
>     *William Bishop, PE, BEMP, BEAP, CEM, LEED AP | Pathfinder Engineers & Architects LLP*
>
>     *Senior Energy Engineer*
>
>     	
>
>     134 South Fitzhugh StreetRochester, NY 14608
>
>     */T: (585) 698-1956/**//*F: (585) 325-6005
>
>     bbishop at pathfinder-ea.com <mailto:wbishop at pathfinder-ea.com>www.pathfinder-ea.com
>     <http://www.pathfinder-ea.com/>
>
>     http://png-5.findicons.com/files/icons/977/rrze/720/globe.pngCarbon Fee and Dividend
>     - simple, effective, and market-based.
>
>     *From:*Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] *On Behalf
>     Of *Nathan Miller via Equest-users
>     *Sent:* Friday, February 02, 2018 2:35 PM
>     *To:* Nathan Miller <nathanm at rushingco.com> <mailto:nathanm at rushingco.com>; Paul
>     Diglio <paul.diglio at sbcglobal.net> <mailto:paul.diglio at sbcglobal.net>;
>     equest-users at onebuilding.org <mailto:equest-users at onebuilding.org>
>     *Subject:* Re: [Equest-users] Slab on Grade Floor Heat Loss
>
>     Fixed my typo in the F-factor heat loss calc (should have read 50 ft of perimeter)…
>     See below.
>
>     *Nathan Miller, PE, LEED AP BD+C – */Mechanical Engineer/Senior Energy Analyst/
>
>     *RUSHING*| *O* 206-285-7100 | *C* 207-650-3942
>
>     *www.rushingco.com <http://www.rushingco.com/>*
>
>     *From:*Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] *On Behalf
>     Of *Nathan Miller via Equest-users
>     *Sent:* Friday, February 2, 2018 2:33 PM
>     *To:* Paul Diglio <paul.diglio at sbcglobal.net <mailto:paul.diglio at sbcglobal.net>>;
>     equest-users at onebuilding.org <mailto:equest-users at onebuilding.org>
>     *Subject:* Re: [Equest-users] Slab on Grade Floor Heat Loss
>
>     In the past I’ve done a conversion of F-factor (perimeter based) slab-on-grade heat
>     loss to U-factor (area) and input that in on a zone-by-zone basis if I really wanted
>     to nail down SOG heat loss.
>
>     Example- Space is 20’ x 30’, but the exposed perimeter is only two of the faces (20’
>     + 30’). Lets say it is uninsulated SOG.
>
>     F-factor from 90.1: F = 0.73 Btu/(hr*ft*F)
>
>     Perimeter based heat loss: 0.73 Btu/(hr*ft*F) * 50 ft = 36.5 BTU/(hr *F)
>
>     Then we can back-calculate the U-factor to assume for the whole floor to equate to
>     that heat loss: 36.5 BTU/(hr *F) = 600 SF * X BTU/(hr*SF*F) -> U = 0.0608 BTU/(hr*SF*F)
>
>     You can create a custom floor construction for each space to provide the U-factor to
>     produce equivalent heat loss that the F-factor calcs are telling you lose. For
>     purely core zones (no exposed perimeter), I guess the F-factor calcs are telling us
>     were not really losing heat through that slab (doesn’t’ seem right, but it probably
>     is relatively small)
>
>     *Nathan Miller, PE, LEED AP BD+C – */Mechanical Engineer/Senior Energy Analyst/
>
>     *RUSHING*| *O* 206-285-7100 | *C* 207-650-3942
>
>     *www.rushingco.com
>     <https://url.emailprotection.link/?a6X-5ry0mOOudUi-eMfQ7K9LfplwNoMV9idJhgEyf85c%7E>*
>
>     *From:*Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] *On Behalf
>     Of *Paul Diglio via Equest-users
>     *Sent:* Friday, February 2, 2018 2:19 PM
>     *To:* equest-users at onebuilding.org <mailto:equest-users at onebuilding.org>
>     *Subject:* [Equest-users] Slab on Grade Floor Heat Loss
>
>     I recently submitted a model to the local utility company for an incentive.  Part of
>     the buildings' first floor is slab on grade.
>
>     One of the comments I received back is that this erroneously shows up as an exterior
>     surface and I should delete all the slab on grade floors in the component tree.
>     Doesn't seem right to me.
>
>     I did a few and it does reduce the overall energy consumption.  In the 3D model, no
>     floors show, just open to the interior of the zone.
>
>     So is eQuest assuming that without this floor, there is no heat loss out the bottom
>     of the zone?  Is this reasonable?
>
>     Thank you,
>
>     Paul Diglio
>
>
>
>
>     _______________________________________________
>
>     Equest-users mailing list
>
>     http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>
>     To unsubscribe from this mailing list send  a blank message toEQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>     <mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
>
>
> ------------------------------------------------------------------------------------------
>
>
> NOTICE: This communication and any attachments ("this message") may contain information 
> which is privileged, confidential, proprietary or otherwise subject to restricted 
> disclosure under applicable law. This message is for the sole use of the intended 
> recipient(s). Any unauthorized use, disclosure, viewing, copying, alteration, 
> dissemination or distribution of, or reliance on, this message is strictly prohibited. 
> If you have received this message in error, or you are not an authorized or intended 
> recipient, please notify the sender immediately by replying to this message, delete this 
> message and all copies from your e-mail system and destroy any printed copies. You are 
> receiving this communication because you are listed as a current WSP contact. Should you 
> have any questions regarding WSP's electronic communications policy, please consult our 
> Anti-Spam Commitment at www.wsp.com/casl <http://www.wsp.com/casl>. For any concern or 
> if you believe you should not be receiving this message, please forward this message to 
> caslcompliance at wsp.com <mailto:caslcompliance at wsp.com> so that we can promptly address 
> your request. Note that not all messages sent by WSP qualify as commercial electronic 
> messages.
>
> AVIS : Ce message, incluant tout fichier l'accompagnant (« le message »), peut contenir 
> des renseignements ou de l'information privilégiés, confidentiels, propriétaires ou à 
> divulgation restreinte en vertu de la loi. Ce message est destiné à l'usage exclusif 
> du/des destinataire(s) voulu(s). Toute utilisation non permise, divulgation, lecture, 
> reproduction, modification, diffusion ou distribution est interdite. Si vous avez reçu 
> ce message par erreur, ou que vous n'êtes pas un destinataire autorisé ou voulu, 
> veuillez en aviser l'expéditeur immédiatement et détruire le message et toute copie 
> électronique ou imprimée. Vous recevez cette communication car vous faites partie des 
> contacts de WSP. Si vous avez des questions concernant la politique de communications 
> électroniques de WSP, veuillez consulter notre Engagement anti-pourriel au 
> www.wsp.com/lcap <http://www.wsp.com/lcap>. Pour toute question ou si vous croyez que 
> vous ne devriez pas recevoir ce message, prière de le transférer au 
> conformitelcap at wsp.com <mailto:conformitelcap at wsp.com> afin que nous puissions 
> rapidement traiter votre demande. Notez que ce ne sont pas tous les messages transmis 
> par WSP qui constituent des messages electroniques commerciaux.
>
>
>
> -LAEmHhHzdJzBlTWfa4Hgs7pbKl 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180205/3ae40c4b/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 25844 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180205/3ae40c4b/attachment.png>


More information about the Equest-users mailing list