[Equest-users] LEED Comment for FAN EFLH--help please
Keith Swartz via Equest-users
equest-users at lists.onebuilding.org
Fri Mar 31 06:22:37 PDT 2017
Pasha,
Are there envelope improvements to the proposed building that significantly reduce the need for overnight heating and cooling?
Keith Swartz, PE | Senior Energy Engineer
Seventhwave
608.210.7123 seventhwave.org
From: Pasha Korber-Gonzalez via Equest-users [mailto:equest-users at lists.onebuilding.org]
Sent: Thursday, March 30, 2017 2:52 PM
To: eQUEST Users List <equest-users at lists.onebuilding.org>
Subject: [Equest-users] LEED Comment for FAN EFLH--help please
Hello fellow eQuesters,
I'm sure we all get the standard LEED review comment regarding Fan equivalent full load hours (EFHL).
I received this one on my current project (elementary school in Ohio with heat recovery units.) I have confirmed that my fan schedules for both models are exactly the same. But I do have drastically different EFLH values for the baseline (over 3,000) and proposed (less than 1,500).
I have made changes in my models, but I cannot seem to get the proposed hours over 1,600 of run time.
QUESTION: Do any of you have any experience of suggesting to the LEED Reviewer that it is possible to have this significant of difference between the two models hvac systems AND how can I show justification for these run hours?? Any advice & suggestions are welcomed at this time.
Here is the LEED comment I received with highlighted notes:
. Table EAp2-5 of the form indicates that the equivalent full load hours for interior fans in the Proposed and Baseline model are 1,200 hours (57,951 kWh/48.31 kW) and 3,702 hours (130,702 kWh/35.31 kW), respectively; however, it is unclear if the HVAC fans are modeled as cycling to meet the cooling and heating loads of the building during unoccupied hours. Table G3.1.4 in the Proposed building column requires that HVAC fans that provide ventilation air in the Proposed model must be modeled as operating continuously during occupied hours and cycled to meet the cooling and heating loads of the building during unoccupied hours, unless one of the exceptions of Table G3.1.4 are met. In addition, Section G3.1.2.4 requires that supply and return fans reflected in the Baseline model must be modeled as operating continuously during occupied hours and cycled to meet the cooling and heating loads of the building during unoccupied hours,
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170331/679f8e68/attachment-0002.htm>
More information about the Equest-users
mailing list