[Equest-users] Maximum number of expression dependency lists exceeded

Lapierre, Patrick plapierre at bpa.ca
Mon Feb 5 06:46:16 PST 2018


I came across this problem before.
As you pointed out, changing the MaxExpDeps didn't work for me.
In the end I deleted every interior wall to reduce the number of components in the model and it worked.
Not ideal but it was better than not running at all.

Patrick Lapierre_ing. BEMP

plapierre at bpa.ca | t: 5143833747x2807
-----Message d'origine-----
De : Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] De la part de Brian Fountain via Equest-users
Envoyé : 4 février 2018 09:31
À : equest-users at lists.onebuilding.org
Objet : [Equest-users] Maximum number of expression dependency lists exceeded

I know this has come up on the list before but I am now struggling with a (large, over-zoned) model that is throwing "Maximum number of expression dependency lists exceeded" errors.

The archive suggested setting  MaxExpDeps=10 in the .pd2.  That does not change the number of errors thrown on my model.

Would greatly appreciate assistance from anyone who has overcome this.

Many thanks,

Brian


_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG


More information about the Equest-users mailing list