[Equest-users] [Bldg-sim] Answers Re: Test your knowledge of simulation weather file formats Part 1: the DOE-2 *.BIN/*.BINM format

Joe Huang yjhuang at whiteboxtechnologies.com
Fri Dec 8 19:23:05 PST 2017


Julien,

When I first read your post, I had the wrong impression that the python script was 
disassembling (unpacking) the binary *.BINM file, which would be quite an achievement 
since I hadn't documented yet the packing procedure for the extra precision, nor have the 
original packing been explained anywhere but in the actual Fortran source code.

After looking at the python script, I then realized it was reading the ASCII dump of the 
weather file, which I've said had a embarrassing glitch in my unpacking :-)

The original packing/unpacking can be seen in the Fortran code of the fmtwth2.f and 
wthfmt2.f  programs that are part of the DOE-2 release package.  In DOE-2.2, the same two 
programs have been renamed as  MKAFT and PKAFT.  My additions can be seen in the Fortran 
code of the fmtwth2M.f and wthfmt2mleapyr.f but please be warned that I need to figure out 
the mysterious extra line I found that was throwing off the solar radiation in November 
and December.  The source code for all 4 programs are attached, in case anyone wants to 
port them to python

Joe

Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 205A
Moraga CA 94556
yjhuang at whiteboxtechnologies.com
http://weather.whiteboxtechnologies.com for simulation-ready weather data
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"

On 12/8/2017 6:24 AM, Jones, Christopher wrote:
>
> Thank you Sir!
>
> **
>
> *Christopher R. Jones*, P.Eng.
>
> Technical Specialist
>
> Sustainability & Energy
>
> T +1 416-644-0252
>
> 2300 Yonge Street, Suite 2300
>
> Toronto, ON M4P 1E4 Canada
>
> wsp.com
>
> __
>
> **
>
> /Please consider the environment before printing.../
>
> *From:*Julien Marrec [mailto:julien.marrec at gmail.com]
> *Sent:* Friday, December 08, 2017 9:22 AM
> *To:* Jones, Christopher <Christopher.r.Jones at wsp.com>
> *Cc:* Joe Huang <yjhuang at whiteboxtechnologies.com>; EnergyPlus_Support 
> <EnergyPlus_Support at yahoogroups.com>; Javed Iqbal <eee.javed at gmail.com>; 
> eQUEST-users at onebuilding.org
> *Subject:* Re: [Bldg-sim] Answers Re: Test your knowledge of simulation weather file 
> formats Part 1: the DOE-2 *.BIN/*.BINM format
>
> Christopher,
>
> This is a jupyter notebook. See http://jupyter.org/ <http://jupyter.org/>.
>
> You can do "pip install jupyter" then start a server with "jupyter notebook" in a 
> terminal, navigate to the location of the ipynb file and open it up. Then you can just 
> run it there, cell by cell interactively (CTRL+ENTER to run a cell).
>
> This is **hugely** helpful in anything that has to do with data analysis, because it 
> allows for interactive exploring. I strongly suggest you try it out.
>
> Note that if you have installed a scientific python distro such as Anaconda, you should 
> already have it installed.
>
> You can also download this as a python file from the notebook, which I've done out of 
> convenience for you (see attached).
>
> Best,
>
> Julien
>
>
> --
> Julien Marrec, EBCP, BPI MFBA
> Owner at EffiBEM <http://www.effibem.com>
> T: +33 6 95 14 42 13
>
> LinkedIn (en <https://www.linkedin.com/in/julienmarrec>) /| /(fr 
> <https://fr.linkedin.com/in/julienmarrec/fr>) :
>
> 2017-12-08 14:26 GMT+01:00 Jones, Christopher <Christopher.r.Jones at wsp.com 
> <mailto:Christopher.r.Jones at wsp.com>>:
>
>     Julien,
>
>     Thank you for the Python code. One question – how do you download just the code
>     without the .png data in the file?
>
>     **
>
>     *Christopher R. Jones*, P.Eng.
>
>     Technical Specialist
>
>     Sustainability & Energy
>
>     T +1 416-644-0252 <tel:+1%20416-644-0252>
>
>     2300 Yonge Street, Suite 2300
>     <https://maps.google.com/?q=2300+Yonge+Street,+Suite+2300%0D+Toronto,+ON+M4P+1E4+Canada&entry=gmail&source=g>
>
>     Toronto, ON M4P 1E4 Canada
>     <https://maps.google.com/?q=2300+Yonge+Street,+Suite+2300%0D+Toronto,+ON+M4P+1E4+Canada&entry=gmail&source=g>
>
>     wsp.com <http://wsp.com>
>
>     **
>
>     /Please consider the environment before printing.../
>
>     *From:*Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org
>     <mailto:bldg-sim-bounces at lists.onebuilding.org>] *On Behalf Of *Julien Marrec via
>     Bldg-sim
>     *Sent:* Thursday, December 07, 2017 7:02 AM
>     *To:* Joe Huang <yjhuang at whiteboxtechnologies.com
>     <mailto:yjhuang at whiteboxtechnologies.com>>
>     *Cc:* EnergyPlus_Support <EnergyPlus_Support at yahoogroups.com
>     <mailto:EnergyPlus_Support at yahoogroups.com>>; Javed Iqbal <eee.javed at gmail.com
>     <mailto:eee.javed at gmail.com>>; eQUEST-users at onebuilding.org
>     <mailto:eQUEST-users at onebuilding.org>; BLDG-SIM <bldg-sim at lists.onebuilding.org
>     <mailto:bldg-sim at lists.onebuilding.org>>
>     *Subject:* Re: [Bldg-sim] Answers Re: Test your knowledge of simulation weather file
>     formats Part 1: the DOE-2 *.BIN/*.BINM format
>
>     Joe,
>
>     This was fun, thanks for putting it together, I'm looking forward to the next one.
>
>     I have to say that I'm impressed by Aaron's knowledge and level of detail, and it's
>     not the first time.
>
>     I've used Python to parse your hourly dump and visualize it, as well as comparing
>     with the Barrow EPW (converting your hourly dump to SI Units). I've posted that on
>     Github, where you can already look at the code + graphs since it's in a jupyter
>     notebook, but you could also download it and run it on your machine. My hope is that
>     I'll convert one or two members of this list to coding :)
>
>     For the record, the actual parsing of the hourly dump into a usable format
>     (pandas.DataFrame) took me about 5 minutes and 16 lines of code (it was a very
>     simple one though).
>     https://github.com/jmarrec/BINM_Challenge/blob/master/Analyse_BINM.ipynb
>
>     Cheers,
>
>     Julien
>
>
>     --
>     Julien Marrec, EBCP, BPI MFBA
>     Owner at EffiBEM <http://www.effibem.com>
>     T: +33 6 95 14 42 13 <tel:06%2095%2014%2042%2013>
>
>     LinkedIn (en <https://www.linkedin.com/in/julienmarrec>) /| /(fr
>     <https://fr.linkedin.com/in/julienmarrec/fr>) :
>
>     2017-12-07 10:40 GMT+01:00 Joe Huang <yjhuang at whiteboxtechnologies.com
>     <mailto:yjhuang at whiteboxtechnologies.com>>:
>
>         I got a total of five responses,  all of which are attached at the end of this
>         e-mail.  Although I was focusing on the FORMAT of the *.BIN weather file, most
>         of the respondents focused on the data instead, and to my chagrin more intensely
>         than I have, esp. Julien who pointed out an anomaly in the direct normal
>         radiation that made me gasp and go back into my file and processing procedures. 
>         Kudos to Julien for spotting that, but I'll explain what happened there
>         following his e-mail attached below.
>
>         The three answers I was seeking are:
>
>         (1) *The weather file is for a location above the Arctic Circle*, which would
>         make DOE-2.1E crash due to a bug in the shading calculation but not in DOE-2.2
>         which fixed this bug in 2004.  The point here is that this is a problem in
>         DOE-2.1E but NOT in the *.BIN format, except it might seem that way because the
>         DOE-2 weather packer also crashes because it uses the same shading routine to
>         generate the weather statistics.
>
>         (2) *The weather file is for a leap year with the output file showing Feb.
>         29th*.  I've heard many people say that DOE-2 weather files contain only 365
>         days, but that's absolutely not true.  The *.BIN format stores data for 12
>         months of 32 days each, or 384 days!  The reason that Feb. 29th never shows up
>         in a DOE-2 run is that the developers never bothered to reset the February day
>         count to 29 on leap years, even though DOE-2 calculates when that's the case. 
>         Now that more people are running DOE-2 with actual historical years, it's well
>         past time for this little fix to be implemented.
>
>         (3) *The weather file reports shows the weather parameters to an additional
>         decimal of precision*, i.e., temperatures are to the 0.1F, pressures to 0.01
>         inches of mercury, solar radiation to 0.1 Btu/sqft, and wind speeds to 0.1 mph. 
>         This required a modest change to the BIN format that I implemented as the *.BINM
>         (M for Modified) starting in 2011.  This leads to what I think is the most
>         fascinating part about the DOE-2 *.BIN format that was developed in the early
>         1980's when computer memory was very limited. Members of the original
>         development team (Ender Erdem and maybe Fred Buhl) came up with the strategy of
>         "packing" the data by converting all data to integers, pack four integers into
>         one big integer, and then store them in the file in binary form. By so doing the
>         *.BIN files are only 146K (70-80KB zipped), whereas other formats can be well
>         over 1MB (200+KB zipped). DOE-2 also uses the *.BIN format to improve execution
>         speed by not reading the data an hour at a time or 8760 ASCII reads, but by
>         reading 16 day chunks at a time or 24 binary reads  for the entire year (which
>         also explains why the *.BIN format contains 24x16 or 384 days).
>
>         So now let's look at how did our contestants do, listed in order of when I
>         received their answers:
>
>         Parag -  0 out of 3  (he looked almost entirely on the data, not on the format)
>
>         Julien -  1 out of 3 (he noticed the leap day, but also focused his attention on
>         the data and pointed out two problems that I will address following his e-mail 
>         below)
>
>         Aaron - 2 out of 3 (I was impressed that he knew about the packing and unpacking
>         process, but did not notice the leap year)
>
>         Javed -  0 out of 3 (but had a good question on why DNI (Direct Normal) is
>         larger than GHI (Global Horizontal) that I will answer following his e-mail below)
>
>         Nathan - 1 out of 3 (he also noticed the leap day, and had other questions that
>         I will answer following his e-mail below).
>
>         So, nobody noticed all three answers, but since it's the holiday season, I will
>         make them all winners and provide a historical year weather file of their
>         choosing. Just e-mail me if you're interested and tell me which one you want.
>
>         This has been an interesting and insightful experience for me.  I hope others
>         also found it entertaining and useful, as well.  I've learned that (1) think
>         twice before coming out with a flawed contest rule, (2) look over more times
>         whatever I put out on the Web.
>
>         (please be sure to read the contestant's submittals and my responses below)
>
>         Joe
>
>         Joe Huang
>
>         White Box Technologies, Inc.
>
>         346 Rheem Blvd., Suite 205A
>         <https://maps.google.com/?q=346+Rheem+Blvd.,+Suite+205A%0D+Moraga+CA+94556&entry=gmail&source=g>
>
>         Moraga CA 94556
>         <https://maps.google.com/?q=346+Rheem+Blvd.,+Suite+205A%0D+Moraga+CA+94556&entry=gmail&source=g>
>
>         yjhuang at whiteboxtechnologies.com <mailto:yjhuang at whiteboxtechnologies.com>
>
>         http://weather.whiteboxtechnologies.com  for simulation-ready weather data
>
>         (o) (925)388-0265
>
>         (c) (510)928-2683
>
>         "building energy simulations at your fingertips"
>
>         Attached e-mails  follow in the same order (only final e-mails shown)
>         -----------------------------------------------------------
>
>         On 12/5/2017 11:24 PM, Parag Rastogi wrote:
>
>             Hi Joe,
>
>               
>
>             Don't know anything about the DOE-2 platform, but here's my take on the meteorological "oddities". Thanks for organising this challenge - it's really cool!
>
>               
>
>             1. A large part of the year has zero sun while the other part has sun for 24 hours.
>
>             2. The humidity is _really_ high - the WBT and DBT are mostly within a degree of each other. Don’t know if DOE-2 has a problem with that?
>
>             3. In the summer months, the direct normal is sometimes larger than global solar. That is really odd!
>
>             4. I would not live here - Glasgow winters are bad enough.
>
>               
>
>             Parag
>
>         YJH answer:   Yes, I picked Barrow on purpose to show that the *.BIN format
>         still works for places above the Arctic Circle or below the Antarctic Circle. 
>         RH is generally very high in frigid climates because the cold air cannot hold
>         much moisture (that's why there's always frost in your refrigerators!).  The DNI
>         can often be greater than the GHI at low sun angles, since the DNI is calculated
>         normal to the sun, while the GHI is calculated for a flat horizontal plane. 
>         Yes, stay in Glasgow or at least don't go to Barrow in place of Glasgow.
>
>         On 12/6/2017 6:35 AM, Julien Marrec wrote:
>
>             Hi Joe,
>
>             Replying off the mailing list, since it would kinda beat the point of "first
>             5 to find the error" otherwise.
>
>             1. There is a 29th of February, but 1912 was indeed a leap year, so I'm not
>             sure whether that qualifies for a bug (can't remember how eQuest/DOE deal
>             with leap year weather files).
>
>             2. There is an unsual peak of Global Solar radiation mid November (11 to
>             18th) while the Direct Normal stays at zero. The peak has values at 400
>             BTU-HR/SQFT while the max is 250 for the rest of the year. 400 means 1250
>             Wh/m2, which is just short of what the Extraterrestrial Direct Normal Solar
>             Radiation is.
>
>             In IP units:
>
>             Images intégrées 1
>
>             I don't see any problem with the Atmospheric pressure, not the relative
>             humidity I computed with Db, Wb and Atm. Wetbulb and drybulb are where I
>             expect them for this location (checked against the EPW file for the same
>             location too).
>
>             So I'm not sure what's the 3rd problem, I'd say that it's probably not a
>             good idea to live there unless you *really* like cold weather?
>
>             Best,
>
>             Julien
>
>             --
>
>             Julien Marrec, EBCP, BPI MFBA
>             Owner at EffiBEM <http://www.effibem.com>
>             T: +33 6 95 14 42 13 <tel:06%2095%2014%2042%2013>
>
>         YJH answer: I was embarrassed that you noticed the input echo has 1912 instead
>         of 2012, which was because DOE-2.1E was not Y2K compliant, so I had to set the
>         year to 1912 in order for DOE-2.1E to run.  I was further more astonished to see
>         the wierd spike of GHI in November, which wasn't there in the actual weather
>         file (see below).
>
>
>         Since DOE-2.1E can't run with this weather file, I used a version that I
>         modified that took care of the high latitude problem as well as adding the extra
>         precision.  When I checked the Fortran source code, I found this extra line
>         (<<<)  that I have no memory of ever inserting nor why I did so (sound like a
>         politician, don't I ? :-) ).
>               DO 500 I=1,14
>               CALC(I) = FLOAT(IWTH(I))*XMASK(I,2) + XMASK(I,1)
>               IF (I.LE.2) CALC(I)=CALC(I)+IWTH2(I)/10.
>               IF (I.EQ.11.OR.I.EQ.12) CALC(I)=CALC(I)+IWTH2(I-8)/10. <<< ???
>           500 CONTINUE
>         So, if you believe my story, this spike in GHI was the result of my unpacking
>         routine and not in the weather file itself.  A curious thing with the solar in
>         such Arctic locations is that the GHI is above 0 for all hours over two months 
>         (see central bottom of the left plot), indicating  the proverbial midnight sun
>         during the summer.
>
>         On 12/6/2017 9:05 AM, Aaron Powers wrote:
>
>             Hey Joe,
>
>             Here's what I could find.  It's really 2 things since the first 2 and last 2
>             are related.
>
>             1. Normal DOE2 binary weather files are made up of 24 records of 6208 bytes
>             each.  So each file is roughly 145 kB.  Your file is 182 kB, so each of the
>             24 records is 7744 bytes in length.  I'm not sure what you have in the extra
>             bytes, but the first 6208 bytes of each record is exactly as you would
>             expect in a DOE2 packed file.  So I am able to read the .bin file by just
>             ignoring the bytes after 6208 of each record.
>
>             2. You have more precision for each data point.  I'm guessing this must be
>             tied up to the extra bytes in each record.  For example, the drybulb,
>             wetbulb, and pressure are usually packed into a single integer value.  The
>             first and last 4 bits of the integer are junk due to the way Fortran writes
>             binary data.  The atmospheric pressure takes up 15 bits and the drybulb and
>             wetbulb take up 8 bits each.  After encryption, this allows the drybulb and
>             wetbulb to be stored with 0 decimal places and the pressure with 1 decimal
>             place. Similarly, the direct normal and global horizontal are usually stored
>             with 0 decimal places. Your output file shows a higher precision for each of
>             these data points.  Again, I'm guessing that this extra precision is in the
>             extra bytes in each record.
>
>             3. Since Barrow is above the Arctic Circle, it gets the midnight sun and
>             polar night.
>
>             4. Related to previous, in the peak of summer, radiation has very little
>             diffuse component and during winter is almost all diffuse (when it exists).
>
>             Aaron
>
>         YJH answer: You're completely correct in all your suppositions, Sherlock Holmes
>         !  What I've done is to add another array of 384, each containing the extra
>         precision for the two temperatures, pressure, wind speed, and the two solar
>         irradiances.  It was my former colleague at LBNL Ender Erdem who assured me that
>         in a binary read, this extra integer would be ignored, thereby guaranteeing
>         compatibility between the *.BIN and *.BINM formats. However, once the extra read
>         is added, there has to be a flag telling DOE-2 NOT to do that for the older
>         *.BIN format.  That's the main reason why I haven't pushed very hard on  this.
>
>         On 12/6/2017 9:18 AM, Javed Iqbal wrote:
>
>             Dear Sir Joe,
>
>             I am able to find something though NOT all which looks to me unusual and
>             hence reporting here.
>
>             1) The following screenshot for *_22nd April_* shows that Direct Normal is
>             greater than the Global solar. As per my limited knowledge in this
>             direction, usually Direct Normal Solar can be greater than Global solar
>             (Direct+diffuse) or GHI during certain periods such as morning or afternoon
>             hours. Whereas, the hourly report shows Direct Normal Solar is always higher
>             (~8-10 times) than the Global Solar. If this is one of the acceptable
>             discrepancy than there are many such instances could be found in in the
>             hourly weather file.
>
>             Inline image 1
>
>             Let me know your thought on this.
>
>             Sorry I could do this much only out of my busy schedule.
>
>             Thanks,
>
>         YJH answer:  The DNI can be larger than the GHI frequently in the Arctic
>         locations because of persistently low sun angles.  However, the numbers that
>         you've highlighted above have DNI/GHI ratios that do seem excessive. All these
>         solar irradiances are calculated using several empirical and analytical models
>         and so could always be wrong. However, the formulation of the direct solar model
>         calculates the DNI as a sigmoid function of the ratio between the GHI and the
>         extraterrestrial global horizontal radiation, so it would seem difficult to
>         produce a DNI that would violate physical reality, i.e., GHI = DNI*sin(solarZ) +
>         DHI. Time permitting, I may look more into this.
>
>         On 12/6/2017 2:01 PM, Nathan Brown wrote:
>
>             Ok, so here’s my revised list:
>
>             1. Hour index is 1, not zero (not different from .epw, but still annoying to
>             deal with while post processing)
>             2. Solar noon is not aligned to the noon timestamp. Does this mean permanent
>             DST?
>             3. This file contains data for 2/29
>
>             Nathan Brown, BEMP, LEED AP~ Associate
>
>             *LOISOS *+*UBBELOHDE *
>
>             - - - - - - - - - - - - - - - - - - - - - - - - - - -
>
>             www.coolshadow.com <http://www.coolshadow.com/>
>
>         YJH answer:  1 is not a correct answer since, as you note, the convention is the
>         same for both *.BIN  and *.BINM, as well as *.epw files.  The annoyance you feel
>         msy be due to the mixed use of cardinal and ordinal numbers in the weather
>         files.  The standard convention on simulation weather files is the formal, i.e.,
>         Hour 1, Hour 2, etc., whereas the convention on weather station reports is the
>         latter, Hour 00:00, Hour 01:00, etc.  In my opinion there is an inconsistency on
>         simulation weather files where most of the measurements (temperatures, etc.) are
>         reported by the timestamp, i.e., 00:00, but incorporated as Hour 1, etc., while
>         others,  notably solar and rainfall, are both measured and reported cardinally
>         as Hour 1, etc. I'll talk more about this in the next contest on the epw file
>         format.
>
>         How are you deducing that solar noon is not aligned to the noon timestamp? As
>         for DST,  I feel that weather files should NEVER incorporate any such human-made
>         artifacts.  There are several factors you should consider when comparing solar
>         noon to local standard noon: (1) difference in longitude between the standard
>         meridian and the location (Barrow); in this case, they are 150.00 West and
>         156.782 West respectively, or a 27 minute effect,  (2) the solar irradiance is
>         given over the past hour, so the average solar position for Hour 12 is at 11:30
>         AM local time rather than 12:00 PM, another 30 minute effect, and (3)  "Equation
>         of time" that makes local time faster or slower than solar time by +- 15 minutes
>         at the most. I don't know if these effects combined accounts for the difference
>         between solar and local noon that you see.
>
>     ------------------------------------------------------------------------------------------
>
>
>
>     NOTICE: This communication and any attachments ("this message") may contain
>     information which is privileged, confidential, proprietary or otherwise subject to
>     restricted disclosure under applicable law. This message is for the sole use of the
>     intended recipient(s). Any unauthorized use, disclosure, viewing, copying,
>     alteration, dissemination or distribution of, or reliance on, this message is
>     strictly prohibited. If you have received this message in error, or you are not an
>     authorized or intended recipient, please notify the sender immediately by replying
>     to this message, delete this message and all copies from your e-mail system and
>     destroy any printed copies. You are receiving this communication because you are
>     listed as a current WSP contact. Should you have any questions regarding WSP's
>     electronic communications policy, please consult our Anti-Spam Commitment at
>     www.wsp.com/casl <http://www.wsp.com/casl>. For any concern or if you believe you
>     should not be receiving this message, please forward this message to
>     caslcompliance at wsp.com <mailto:caslcompliance at wsp.com> so that we can promptly
>     address your request. Note that not all messages sent by WSP qualify as commercial
>     electronic messages.
>
>     AVIS : Ce message, incluant tout fichier l'accompagnant (« le message »), peut
>     contenir des renseignements ou de l'information privilégiés, confidentiels,
>     propriétaires ou à divulgation restreinte en vertu de la loi. Ce message est destiné
>     à l'usage exclusif du/des destinataire(s) voulu(s). Toute utilisation non permise,
>     divulgation, lecture, reproduction, modification, diffusion ou distribution est
>     interdite. Si vous avez reçu ce message par erreur, ou que vous n'êtes pas un
>     destinataire autorisé ou voulu, veuillez en aviser l'expéditeur immédiatement et
>     détruire le message et toute copie électronique ou imprimée. Vous recevez cette
>     communication car vous faites partie des contacts de WSP. Si vous avez des questions
>     concernant la politique de communications électroniques de WSP, veuillez consulter
>     notre Engagement anti-pourriel au www.wsp.com/lcap <http://www.wsp.com/lcap>. Pour
>     toute question ou si vous croyez que vous ne devriez pas recevoir ce message, prière
>     de le transférer au conformitelcap at wsp.com <mailto:conformitelcap at wsp.com> afin que
>     nous puissions rapidement traiter votre demande. Notez que ce ne sont pas tous les
>     messages transmis par WSP qui constituent des messages electroniques commerciaux.
>
>
>
>     -LAEmHhHzdJzBlTWfa4Hgs7pbKl
>

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20171208/d2674c7c/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 25844 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20171208/d2674c7c/attachment-0020.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 73807 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20171208/d2674c7c/attachment-0021.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 8656 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20171208/d2674c7c/attachment-0022.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 7978 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20171208/d2674c7c/attachment-0023.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.png
Type: image/png
Size: 130605 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20171208/d2674c7c/attachment-0024.png>
-------------- next part --------------
      PROGRAM FMTWTH
C      
C     THIS PROGRAM READS A FORMATTED WEATHER FILE (WEATHER.FMT)
C     AND A FORMATTED INPUT FILE (FMTWTH.INP) AND WRITES A
C     PACKED BINARY DOE2 WEATHER FILE (WEATHER.BIN)
C
      DIMENSION CLN(12),GT(12),MDAYS(12),IDAT(1536),IWDID(5)
C     
      DATA MDAYS / 31,28,31,30,31,30,31,31,30,31,30,31 /
C      
      OPEN(UNIT=12,FILE='FMTWTH.INP')
      OPEN(UNIT=11,FILE='WEATHER.FMT')
      OPEN(UNIT=10,FILE='WEATHER.BIN',FORM='UNFORMATTED')
C              
C     IWSZ           WORD SIZE          1 = 60-BIT, 2 = 30-BIT
C     IFTYP          FILE TYPE          1 = OLD, 2 = NORMAL (NO SOLAR),
C                                       3 = THE DATA HAS SOLAR
C     IWDID          LOCATION I.D.
C     IWYR           YEAR
C     WLAT           LATITUDE
C     WLONG          LONGITUDE
C     IWTZN          TIME ZONE NUMBER
C     IWSOL          SOLAR FLAG         FUNCTION OF IWSZ + IFTYP
C     CLN            CLEARNESS NO.
C     GT             GROUND TEMP.       (DEG R)
C     KMON           MONTH              (1-12)
C     KDAY           DAY OF MONTH
C     KH             HOUR OF DAY
C     WBT            WET BULB TEMP      (DEG F)
C     DBT            DRY BULB TEMP      (DEG F)
C     PATM           PRESSURE           (INCHES OF HG)
C     CLDAMT         CLOUD AMOUNT       (0 - 10)
C     ISNOW          SNOW FLAG          (1 = SNOWFALL)
C     IRAIN          RAIN FLAG          (1 = RAINFALL)
C     IWNDDR         WIND DIRECTION     (0 - 15; 0=N, 1=NNE, ETC)
C     HUMRAT         HUMIDITY RATIO     (LB H2O/LB AIR)
C     DENSTY         DENSITY OF AIR     (LB/CU FT)
C     ENTHAL         SPECIFIC ENTHALPY  (BTU/LB)
C     SOLRAD         TOTAL HOR. SOLAR   (BTU/HR-SQFT)
C     DIRSOL         DIR. NORMAL SOLAR  (BTU/HR-SQFT)
C     ICLDTY         CLOUD TYPE         (0 - 2)
C     WNDSPD         WIND SPEED         KNOTS
C
      REWIND 12
      READ (12,9001) IWSZ,IFTYP
 9001 FORMAT(12X,I1,17X,I1)     
      REWIND 11
      READ (11,9002) (IWDID(I),I=1,5),IWYR,WLAT,WLONG,IWTZN,IWSOL
 9002 FORMAT(5A4,I5,2F8.2,2I5)     
      IWSOL = IWSZ + (IFTYP-1)*2 - 1
      READ (11,9003) (CLN(I),I=1,12)
      READ (11,9004) (GT(I),I=1,12)
 9003 FORMAT(12F6.2)      
 9004 FORMAT(12F6.1)
      DO 1000 IM=1,12
      IDE = MDAYS(IM)
      DO 1000 ID=1,IDE
      IRECXO = IM*2 + (ID-1)/16 - 1
      IDXO = MOD(ID-1,16) + 1
      DO 500 IH=1,24
      READ (11,9005) KMON, KDAY, KH, WBT, DBT, PATM, CLDAMT, ISNOW, 
     1               IRAIN, IWNDDR, HUMRAT, DENSTY, ENTHAL, SOLRAD,
     2               DIRSOL, ICLDTY, WNDSPD
 9005 FORMAT(3I2,2F5.0,F6.1,F5.0,2I3,I4,F7.4,F6.3,F6.1,2F7.1,I3,F5.0)      
      ISOL = INT(SOLRAD + .5)
      IDN = INT(DIRSOL + .5)
      IWET = INT(WBT+99.5)
      IDRY = INT(DBT+99.5)
      IPRES = INT(PATM*10.-149.5)
      ICLDAM = INT(CLDAMT)
      IWNDSP = INT(WNDSPD+0.5)
      IHUMRT = INT(HUMRAT*10000.+0.5)
      IDENS = INT(DENSTY*1000.-19.5)
      IENTH = INT(ENTHAL*2.0+60.5)
      IP1 = (IDXO-1)*96 + IH*4 - 3
      IDAT(IP1) = IPRES*65536 + IWET*256 + IDRY
      IDAT(IP1+1) = ISOL*1048576 + IDN*1024 + 
     1              ICLDAM*64 + ISNOW*32 + IRAIN*16 + IWNDDR 
      IDAT(IP1+2) = IHUMRT*128 + IDENS
      IDAT(IP1+3) = IENTH*2048 + ICLDTY*128 + IWNDSP
  500 CONTINUE      
      IF ((ID .NE. 16) .AND. (ID .NE. IDE))  GO TO 1000
      WRITE (10) IWDID,IWYR,WLAT,WLONG,IWTZN,IRECXO,IDE,CLN(IM),
     1           GT(IM),IWSOL,IDAT 
 1000 CONTINUE     
      END
      
-------------- next part --------------
      PROGRAM FMTWTH
C      
C     THIS PROGRAM READS A FORMATTED WEATHER FILE (WEATHER.FMT)
C     AND A FORMATTED INPUT FILE (FMTWTH.INP) AND WRITES A
C     PACKED BINARY DOE2 WEATHER FILE (WEATHER.BIN)
C
      DIMENSION CLN(12),GT(12),MDAYS(12),IDAT(1536),IDAT2(384),IWDID(5)
C     
      DATA MDAYS / 31,28,31,30,31,30,31,31,30,31,30,31 /
C      
      OPEN(UNIT=12,FILE='FMTWTH.INP')
      OPEN(UNIT=11,FILE='WEATHER.FMTM')
      OPEN(UNIT=10,FILE='WEATHER.BINM',FORM='UNFORMATTED')
      OPEN(UNIT=13,FILE='WEATHER.DBG')
C              
C     IWSZ           WORD SIZE          1 = 60-BIT, 2 = 30-BIT
C     IFTYP          FILE TYPE          1 = OLD, 2 = NORMAL (NO SOLAR),
C                                       3 = THE DATA HAS SOLAR
C     IWDID          LOCATION I.D.
C     IWYR           YEAR
C     WLAT           LATITUDE
C     WLONG          LONGITUDE
C     IWTZN          TIME ZONE NUMBER
C     IWSOL          SOLAR FLAG         FUNCTION OF IWSZ + IFTYP
C     CLN            CLEARNESS NO.
C     GT             GROUND TEMP.       (DEG R)
C     KMON           MONTH              (1-12)
C     KDAY           DAY OF MONTH
C     KH             HOUR OF DAY
C     WBT            WET BULB TEMP      (DEG F)
C     DBT            DRY BULB TEMP      (DEG F)
C     PATM           PRESSURE           (INCHES OF HG)
C     CLDAMT         CLOUD AMOUNT       (0 - 10)
C     ISNOW          SNOW FLAG          (1 = SNOWFALL)
C     IRAIN          RAIN FLAG          (1 = RAINFALL)
C     IWNDDR         WIND DIRECTION     (0 - 15; 0=N, 1=NNE, ETC)
C     HUMRAT         HUMIDITY RATIO     (LB H2O/LB AIR)
C     DENSTY         DENSITY OF AIR     (LB/CU FT)
C     ENTHAL         SPECIFIC ENTHALPY  (BTU/LB)
C     SOLRAD         TOTAL HOR. SOLAR   (BTU/HR-SQFT)
C     DIRSOL         DIR. NORMAL SOLAR  (BTU/HR-SQFT)
C     ICLDTY         CLOUD TYPE         (0 - 2)
C     WNDSPD         WIND SPEED         KNOTS
C
      REWIND 12
      READ (12,9001) IWSZ,IFTYP
 9001 FORMAT(12X,I1,17X,I1)     
      REWIND 11
      READ (11,9002) (IWDID(I),I=1,5),IWYR,WLAT,WLONG,IWTZN,IWSOL
 9002 FORMAT(5A4,I5,2F8.2,2I5)     
      IWSOL = IWSZ + (IFTYP-1)*2 - 1
      READ (11,9003) (CLN(I),I=1,12)
      READ (11,9004) (GT(I),I=1,12)
 9003 FORMAT(12F6.2)      
 9004 FORMAT(12F6.1)
      DO 1000 IM=1,12
      IDE = MDAYS(IM)
      DO 1000 ID=1,IDE
      IRECXO = IM*2 + (ID-1)/16 - 1
      IDXO = MOD(ID-1,16) + 1
      DO 500 IH=1,24
      READ (11,9005) KMON, KDAY, KH, WBT, DBT, PATM, CLDAMT, ISNOW, 
     1               IRAIN, IWNDDR, HUMRAT, DENSTY, ENTHAL, SOLRAD,
     2               DIRSOL, ICLDTY, WNDSPD
 9005 FORMAT(3I2,2F5.1,F6.1,F5.0,2I3,I4,F7.4,F6.3,F6.1,2F7.1,I3,F5.0)      
      ISOL = INT(SOLRAD + .5)
      IDN = INT(DIRSOL + .5)
      IWET = INT(WBT+99.5)
      IDRY = INT(DBT+99.5)
      IPRES = INT(PATM*10.-149.5)
      ICLDAM = INT(CLDAMT)
      IWNDSP = INT(WNDSPD+0.5)
      IHUMRT = INT(HUMRAT*10000.+0.5)
      IDENS = INT(DENSTY*1000.-19.5)
      IENTH = INT(ENTHAL*2.0+60.5)
      IP1 = (IDXO-1)*96 + IH*4 - 3
      IDAT(IP1) = IPRES*65536 + IWET*256 + IDRY
      IDAT(IP1+1) = ISOL*1048576 + IDN*1024 + 
     1              ICLDAM*64 + ISNOW*32 + IRAIN*16 + IWNDDR 
      IDAT(IP1+2) = IHUMRT*128 + IDENS
      IDAT(IP1+3) = IENTH*2048 + ICLDTY*128 + IWNDSP
      IWETMOD = (WBT-IWET+99)*10
      IF (IWETMOD.LT.0) IWETMOD=10+IWETMOD
      IDRYMOD = (DBT-IDRY+99)*10
      IF (IDRYMOD.LT.0) IDRYMOD=10+IDRYMOD
      ISOLMOD = (SOLRAD - ISOL)*10
      IF (ISOLMOD.LT.0) ISOLMOD=10+ISOLMOD
      IDNMOD = (DIRSOL - IDN)*10
      IF (IDNMOD.LT.0) IDNMOD=10+IDNMOD
      IP2 = (IDXO-1)*24 + IH  
      IDAT2(IP2) = IDNMOD*1000 + ISOLMOD*100 + IDRYMOD*10 + IWETMOD
      WRITE(13,550) IDAT2(IP2),IDNMOD,ISOLMOD,IDRYMOD,IWETMOD
  550 FORMAT('IDAT2=',I10,' IDNMOD=',I3,' ISOLMOD=',I3,
     #        ' IDRYMOD=',I5,' IWETMOD=',I5)
  500 CONTINUE      
      IF ((ID .NE. 16) .AND. (ID .NE. IDE))  GO TO 1000
      WRITE (10) IWDID,IWYR,WLAT,WLONG,IWTZN,IRECXO,IDE,CLN(IM),
     1           GT(IM),IWSOL,IDAT,IDAT2 
 1000 CONTINUE     
      END
      
-------------- next part --------------
      
C
C     THIS PROGRAM READS A PACKED BINARY DOE-2 WEATHER FILE AND
C     CREATES A FORMATTED WEATHER FILE AS OUTPUT.  THE INPUT
C     FILE IS TAPE10, THE OUTPUT FILE IS TAPE11.
C
C     ADDED ADDITIONAL FIELD IDAT31 to increase precision of data
C     TO ONE SIGNIFICANT PLACE - YJHUANG AUG 2008
C
      DIMENSION CLN(12),GT(12),MDAYS(12),IDAT30(1536),IDAT31(384),
     _          IWDID(5),IWTH(14),IWTH2(4)
      DIMENSION XMASK(16,2), CALC(16)
      INTEGER IDUM
C
      DATA MDAYS / 31,29,31,30,31,30,31,31,30,31,30,31 /
      DATA IWDID /5*4H    /
      DATA XMASK / -99., -99., 15., 0., 0., 0., 0., 0., .02, -30., 0.,
     1             .0, .0, .0, .0, 10., 
     2              1., 1., .1, 1., 1., 1., 1., .0001, .001, .5,
     3             1., 1., 1., 1., 0., 0. /
C
      OPEN (UNIT=11,FILE='WEATHER.FMTM')
      OPEN (UNIT=10,FILE='WEATHER.BINM',FORM='UNFORMATTED')
      REWIND 10
      DO 100 IM1=1,12
      READ (10) (IWDID(I),I=1,5),IWYR,WLAT,WLONG,IWTZN,LRECX,NUMDAY,
     _          CLN(IM1),GT(IM1),IWSOL
      READ (10) IDUM
  100 CONTINUE
      REWIND 10
      LRECX = 0
      WRITE (11,9001) (IWDID(I),I=1,5),IWYR,WLAT,WLONG,IWTZN,IWSOL
      WRITE (11,9002) (CLN(I),I=1,12)
      WRITE (11,9003) (GT(I),I=1,12)
 9001 FORMAT(5A4,I5,2F8.2,2I5)
 9002 FORMAT(12F6.2)
 9003 FORMAT(12F6.1)
      DO 1000 IM2=1,12
      IDE = MDAYS(IM2)
      DO 1000 ID=1,IDE
      DO 1000 IH=1,24
  105 IRECX = IM2*2 + (ID-1)/16 - 1
      IDX = MOD(ID-1,16) + 1
      IF (IRECX-LRECX) 200,400,300
  200 IDIF = LRECX - IRECX + 1
      DO 220 I=1,IDIF
      BACKSPACE 10
  220 CONTINUE
  300 READ (10) IWDID,IWYR,WLAT,WLONG,IWTZN,LRECX,NUMDAY,CLRNES,
     #          TGRND,IDUM,IDAT30,IDAT31
      GO TO 105
  400 CONTINUE
      IP1 = 96*(IDX-1) + 4*IH - 3
      IP2 = 24*(IDX-1) + IH 
C      WRITE (11,9008) IDX,IH,IP1,IP2
C 9008 format('IDX=',I3,' IH=',I3,' IP1=',I4,' IP2=',I3)
      IWTH(3) = IDAT30(IP1)/65536
      IWTH(1) = MOD(IDAT30(IP1),65536)/256
      IWTH(2) = MOD(IDAT30(IP1),256)
      IWTH(11) = IDAT30(IP1+1)/1048576
      IWTH(12) = MOD(IDAT30(IP1+1),1048576)/1024
      IWTH(4) = MOD(IDAT30(IP1+1),1024)/64
      IWTH(5) = MOD(IDAT30(IP1+1),64)/32
      IWTH(6) = MOD(IDAT30(IP1+1),32)/16
      IWTH(7) = MOD(IDAT30(IP1+1),16)
      IWTH(8) = IDAT30(IP1+2)/128
      IWTH(9) = MOD(IDAT30(IP1+2),128)
      IWTH(10) = IDAT30(IP1+3)/2048
      IWTH(13) = MOD(IDAT30(IP1+3),2048)/128
      IWTH(14) = MOD(IDAT30(IP1+3),128)
      IWTH2(1) = MOD(IDAT31(IP2),10)
      IWTH2(2) = MOD(IDAT31(IP2),100)/10
      IWTH2(3) = MOD(IDAT31(IP2),1000)/100
      IWTH2(4) = MOD(IDAT31(IP2),10000)/1000
      DO 450 I=1,4
      IF (IWTH2(I).GE.5) IWTH2(I)=IWTH2(I)-10
  450 CONTINUE
C      WRITE (11,9009) IDAT31(IP2),IWTH2(1),IWTH2(2),IWTH2(3),IWTH2(4)
C 9009 FORMAT('IDAT31=',I4,' WET=',I2,' DRY=',I2,' SOLD=',I2,' DIR=',I2)      
      DO 500 I=1,14
      CALC(I) = FLOAT(IWTH(I))*XMASK(I,2) + XMASK(I,1)
      IF (I.LE.2) CALC(I)=CALC(I)+IWTH2(I)/10.
      IF (I.EQ.11.OR.I.EQ.12) CALC(I)=CALC(I)+IWTH2(I-8)/10.
  500 CONTINUE    
      ISNOW = INT(CALC(5) + .01)
      IRAIN = INT(CALC(6) + .01)
      IWNDDR = INT(CALC(7) + .01)
      ICLDTY = INT(CALC(13) + .01)
C              
C              IM2            MOMTH              (1-12)
C              ID             DAY OF MONTH
C              IH             HOUR OF DAY
C              CALC(1)        WET BULB TEMP      (DEG F)
C              CALC(2)        DRY BULB TEMP      (DEG F)
C              CALC(3)        PRESSURE           (INCHES OF HG)
C              CALC(4)        CLOUD AMOUNT       (0 - 10)
C              ISNOW          SNOW FLAG          (1 = SNOWFALL)
C              IRAIN          RAIN FLAG          (1 = RAINFALL)
C              IWNDDR         WIND DIRECTION     (0 - 15; 0=N, 1=NNE, ETC)
C              CALC(8)        HUMIDITY RATIO     (LB H2O/LB AIR)
C              CALC(9)        DENSITY OF AIR     (LB/CU FT)
C              CALC(10)       SPECIFIC ENTHALPY  (BTU/LB)
C              CALC(11)       TOTAL HOR. SOLAR   (BTU/HR-SQFT)
C              CALC(12)       DIR. NORMAL SOLAR  (BTU/HR-SQFT)
C              ICLDTY         CLOUD TYPE         (0 - 2)
C              CALC(14)       WIND SPEED         KNOTS
C
  900 WRITE (11,9005) IM2, ID, IH, CALC(1), CALC(2), CALC(3), CALC(4),
     1                ISNOW, IRAIN,IWNDDR, CALC(8), CALC(9), CALC(10),
     2                CALC(11), CALC(12), ICLDTY, CALC(14)
 9005 FORMAT(3I2,2F5.1,F6.2,F5.0,2I3,I4,F7.4,F6.3,F6.1,2F7.1,I3,F5.0)
 1000 CONTINUE
      ENDFILE 11
      END
-------------- next part --------------
      
C
C     THIS PROGRAM READS A PACKED BINARY DOE-2 WEATHER FILE AND
C     CREATES A FORMATTED WEATHER FILE AS OUTPUT.  THE INPUT
C     FILE IS TAPE10, THE OUTPUT FILE IS TAPE11.
C
      DIMENSION CLN(12),GT(12),MDAYS(12),IDAT30(1536),
     _          IWDID(5),IWTH(14)
      DIMENSION XMASK(16,2), CALC(16)
      INTEGER IDUM
C
      DATA MDAYS / 31,28,31,30,31,30,31,31,30,31,30,31 /
      DATA IWDID /5*4H    /
      DATA XMASK / -99., -99., 15., 0., 0., 0., 0., 0., .02, -30., 0.,
     1             .0, .0, .0, .0, 10., 
     2              1., 1., .1, 1., 1., 1., 1., .0001, .001, .5,
     3             1., 1., 1., 1., 0., 0. /
C
      OPEN (UNIT=11,FILE='WEATHER.FMT')
      OPEN (UNIT=10,FILE='WEATHER.BIN',FORM='UNFORMATTED')
      REWIND 10
      DO 100 IM1=1,12
      READ (10) (IWDID(I),I=1,5),IWYR,WLAT,WLONG,IWTZN,LRECX,NUMDAY,
     _          CLN(IM1),GT(IM1),IWSOL
      READ (10) IDUM
  100 CONTINUE
      REWIND 10
      LRECX = 0
      WRITE (11,9001) (IWDID(I),I=1,5),IWYR,WLAT,WLONG,IWTZN,IWSOL
      WRITE (11,9002) (CLN(I),I=1,12)
      WRITE (11,9003) (GT(I),I=1,12)
 9001 FORMAT(5A4,I5,2F8.2,2I5)
 9002 FORMAT(12F6.2)
 9003 FORMAT(12F6.1)
      DO 1000 IM2=1,12
      IDE = MDAYS(IM2)
      DO 1000 ID=1,IDE
      DO 1000 IH=1,24
  105 IRECX = IM2*2 + (ID-1)/16 - 1
      IDX = MOD(ID-1,16) + 1
      IF (IRECX-LRECX) 200,400,300
  200 IDIF = LRECX - IRECX + 1
      DO 220 I=1,IDIF
      BACKSPACE 10
  220 CONTINUE
  300 READ (10) IWDID,IWYR,WLAT,WLONG,IWTZN,LRECX,NUMDAY,CLRNES,
     _          TGRND,IDUM,IDAT30
      GO TO 105
  400 CONTINUE
      IP1 = 96*(IDX-1) + 4*IH - 3
      IWTH(3) = IDAT30(IP1)/65536
      IWTH(1) = MOD(IDAT30(IP1),65536)/256
      IWTH(2) = MOD(IDAT30(IP1),256)
      IWTH(11) = IDAT30(IP1+1)/1048576
      IWTH(12) = MOD(IDAT30(IP1+1),1048576)/1024
      IWTH(4) = MOD(IDAT30(IP1+1),1024)/64
      IWTH(5) = MOD(IDAT30(IP1+1),64)/32
      IWTH(6) = MOD(IDAT30(IP1+1),32)/16
      IWTH(7) = MOD(IDAT30(IP1+1),16)
      IWTH(8) = IDAT30(IP1+2)/128
      IWTH(9) = MOD(IDAT30(IP1+2),128)
      IWTH(10) = IDAT30(IP1+3)/2048
      IWTH(13) = MOD(IDAT30(IP1+3),2048)/128
      IWTH(14) = MOD(IDAT30(IP1+3),128)
      DO 500 I=1,14
      CALC(I) = FLOAT(IWTH(I))*XMASK(I,2) + XMASK(I,1)
  500 CONTINUE    
      ISNOW = INT(CALC(5) + .01)
      IRAIN = INT(CALC(6) + .01)
      IWNDDR = INT(CALC(7) + .01)
      ICLDTY = INT(CALC(13) + .01)
C              
C              IM2            MOMTH              (1-12)
C              ID             DAY OF MONTH
C              IH             HOUR OF DAY
C              CALC(1)        WET BULB TEMP      (DEG F)
C              CALC(2)        DRY BULB TEMP      (DEG F)
C              CALC(3)        PRESSURE           (INCHES OF HG)
C              CALC(4)        CLOUD AMOUNT       (0 - 10)
C              ISNOW          SNOW FLAG          (1 = SNOWFALL)
C              IRAIN          RAIN FLAG          (1 = RAINFALL)
C              IWNDDR         WIND DIRECTION     (0 - 15; 0=N, 1=NNE, ETC)
C              CALC(8)        HUMIDITY RATIO     (LB H2O/LB AIR)
C              CALC(9)        DENSITY OF AIR     (LB/CU FT)
C              CALC(10)       SPECIFIC ENTHALPY  (BTU/LB)
C              CALC(11)       TOTAL HOR. SOLAR   (BTU/HR-SQFT)
C              CALC(12)       DIR. NORMAL SOLAR  (BTU/HR-SQFT)
C              ICLDTY         CLOUD TYPE         (0 - 2)
C              CALC(14)       WIND SPEED         KNOTS
C
  900 WRITE (11,9005) IM2, ID, IH, CALC(1), CALC(2), CALC(3), CALC(4),
     1                ISNOW, IRAIN,IWNDDR, CALC(8), CALC(9), CALC(10),
     2                CALC(11), CALC(12), ICLDTY, CALC(14)
 9005 FORMAT(3I2,2F5.0,F6.1,F5.0,2I3,I4,F7.4,F6.3,F6.1,2F7.1,I3,F5.0)
 1000 CONTINUE
      ENDFILE 11
      END


More information about the Equest-users mailing list