[Equest-users] Can we reference DESIGN-DAY inputs in zonal expressions?
Bishop, Bill via Equest-users
equest-users at lists.onebuilding.org
Thu Sep 7 13:11:59 PDT 2017
Hi Nick,
I haven't figured out a way to reference DESIGN-DAY keywords from outside of the command. The DESIGN-DAYs are not global parameters (so you can't use #G), and they do not have children that can reference them as parents. You could create global parameters per your own suggestion below.
An alternative is to reference other climate data inputs for your DESIGN-COOL-T and DESIGN-HEAT-T zone keywords.
For example, you could enter the monthly ground temperatures. Then, say you want the unconditioned zone DESIGN-HEAT-T to match the December ground temperature:
if(#RV(#G("SITE-PARAMETERS","GROUND-T",11))==0)
then #G("SITE-PARAMETERS","GROUND-T",11)
else 70 endif
Regards,
~Bill
William Bishop, PE, BEMP, BEAP, CEM, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer
[cid:image004.jpg at 01D327F4.24989800] [cid:image006.jpg at 01D327F4.24989800]
134 South Fitzhugh Street Rochester, NY 14608
T: (585) 698-1956 F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com> www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
[http://png-5.findicons.com/files/icons/977/rrze/720/globe.png]Carbon Fee and Dividend - simple, effective, and market-based.
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Nicholas Caton via Equest-users
Sent: Thursday, September 07, 2017 11:59 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Can we reference DESIGN-DAY inputs in zonal expressions?
Hi friends!
Is fundamentally possible to, from within a user-expression, pull a value from cooling / heating DESIGN-DAY inputs?
In particular, I'd like to return DRYBULB-HIGH from both my cooling and heating DESIGN-DAY, using those values to inform zonal DESIGN-COOL-T and DESIGN-HEAT-T for unconditioned and plenum zones. I can see a path to have both DESIGN-DAY and zonal inputs reference a pair of global parameters, but I'm making every effort to minimize "#PA spam" in my regular model development.
~Nick
[cid:image009.png at 01D327EB.5D9B6820]
Nick Caton, P.E., BEMP
Senior Energy Engineer
Regional Energy Engineering Manager
Energy and Sustainability Services
Schneider Electric
D 913.564.6361
M 785.410.3317
F 913.564.6380
E nicholas.caton at schneider-electric.com<mailto:nicholas.caton at schneider-electric.com>
15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States
[cid:image010.png at 01D327EB.5D9B6820]
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170907/afd93249/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image009.png
Type: image/png
Size: 255 bytes
Desc: image009.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170907/afd93249/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image010.png
Type: image/png
Size: 8477 bytes
Desc: image010.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170907/afd93249/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.jpg
Type: image/jpeg
Size: 1517 bytes
Desc: image004.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170907/afd93249/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.jpg
Type: image/jpeg
Size: 1647 bytes
Desc: image006.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170907/afd93249/attachment-0001.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image008.png
Type: image/png
Size: 3852 bytes
Desc: image008.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170907/afd93249/attachment-0002.png>
More information about the Equest-users
mailing list