[Equest-users] Issue with floors being offset in Wizard?

Nicholas Caton via Equest-users equest-users at lists.onebuilding.org
Fri Sep 15 06:46:20 PDT 2017


I’m sure there are multiple good approaches, but the one that works for me when I have fairly complex shell layouts is to do the following:

  1.  Before starting geometries in the wizards, make sure all your CAD references for multi-level buildings are origin-aligned.  If you were to copy one onto another using the origin as a reference point, the plans should should properly align.
  2.  After the first shell, be sure to specify the following in the first screen for every subsequent shell:
     *   Position this shell:  via Coordinates
     *   Tick the box for Exact Site Coordinates
     *   Leave X and Y at 0.0 (matching the first shell’s default)
     *   Provide a Z value as needed to ensure the shell is the right height from the ground.  Note that below grade floors for a given shell’s Z-coordinate will extend downward from that elevation.

[cid:image003.png at 01D32DFE.40EA33F0]


  1.  It’s never a bad idea to finish the wizards just to check your work in the 3D view - you can always hop back in to make corrections!

For reference, in the event you’re ever well into detailed edits, and wish you made a different decision, these inputs are basically replicated as FLOOR geometries.  You can adjust/tweak them here and observe the results in the 3D view dynamically:
[cid:image004.png at 01D32DFF.16062C10]

I suspect that because you have an “alignment” step within the wizards, you might not have your CAD files pre-aligned as I’m recommending above.  If you already have a bunch of zones traced out I’d recommend just tweaking the floor’s X/Y coordinates post-wizards until it looks about right.  You could overlay your CAD files outside of eQuest to inform exactly how much of a shift is needed.

Hope that’s a bit helpful!

~Nick

[cid:image001.png at 01D32DFD.ABAB1C50]
Nick Caton, P.E., BEMP
  Senior Energy Engineer
  Regional Energy Engineering Manager
  Energy and Sustainability Services
  Schneider Electric

D  913.564.6361
M  785.410.3317
F  913.564.6380
E  nicholas.caton at schneider-electric.com<mailto:nicholas.caton at schneider-electric.com>

15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States

[cid:image002.png at 01D32DFD.ABAB1C50]



From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Michael Campbell via Equest-users
Sent: Thursday, September 14, 2017 10:17 AM
To: equest-users <equest-users at lists.onebuilding.org>
Subject: [Equest-users] Issue with floors being offset in Wizard?

Hello eQUEST Users,
I'm having an issue right now when drawing in the Wizard.
I am working on a multi-story building and I am trying to line each floor up correctly when drawing the shells.
I have selected to draw the floor directly above, and I align the CAD file with the background as it should be.
However, when moving on to the Detailed Mode, the floors are offset and I cannot get them back to the way they were.
Has anyone had this issue or know of a potential solution?
Thank you,
Mike Campbell

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170915/1db7431a/attachment-0003.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 255 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170915/1db7431a/attachment-0016.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 8477 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170915/1db7431a/attachment-0017.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: oledata.mso
Type: application/octet-stream
Size: 7126 bytes
Desc: oledata.mso
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170915/1db7431a/attachment-0004.obj>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 62474 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170915/1db7431a/attachment-0018.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 98507 bytes
Desc: image004.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170915/1db7431a/attachment-0019.png>


More information about the Equest-users mailing list