Hi Tanya,
Are you trying to ask "why are so many systems created?"
-It is because in wizard mode-under the “Air side systems” tab, you have
selected your system to be "system per zone". That’s the reason why you
have one system for each zone.
ASHRAE appendix says that in Baseline case"System per floor” should be used
and for the proposed case it has to be modeled as per the HVAC drawings.
(multiple zones under 1 system as applicable)
As of now you have already entered detailed wizard mode, so I guess the
only option you have is to create new systems and assign the zones to it.
Hope I am clear
Revert if any assistance needed.
Thanks,
Tejas
On Wed, Aug 15, 2018 at 5:27 PM, Tanya Soji via Equest-users <
equest-users at lists.onebuilding.org> wrote:
> Hey there eQuest Users,
>
>
>
> I’m new to the eQuest softwarr,
>
>
>
> Please find the attached screenshot given below. It’s a multi-storey
> building with G+6 floors (distributed differently building-wise, some are
> G+4) and 3 Basement floors. There are 5 shells totally.
>
> I’ve finished entering details on the Wizard mode and have moved on to the
> Detailed mode; However, inorder to enter more specific details (zonewise),
> multiple active systems are available as seen. I’m not quite sure if every
> zone entry needs to be made. And also how does eQuest generate default zone
> definitions ? The template given doesn’t match to the ones given such as EL1
> Sys1 (MZS) (G.W1).
>
>
>
>
>
> *Thanks & Regards, *
>
>
>
> *Tanya Soji *| *Energy Engineer *
>
> *E.*: tanya.soji at quantumesco.com | *D.*: + 971 4 567 4212
>
>
>
> [image: QE Logo - 13NOV2017-01.png]
>
>
>
> QUANTUM *EUROSTAR ENERGY SOLUTION CO. L.L.C*
>
> 📍 33rd Floor, Vision Tower, Business bay. P. O. Box - 51098, Dubai - UAE.
>
> *☎ *: + 971 4 451 4444
>
> Ê : + 971 4 451 4441
>
> " : www.quantumesco.com
>
> [image: facebook icon] <https://www.facebook.com/eurostargroup>[image:
> youtube icon]
> <https://www.youtube.com/channel/UCG902il67o-nQqnMYduBVUQ/feed?view_as=subscriber>[image:
> linkedin icon] <https://www.linkedin.com/company/eurostar_2/>[image:
> google plus icon] <https://plus.google.com/u/0/112676746965733378647>[image:
> twitter icon] <https://twitter.com/eurostar_group?lang=en>
>
>
>
>
>
> This e-mail is from Eurostar Group. is intended solely for the person to
> whom it has been addressed. It should not be used by anyone else. It may
> contain confidential and/or legally privileged information. If you are not
> the intended recipient, you are notified that any use, distribution,
> transmission, printing, copying, dissemination or any action in reliance on
> it is strictly prohibited. If you have received this email erroneously,
> please delete this message and notify the sender.
> The recipient acknowledges that Eurostar Group /subsidiaries/ associated
> companies, are unable to exercise control or ensure or guarantee the
> integrity of/over the contents of the information contained in e-mail
> transmissions and further acknowledges that any views expressed in this
> message are those of the individual sender and no binding nature of the
> message shall be implied or assumed unless the sender does so expressly
> with due authority of Eurostar Group. If the recipient thinks that any
> part of this email transgresses any law of the land, he/she I shall
> immediately alert Eurostar Group, by mailing their specific concern on
> compliance at eurostargroup.com Needless to reiterate that Consequently,
> Eurostar does not take any liability whatsoever, for any such
> transgressions.
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180816/3eb7755d/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 63844 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180816/3eb7755d/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.png
Type: image/png
Size: 486 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180816/3eb7755d/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image008.png
Type: image/png
Size: 518 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180816/3eb7755d/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 481 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180816/3eb7755d/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.png
Type: image/png
Size: 500 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180816/3eb7755d/attachment-0003.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 2642 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180816/3eb7755d/attachment-0001.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image007.png
Type: image/png
Size: 487 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180816/3eb7755d/attachment-0004.png>
More information about the Equest-users
mailing list