Are the two fuels being combusted in the same process, or is “mine” something equivalent to a purchased steam where the client is only billed for the latent energy? If the issue could be traced to a difference in combustion efficiency maybe that can explain
the difference (purchased fuel vs raw fuel) or narrow down the equipment efficiency that may be varying between runs.
<div><br>
</div>
<div>David</div>
<div>
<div>
<div id="AppleMailSignature">Sent from my iPad</div>
<div><br>
On Oct 5, 2017, at 9:02 PM, Jones, Christopher via Equest-users <<a href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a>> wrote:<br>
<br>
</div>
<blockquote type="cite">
<div>
<meta name="Generator" content="Microsoft Word 15 (filtered medium)">
<!--[if !mso]><style>v\:* {behavior:url(#default#VML);}
o\:* {behavior:url(#default#VML);}
w\:* {behavior:url(#default#VML);}
.shape {behavior:url(#default#VML);}
</style><![endif]--><style><!--
/* Font Definitions */
@font-face
{font-family:"Cambria Math";
panose-1:2 4 5 3 5 4 6 3 2 4;}
@font-face
{font-family:Calibri;
panose-1:2 15 5 2 2 2 4 3 2 4;}
@font-face
{font-family:"Franklin Gothic Medium";
panose-1:2 11 6 3 2 1 2 2 2 4;}
@font-face
{font-family:"Century Gothic";
panose-1:2 11 5 2 2 2 2 2 2 4;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
{margin:0in;
margin-bottom:.0001pt;
font-size:11.0pt;
font-family:"Calibri",sans-serif;}
a:link, span.MsoHyperlink
{mso-style-priority:99;
color:#0563C1;
text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
{mso-style-priority:99;
color:#954F72;
text-decoration:underline;}
span.EmailStyle17
{mso-style-type:personal;
font-family:"Calibri",sans-serif;
color:windowtext;}
span.EmailStyle18
{mso-style-type:personal;
font-family:"Calibri",sans-serif;
color:#1F497D;}
span.EmailStyle19
{mso-style-type:personal-reply;
font-family:"Calibri",sans-serif;
color:#1F497D;}
.MsoChpDefault
{mso-style-type:export-only;
font-size:10.0pt;}
@page WordSection1
{size:8.5in 11.0in;
margin:1.0in 1.0in 1.0in 1.0in;}
div.WordSection1
{page:WordSection1;}
--></style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
<div class="WordSection1">
<p class="MsoNormal"><span style="color:#1F497D">I am trying to create a different natural gas unit. Call it “mine”? I define the Btu/unit in the new fuel meter. I assign the new fuel meter to the Air-side and Water-Side equipment. Then I compare the number
of fuel units (eQuest doesn’t provide a way to change “Therms” in the ES-D report – that I could find – I didn’t review the DOE2 manual to see if it is possible). I calculate the ratio of Btu/unit between “Therm” and “mine”. I would expect that ratio to be
the same as the ratio of units consumed between the two simulation runs. But this, somewhat poorly organized, table demonstrates my confusion:<o:p></o:p></span></p>
<p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Times New Roman",serif"><o:p></o:p></span></p>
<table class="MsoTableGrid" border="1" cellspacing="0" cellpadding="0" width="0" style="width:258.0pt;border-collapse:collapse;border:none">
<tbody>
<tr style="height:15.0pt">
<td width="64" nowrap="" valign="top" style="width:48.0pt;border:solid windowtext 1.0pt;padding:0in 5.4pt 0in 5.4pt;height:15.0pt">
<p class="MsoNormal"><b><span style="color:#1F497D"> <o:p></o:p></span></b></p>
</td>
<td width="103" nowrap="" valign="top" style="width:77.0pt;border:solid windowtext 1.0pt;border-left:none;padding:0in 5.4pt 0in 5.4pt;height:15.0pt">
<p class="MsoNormal"><b><span style="color:#1F497D">ES-D "Therms"<o:p></o:p></span></b></p>
</td>
<td width="103" nowrap="" valign="top" style="width:77.0pt;border:solid windowtext 1.0pt;border-left:none;padding:0in 5.4pt 0in 5.4pt;height:15.0pt">
<p class="MsoNormal"><b><span style="color:#1F497D">Meter Btu/unit<o:p></o:p></span></b></p>
</td>
<td width="75" nowrap="" valign="top" style="width:56.0pt;border:solid windowtext 1.0pt;border-left:none;padding:0in 5.4pt 0in 5.4pt;height:15.0pt">
<p class="MsoNormal"><b><span style="color:#1F497D">ES-D Cost<o:p></o:p></span></b></p>
</td>
</tr>
<tr style="height:12.75pt">
<td width="64" nowrap="" valign="top" style="width:48.0pt;border:solid windowtext 1.0pt;border-top:none;padding:0in 5.4pt 0in 5.4pt;height:12.75pt">
<p class="MsoNormal"><b><span style="color:#1F497D">mine<o:p></o:p></span></b></p>
</td>
<td width="103" nowrap="" valign="top" style="width:77.0pt;border-top:none;border-left:none;border-bottom:solid windowtext 1.0pt;border-right:solid windowtext 1.0pt;padding:0in 5.4pt 0in 5.4pt;height:12.75pt">
<p class="MsoNormal"><span style="color:#1F497D">37948<o:p></o:p></span></p>
</td>
<td width="103" nowrap="" valign="top" style="width:77.0pt;border-top:none;border-left:none;border-bottom:solid windowtext 1.0pt;border-right:solid windowtext 1.0pt;padding:0in 5.4pt 0in 5.4pt;height:12.75pt">
<p class="MsoNormal"><span style="color:#1F497D">35,724<o:p></o:p></span></p>
</td>
<td width="75" nowrap="" valign="top" style="width:56.0pt;border-top:none;border-left:none;border-bottom:solid windowtext 1.0pt;border-right:solid windowtext 1.0pt;padding:0in 5.4pt 0in 5.4pt;height:12.75pt">
<p class="MsoNormal"><span style="color:#1F497D">$26,230<o:p></o:p></span></p>
</td>
</tr>
<tr style="height:12.75pt">
<td width="64" nowrap="" valign="top" style="width:48.0pt;border:solid windowtext 1.0pt;border-top:none;padding:0in 5.4pt 0in 5.4pt;height:12.75pt">
<p class="MsoNormal"><b><span style="color:#1F497D">therm<o:p></o:p></span></b></p>
</td>
<td width="103" nowrap="" valign="top" style="width:77.0pt;border-top:none;border-left:none;border-bottom:solid windowtext 1.0pt;border-right:solid windowtext 1.0pt;padding:0in 5.4pt 0in 5.4pt;height:12.75pt">
<p class="MsoNormal"><span style="color:#1F497D">15360<o:p></o:p></span></p>
</td>
<td width="103" nowrap="" valign="top" style="width:77.0pt;border-top:none;border-left:none;border-bottom:solid windowtext 1.0pt;border-right:solid windowtext 1.0pt;padding:0in 5.4pt 0in 5.4pt;height:12.75pt">
<p class="MsoNormal"><span style="color:#1F497D">100,000<o:p></o:p></span></p>
</td>
<td width="75" nowrap="" valign="top" style="width:56.0pt;border-top:none;border-left:none;border-bottom:solid windowtext 1.0pt;border-right:solid windowtext 1.0pt;padding:0in 5.4pt 0in 5.4pt;height:12.75pt">
<p class="MsoNormal"><span style="color:#1F497D">$10,617<o:p></o:p></span></p>
</td>
</tr>
<tr style="height:12.75pt">
<td width="64" nowrap="" valign="top" style="width:48.0pt;border:solid windowtext 1.0pt;border-top:none;padding:0in 5.4pt 0in 5.4pt;height:12.75pt">
<p class="MsoNormal"><b><span style="color:#1F497D">ratio<o:p></o:p></span></b></p>
</td>
<td width="103" nowrap="" valign="top" style="width:77.0pt;border-top:none;border-left:none;border-bottom:solid windowtext 1.0pt;border-right:solid windowtext 1.0pt;padding:0in 5.4pt 0in 5.4pt;height:12.75pt">
<p class="MsoNormal"><span style="color:#1F497D">2.47<o:p></o:p></span></p>
</td>
<td width="103" nowrap="" valign="top" style="width:77.0pt;border-top:none;border-left:none;border-bottom:solid windowtext 1.0pt;border-right:solid windowtext 1.0pt;padding:0in 5.4pt 0in 5.4pt;height:12.75pt">
<p class="MsoNormal"><span style="color:#1F497D">2.80<o:p></o:p></span></p>
</td>
<td width="75" nowrap="" valign="top" style="width:56.0pt;border-top:none;border-left:none;border-bottom:solid windowtext 1.0pt;border-right:solid windowtext 1.0pt;padding:0in 5.4pt 0in 5.4pt;height:12.75pt">
<p class="MsoNormal"><span style="color:#1F497D">2.47<o:p></o:p></span></p>
</td>
</tr>
</tbody>
</table>
<p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
<p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
<div>
<p class="MsoNormal"><b><span style="font-size:6.0pt;color:#1F497D;mso-fareast-language:FR"><o:p> </o:p></span></b></p>
<p class="MsoNormal"><b><span lang="EN-GB" style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#1F497D;mso-fareast-language:FR">Christopher R. Jones</span></b><span lang="EN-GB" style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#1F497D;mso-fareast-language:FR">,
P.Eng.<o:p></o:p></span></p>
<p class="MsoNormal"><span lang="EN-GB" style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#1F497D;mso-fareast-language:FR">Technical Specialist<o:p></o:p></span></p>
<p class="MsoNormal"><span lang="EN-GB" style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#1F497D;mso-fareast-language:FR">Sustainability & Energy<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#1F497D;mso-fareast-language:FR"><o:p> </o:p></span></p>
<p class="MsoNormal"><span style="color:#1F497D"><image001.png></span><span style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#1F497D;mso-fareast-language:FR"><o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#1F497D;mso-fareast-language:FR">T +1 416-644-0252<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#1F497D;mso-fareast-language:FR"><o:p> </o:p></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#1F497D;mso-fareast-language:FR">2300 Yonge Street, Suite 2300<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#1F497D;mso-fareast-language:FR">Toronto, ON M4P 1E4 Canada</span><span lang="EN-GB" style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#1F497D;mso-fareast-language:FR"><br>
<br>
</span><span style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#1F497D;mso-fareast-language:FR"><o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#1F497D;mso-fareast-language:EN-CA"><a href="wsp.com">wsp.com</a><o:p></o:p></span></p>
<p class="MsoNormal"><u><span lang="EN-CA" style="color:blue;mso-fareast-language:EN-CA"><o:p><span style="text-decoration:none"> </span></o:p></span></u></p>
<p class="MsoNormal" style="text-autospace:none"><b><span style="color:#7F7F7F;mso-fareast-language:FR"><o:p> </o:p></span></b></p>
<p class="MsoNormal" style="text-autospace:none"><i><span style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#6EA900;mso-fareast-language:FR">Please consider the environment before printing...<o:p></o:p></span></i></p>
<p class="MsoNormal"><span lang="EN-CA" style="color:#1F497D"><o:p> </o:p></span></p>
</div>
<p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
<div>
<div style="border:none;border-top:solid #E1E1E1 1.0pt;padding:3.0pt 0in 0in 0in">
<p class="MsoNormal"><b>From:</b> Equest-users [<a href="mailto:equest-users-bounces@lists.onebuilding.org">mailto:equest-users-bounces@lists.onebuilding.org</a>]
<b>On Behalf Of </b>Bishop, Bill via Equest-users<br>
<b>Sent:</b> Wednesday, October 04, 2017 2:32 PM<br>
<b>To:</b> Jeff Ross-Bain <<a href="mailto:jeff@rbgb.com">jeff@rbgb.com</a>><br>
<b>Cc:</b> <a href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
<b>Subject:</b> Re: [Equest-users] DOAS and system HP<o:p></o:p></p>
</div>
</div>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal"><span style="color:#1F497D">Jeff,<o:p></o:p></span></p>
<p class="MsoNormal"><span style="color:#1F497D">There are a number of workarounds for modeling DOAS units in eQUEST. The latest eQUEST beta version can run DOE-2.3 which has explicit options for modeling DOAS systems. A single DOAS can serve multiple other
systems and be configured to supply the zones directly or to connect to the mixed air, as in your WSHP case. I don’t have much experience with it but it looks promising.<o:p></o:p></span></p>
<p class="MsoNormal"><span style="color:#1F497D">For fan power, it sounds like you have sized the DOAS already, so the 20HP supply and 7.5HP return fan power (or better yet, the BHP for the fan selections) should be entered via some combination of inputs instead
of letting the system(s) be autosized. If you specify HVAC-SUPPLY/RETURN for ERV-FANS, then any fan power entered in the Heat Recovery 2 tab inputs will be added to the fan power entered for the system SUPPLY-KW/FLOW or SUPPLY-STATIC. The fan power penalty
for the ERV section appears in the ERV Energy Recovery Summary reports. I would also look at the SV-A and SS-H reports for the systems in question. You could multiply the fan hours reported in the SS-L report by the DOAS fan power to see if the reported energy
makes sense.<o:p></o:p></span></p>
<p class="MsoNormal"><span style="color:#1F497D">Regards,<o:p></o:p></span></p>
<p class="MsoNormal"><span style="color:#1F497D">~Bill<o:p></o:p></span></p>
<p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
<div>
<p class="MsoNormal"><b><span style="font-size:10.0pt;font-family:"Franklin Gothic Medium",sans-serif;color:black">William Bishop, PE, BEMP, BEAP, CEM, LEED AP
</span></b><b><span style="font-size:10.0pt;font-family:"Franklin Gothic Medium",sans-serif;color:#006600">|</span></b><b><span style="font-size:10.0pt;font-family:"Franklin Gothic Medium",sans-serif;color:black"> Pathfinder Engineers & Architects LLP<o:p></o:p></span></b></p>
<table class="MsoNormalTable" border="0" cellspacing="0" cellpadding="0" width="0" style="width:394.8pt;border-collapse:collapse">
<tbody>
<tr style="height:13.45pt">
<td width="345" style="width:258.45pt;padding:0in 5.4pt 0in 5.4pt;height:13.45pt">
<p class="MsoNormal" style="line-height:105%"><b><span style="font-size:9.0pt;line-height:105%;font-family:"Arial",sans-serif;color:black">Senior Energy Engineer<o:p></o:p></span></b></p>
</td>
<td width="182" rowspan="6" style="width:136.35pt;padding:0in 5.4pt 0in 5.4pt;height:13.45pt">
<p class="MsoNormal" style="line-height:105%"><span style="font-size:9.0pt;line-height:105%;font-family:"Arial",sans-serif;color:black"><image005.jpg> <image006.jpg><o:p></o:p></span></p>
</td>
</tr>
<tr style="height:4.55pt">
<td width="345" valign="top" style="width:258.45pt;padding:0in 5.4pt 0in 5.4pt;height:4.55pt">
<p class="MsoNormal" style="line-height:105%"><span style="font-size:5.0pt;line-height:105%;font-family:"Arial",sans-serif;color:black"><o:p> </o:p></span></p>
</td>
</tr>
<tr style="height:9.8pt">
<td width="345" nowrap="" valign="bottom" style="width:258.45pt;padding:0in 5.4pt 0in 5.4pt;height:9.8pt">
<p class="MsoNormal" style="line-height:105%"><span style="font-size:9.0pt;line-height:105%;font-family:"Arial",sans-serif;color:#1F497D">134 South Fitzhugh Street</span><span style="font-size:9.0pt;line-height:105%;color:#1F497D">
</span><span style="font-size:9.0pt;line-height:105%;font-family:"Arial",sans-serif;color:#1F497D">Rochester, NY 14608<o:p></o:p></span></p>
</td>
</tr>
<tr style="height:12.4pt">
<td width="345" valign="top" style="width:258.45pt;padding:0in 5.4pt 0in 5.4pt;height:12.4pt">
<p class="MsoNormal" style="line-height:105%"><b><i><span style="font-size:9.0pt;line-height:105%;font-family:"Arial",sans-serif;color:#002060">T: (585) 698-1956</span><span style="color:#002060">
</span></i></b><span style="color:#1F497D"> </span><span style="font-size:9.0pt;line-height:105%;font-family:"Arial",sans-serif;color:#1F497D">F: (585) 325-6005</span><span style="font-size:9.0pt;line-height:105%;font-family:"Arial",sans-serif;color:black"><o:p></o:p></span></p>
</td>
</tr>
<tr style="height:9.8pt">
<td width="345" valign="top" style="width:258.45pt;padding:0in 5.4pt 0in 5.4pt;height:9.8pt">
<p class="MsoNormal" style="line-height:105%"><span style="color:#1F497D"><a href="mailto:wbishop@pathfinder-ea.com"><span style="font-size:9.0pt;line-height:105%;font-family:"Arial",sans-serif;color:blue">bbishop@pathfinder-ea.com</span></a></span><span style="font-size:9.0pt;line-height:105%;font-family:"Arial",sans-serif;color:black">
</span><span style="color:#1F497D"><a href="http://www.pathfinder-ea.com/"><span style="font-size:9.0pt;line-height:105%;font-family:"Arial",sans-serif;color:blue">www.pathfinder-ea.com</span></a><o:p></o:p></span></p>
</td>
</tr>
<tr style="height:24.6pt">
<td width="345" valign="top" style="width:258.45pt;padding:0in 5.4pt 0in 5.4pt;height:24.6pt">
<p class="MsoNormal" style="margin-top:3.0pt;line-height:105%"><span style="color:#1F497D"><image007.png></span><span style="font-size:7.5pt;line-height:105%;color:#00B0F0">Carbon Fee and Dividend - simple, effective, and market-based.</span><span style="color:#1F497D"><o:p></o:p></span></p>
</td>
</tr>
</tbody>
</table>
</div>
<p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
<div>
<div style="border:none;border-top:solid #E1E1E1 1.0pt;padding:3.0pt 0in 0in 0in">
<p class="MsoNormal"><b>From:</b> Equest-users [<a href="mailto:equest-users-bounces@lists.onebuilding.org">mailto:equest-users-bounces@lists.onebuilding.org</a>]
<b>On Behalf Of </b>Jeff Ross-Bain via Equest-users<br>
<b>Sent:</b> Wednesday, October 04, 2017 11:54 AM<br>
<b>To:</b> <a href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
<b>Subject:</b> [Equest-users] DOAS and system HP<o:p></o:p></p>
</div>
</div>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal">Dear eQuest Experts,<o:p></o:p></p>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal">I have a nagging issue that I hope someone can clarify. It has to do with DOAS units and fan motor HP.<o:p></o:p></p>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal">We have a DOAS unit that supplies all outside air (OA) to a battery of WSHP units. In preparing the model, I used the “dummy zone” approach, conditioned the air, and all of that air is then the source of OA to the WSHPs. By the way, in
this system, a portion of the return air from the WSHPs enters the DOAS.<o:p></o:p></p>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal">The question is how is the actual DOAS unit HP modeled? This unit is 20HP supply and 7.5HP return (exhaust). The dummy zone HP auto sized is much less than the actual. However, if I input actual (i.e. kW/cfm), the energy use soars.
<o:p></o:p></p>
<p class="MsoNormal">Am I missing something? I wonder if the size of the dummy zone matters, or if some of the fan power is included in the WSHP and exhaust systems…<o:p></o:p></p>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal">Thanks,<o:p></o:p></p>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal"><b><span style="font-size:8.0pt;font-family:"Century Gothic",sans-serif;color:#006E78">Jeff Ross-Bain, BEMP, LEED Fellow<o:p></o:p></span></b></p>
<p class="MsoNormal"><span style="font-size:7.5pt;font-family:"Century Gothic",sans-serif;color:#535053">President<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size:7.5pt;font-family:"Century Gothic",sans-serif;color:#535053">404-220-8955<br>
</span><b><span style="font-size:7.5pt;font-family:"Century Gothic",sans-serif;color:#006E78"><a href="http://www.rbgb.com/">www.rbgb.com</a></span></b><span style="font-size:7.5pt;font-family:"Century Gothic",sans-serif;color:#535053"><br>
<br>
</span><span style="font-size:7.5pt;font-family:"Century Gothic",sans-serif;color:#006E78">Build Green. Save Time. Save Money.<o:p></o:p></span></p>
<p class="MsoNormal"><b><span style="font-size:7.5pt;font-family:"Century Gothic",sans-serif;color:#006E78"><o:p> </o:p></span></b></p>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal"><o:p> </o:p></p>
</div>
<br>
<hr>
<font face="Arial" color="Gray" size="1"><br>
<br>
NOTICE: This communication and any attachments ("this message") may contain information which is privileged, confidential, proprietary or otherwise subject to restricted disclosure under applicable law. This message is for the sole use of the intended recipient(s).
Any unauthorized use, disclosure, viewing, copying, alteration, dissemination or distribution of, or reliance on, this message is strictly prohibited. If you have received this message in error, or you are not an authorized or intended recipient, please notify
the sender immediately by replying to this message, delete this message and all copies from your e-mail system and destroy any printed copies. You are receiving this communication because you are listed as a current WSP contact. Should you have any questions
regarding WSP's electronic communications policy, please consult our Anti-Spam Commitment at
<a href="http://www.wsp.com/casl">www.wsp.com/casl</a>. For any concern or if you believe you should not be receiving this message, please forward this message to
<a href="mailto:caslcompliance@wsp.com">caslcompliance@wsp.com</a> so that we can promptly address your request. Note that not all messages sent by WSP qualify as commercial electronic messages.
<br>
<br>
AVIS : Ce message, incluant tout fichier l'accompagnant (« le message »), peut contenir des renseignements ou de l'information privilégiés, confidentiels, propriétaires ou à divulgation restreinte en vertu de la loi. Ce message est destiné à l'usage exclusif
du/des destinataire(s) voulu(s). Toute utilisation non permise, divulgation, lecture, reproduction, modification, diffusion ou distribution est interdite. Si vous avez reçu ce message par erreur, ou que vous n'êtes pas un destinataire autorisé ou voulu, veuillez
en aviser l'expéditeur immédiatement et détruire le message et toute copie électronique ou imprimée. Vous recevez cette communication car vous faites partie des contacts de WSP. Si vous avez des questions concernant la politique de communications électroniques
de WSP, veuillez consulter notre Engagement anti-pourriel au <a href="http://www.wsp.com/lcap">
www.wsp.com/lcap</a>. Pour toute question ou si vous croyez que vous ne devriez pas recevoir ce message, prière de le transférer au
<a href="mailto:conformitelcap@wsp.com">conformitelcap@wsp.com</a> afin que nous puissions rapidement traiter votre demande. Notez que ce ne sont pas tous les messages transmis par WSP qui constituent des messages electroniques commerciaux.
<br>
</font><br>
<font face="Arial" color="WhiteSmoke" size="0.10"><br>
<br>
-LAEmHhHzdJzBlTWfa4Hgs7pbKl </font></div>
</blockquote>
<blockquote type="cite">
<div><span>_______________________________________________</span><br>
<span>Equest-users mailing list</span><br>
<span><a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a></span><br>
<span>To unsubscribe from this mailing list send a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">
EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a></span><br>
</div>
</blockquote>
</div>
</div>
</body>
</html>