Agreed on all points.  Is 4 a typo?  I'd consider that a pretty darn comfortable building if not!

Adding some (unasked for) perspective:  Unmet hours do not always mean the model inputs/outputs are incorrect.   Real buildings are not always comfortable, and expectations/thresholds of comfort for occupants are not static/binary.  On the flip side of the coin:  a "correct" model (approaching calibrated reality in behavior) might attract my critical eye if it's reporting absolutely zero unmet hours in the baseline / proposed case.  Then again... I work a lot on buildings with comfort issues to resolve, so maybe that's just par for the course!

The airside summary reports are where I'd start to help isolate the exact zone(s) reporting this (tiny) number of unmet hours, spatially & by system.  The detailed reports can from there inform you what time of day those hours occur, and if need be you can dig into hourly custom reports to drill down whether the source is in system capacities (airflow, heating), system operations (see schedules, night cycling inputs, lockouts), unrealistic internal/envelope loads, or else due to the need for thermostat tweaks (setpoint/setback schedules, building warmup, whether a thermostat should be in the zones of concern to start with...).  I'd spitball 9 times out of 10 it's some combination of those issues for of unmet hours in relatively small quantities.

As an option, you can share a copy of your project with the list also and potentially gather some others' hands-on perspectives.  Include the INP + PD2, and indicate the climate/weather location as well if it isn't referenced from doe2.com.  Include the PRD if parametric runs feed into your concerns.

~Nick

[cid:image001.png at 01D2BF81.82049330]
Nick Caton, P.E., BEMP
  Senior Energy Engineer
  Regional Energy Engineering Manager
  Energy and Sustainability Services
  Schneider Electric

D  913.564.6361
M  785.410.3317
F  913.564.6380
E  nicholas.caton at schneider-electric.com<mailto:nicholas.caton at schneider-electric.com>

15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States

[cid:image002.png at 01D2BF81.82049330]



From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of David Eldridge via Equest-users
Sent: Thursday, April 27, 2017 5:27 PM
To: Tim Burke <tburke at tei-engineering.com>; equest-users at onebuilding.org
Subject: Re: [Equest-users] unmet heating load hours

Four hours doesn't seem unreasonable...you are referring to a requirement to not have more unmet hours in the proposed than the baseline?

My suggestion is to take a look and see when these hours are occurring to try and find a common theme -  what's the occupancy then, time of day where the spurious hours could be at start-up or later in the main shift, or during a lightly occupied time?

This might lead you to identify an equipment capacity constraint or else a tweak to the control scheme in use for the zone(s).

David



David S. Eldridge, Jr., P.E., LEED AP BD+C, BEMP, BEAP, HBDP
Grumman/Butkus Associates



From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Tim Burke via Equest-users
Sent: Thursday, April 27, 2017 4:50 PM
To: equest-users at onebuilding.org<mailto:equest-users at onebuilding.org>
Subject: [Equest-users] unmet heating load hours

I have a Costco warehouse equest model with 4 unmet heating load hours in my proposed model with zero in my baseline budget model.  I need to be able to tweak my model to get rid of these unmet load hours but minor tweaks don't seem to make a difference.  Could there be something wrong with the model that results in having a few unmet load hours that are hard to get rid of?

Tim Burke

T.E., Inc.
830 North Riverside Drive #200
Renton, WA. 98057
(425) 970-3753 Phone
(425) 970-3756 Fax
WWW.TEI-ENGINEERING.COM<http://www.tei-engineering.com/>
This message contains information that is confidential or privileged. The information is intended for the use of the individual or entity named above. If you are not the intended recipient, be aware that any disclosure, copying, distribution or use of the contents of this information is prohibited. If you have received this electronic transmission in error, please notify the sender and delete this message and any attachments


______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170427/dbb62eaa/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 255 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170427/dbb62eaa/attachment-0004.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 8477 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170427/dbb62eaa/attachment-0005.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: oledata.mso
Type: application/octet-stream
Size: 7129 bytes
Desc: oledata.mso
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170427/dbb62eaa/attachment-0002.obj>


More information about the Equest-users mailing list