[Equest-users] Costco warehouse model unmet heating load hours

Chris Baker via Equest-users equest-users at lists.onebuilding.org
Mon May 1 12:42:30 PDT 2017


Tim,

It sounds like the heating system is fighting the cooling system off and on  (but moreso during your HDD's resulting in underheated hours).  This can happen for a number of reasons.  It could have to do with either exhaust fan settings to the zone or schedules that are at odds with each other (or both).

We call it the "yoyo" effect (or at least I do).

How to approach this depends on how you are modeling OSA, whether or not you re modeling exhaust fans in the space and what other factors apply (HW coils, RH coils, etc).

I would also go back and check your reports because they always give away the culprit in instances like this.  Look for excessive heating and/or cooling loads in your zones.

The LS-A reports would be useful because the peak load summaries are zone-specific.

The zone air-side system will do it's best to maintain setpoint given the parameters you've specified.  If you try to input more heat by manual methods, the system will still try to cool the space more at the same time to maintain setpoint- resulting in even more competition between the heating/cooling sides of the system along with a lot more energy usage than you are intending.

However, this also hints that the cause of the problem is elsewhere.  Like Nick once told me - this is probably one of those cases where it's not an issue of "not enough heat" and more of a problem with too much heat AND too much cooling.

In the past, I've seen that checking OSA coming into the zone is useful along with ensuring any exhaust fans are being modeled with a schedule so that OSA coming in on the back-end doesn't ever exceed intended design specs.

Too much OSA isn't necessarily an issue that gives itself up right away in equest until the OSA temp gets to a point that your heating or cooling capacity isn't enough to heat or cool the space readily.  And if this is the case, your exhaust fans will always tie in to the equation somehow (if modeled).

Hope this helps.

Chris Baker
CCI Alliance of Companies
Fort Wainwright, Alaska
907-356-1681 (x105) office
907-750-4922 cell

From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Tim Burke via Equest-users
Sent: Friday, April 28, 2017 11:02 AM
To: equest-users at lists.onebuilding.org; equest-users at onebuilding.org
Subject: [Equest-users] Costco warehouse model unmet heating load hours

I have about 4 unmet heating load hours.  After tweaking things I have found that I can reduce it to 1 by increasing the internal equipment load and adjusting the schedule.  Then I tried increasing the heat capacity but that didn't help.  Why wouldn't increasing the heating capacity by double get rid of 1 heating load hour?  Makes no sense to me.

Tim Burke

T.E., Inc.
830 North Riverside Drive #200
Renton, WA. 98057
(425) 970-3753 Phone
(425) 970-3756 Fax
WWW.TEI-ENGINEERING.COM<http://www.tei-engineering.com/>
This message contains information that is confidential or privileged. The information is intended for the use of the individual or entity named above. If you are not the intended recipient, be aware that any disclosure, copying, distribution or use of the contents of this information is prohibited. If you have received this electronic transmission in error, please notify the sender and delete this message and any attachments


________________________________

CCI-Alliance Confidentiality notice: This message is intended only for the person to whom addressed in the text above and may contain privileged or confidential information. If you are not that person, any use of this message is prohibited. We request that you notify us by reply to this message, and then delete all copies of this message including any contained in your reply. Thank you.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170501/0d66795e/attachment-0005.htm>


More information about the Equest-users mailing list