[Equest-users] Defining a different fuel unit
David Eldridge
DEldridge at grummanbutkus.com
Thu Oct 5 23:07:14 PDT 2017
Are the two fuels being combusted in the same process, or is “mine” something equivalent to a purchased steam where the client is only billed for the latent energy? If the issue could be traced to a difference in combustion efficiency maybe that can explain the difference (purchased fuel vs raw fuel) or narrow down the equipment efficiency that may be varying between runs.
David
Sent from my iPad
On Oct 5, 2017, at 9:02 PM, Jones, Christopher via Equest-users <equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>> wrote:
I am trying to create a different natural gas unit. Call it “mine”? I define the Btu/unit in the new fuel meter. I assign the new fuel meter to the Air-side and Water-Side equipment. Then I compare the number of fuel units (eQuest doesn’t provide a way to change “Therms” in the ES-D report – that I could find – I didn’t review the DOE2 manual to see if it is possible). I calculate the ratio of Btu/unit between “Therm” and “mine”. I would expect that ratio to be the same as the ratio of units consumed between the two simulation runs. But this, somewhat poorly organized, table demonstrates my confusion:
ES-D "Therms"
Meter Btu/unit
ES-D Cost
mine
37948
35,724
$26,230
therm
15360
100,000
$10,617
ratio
2.47
2.80
2.47
Christopher R. Jones, P.Eng.
Technical Specialist
Sustainability & Energy
<image001.png>
T +1 416-644-0252
2300 Yonge Street, Suite 2300
Toronto, ON M4P 1E4 Canada
wsp.com
Please consider the environment before printing...
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Bishop, Bill via Equest-users
Sent: Wednesday, October 04, 2017 2:32 PM
To: Jeff Ross-Bain <jeff at rbgb.com<mailto:jeff at rbgb.com>>
Cc: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] DOAS and system HP
Jeff,
There are a number of workarounds for modeling DOAS units in eQUEST. The latest eQUEST beta version can run DOE-2.3 which has explicit options for modeling DOAS systems. A single DOAS can serve multiple other systems and be configured to supply the zones directly or to connect to the mixed air, as in your WSHP case. I don’t have much experience with it but it looks promising.
For fan power, it sounds like you have sized the DOAS already, so the 20HP supply and 7.5HP return fan power (or better yet, the BHP for the fan selections) should be entered via some combination of inputs instead of letting the system(s) be autosized. If you specify HVAC-SUPPLY/RETURN for ERV-FANS, then any fan power entered in the Heat Recovery 2 tab inputs will be added to the fan power entered for the system SUPPLY-KW/FLOW or SUPPLY-STATIC. The fan power penalty for the ERV section appears in the ERV Energy Recovery Summary reports. I would also look at the SV-A and SS-H reports for the systems in question. You could multiply the fan hours reported in the SS-L report by the DOAS fan power to see if the reported energy makes sense.
Regards,
~Bill
William Bishop, PE, BEMP, BEAP, CEM, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer
<image005.jpg> <image006.jpg>
134 South Fitzhugh Street Rochester, NY 14608
T: (585) 698-1956 F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com> www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
<image007.png>Carbon Fee and Dividend - simple, effective, and market-based.
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Jeff Ross-Bain via Equest-users
Sent: Wednesday, October 04, 2017 11:54 AM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] DOAS and system HP
Dear eQuest Experts,
I have a nagging issue that I hope someone can clarify. It has to do with DOAS units and fan motor HP.
We have a DOAS unit that supplies all outside air (OA) to a battery of WSHP units. In preparing the model, I used the “dummy zone” approach, conditioned the air, and all of that air is then the source of OA to the WSHPs. By the way, in this system, a portion of the return air from the WSHPs enters the DOAS.
The question is how is the actual DOAS unit HP modeled? This unit is 20HP supply and 7.5HP return (exhaust). The dummy zone HP auto sized is much less than the actual. However, if I input actual (i.e. kW/cfm), the energy use soars.
Am I missing something? I wonder if the size of the dummy zone matters, or if some of the fan power is included in the WSHP and exhaust systems…
Thanks,
Jeff Ross-Bain, BEMP, LEED Fellow
President
404-220-8955
www.rbgb.com<http://www.rbgb.com/>
Build Green. Save Time. Save Money.
________________________________
NOTICE: This communication and any attachments ("this message") may contain information which is privileged, confidential, proprietary or otherwise subject to restricted disclosure under applicable law. This message is for the sole use of the intended recipient(s). Any unauthorized use, disclosure, viewing, copying, alteration, dissemination or distribution of, or reliance on, this message is strictly prohibited. If you have received this message in error, or you are not an authorized or intended recipient, please notify the sender immediately by replying to this message, delete this message and all copies from your e-mail system and destroy any printed copies. You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSP's electronic communications policy, please consult our Anti-Spam Commitment at www.wsp.com/casl<http://www.wsp.com/casl>. For any concern or if you believe you should not be receiving this message, please forward this message to caslcompliance at wsp.com<mailto:caslcompliance at wsp.com> so that we can promptly address your request. Note that not all messages sent by WSP qualify as commercial electronic messages.
AVIS : Ce message, incluant tout fichier l'accompagnant (« le message »), peut contenir des renseignements ou de l'information privilégiés, confidentiels, propriétaires ou à divulgation restreinte en vertu de la loi. Ce message est destiné à l'usage exclusif du/des destinataire(s) voulu(s). Toute utilisation non permise, divulgation, lecture, reproduction, modification, diffusion ou distribution est interdite. Si vous avez reçu ce message par erreur, ou que vous n'êtes pas un destinataire autorisé ou voulu, veuillez en aviser l'expéditeur immédiatement et détruire le message et toute copie électronique ou imprimée. Vous recevez cette communication car vous faites partie des contacts de WSP. Si vous avez des questions concernant la politique de communications électroniques de WSP, veuillez consulter notre Engagement anti-pourriel au www.wsp.com/lcap<http://www.wsp.com/lcap>. Pour toute question ou si vous croyez que vous ne devriez pas recevoir ce message, prière de le transférer au conformitelcap at wsp.com<mailto:conformitelcap at wsp.com> afin que nous puissions rapidement traiter votre demande. Notez que ce ne sont pas tous les messages transmis par WSP qui constituent des messages electroniques commerciaux.
-LAEmHhHzdJzBlTWfa4Hgs7pbKl
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20171006/e2df3316/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 25844 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20171006/e2df3316/attachment-0008.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.jpg
Type: image/jpeg
Size: 1240 bytes
Desc: image005.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20171006/e2df3316/attachment-0008.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.jpg
Type: image/jpeg
Size: 1311 bytes
Desc: image006.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20171006/e2df3316/attachment-0009.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image007.png
Type: image/png
Size: 2851 bytes
Desc: image007.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20171006/e2df3316/attachment-0009.png>
More information about the Equest-users
mailing list