I had always assumed temperature first but reading the PNNL 90.1-2010 Performance Rating Method Reference Manual, 3.121 (pdf page 151), it states “For systems 5 through 8, the air temperature for cooling shall be reset higher by 5°F under the minimum cooling load conditions using a reset by warmest zone, airflow first strategy.”
The manual states that the airflow first strategy minimizes zone reheat coil energy ( or overcooling) and central chiller energy consumption at the cost of possible increased fan energy.
Unfortunately, the reviewer may have a case.
[cid:image001.jpg at 01D2A6E9.840756F0]
Christopher R. Jones, P.Eng.
Technical Specialist
WSP Canada Inc.
2300 Yonge Street, Suite 2300
Toronto, ON M4P 1E4 Canada
T +1 416-644-0252
www.wspgroup.ca<http://www.wspgroup.ca/>
Please consider the environment before printing...
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Pasha Korber-Gonzalez via Equest-users
Sent: Thursday, April 20, 2017 3:59 AM
To: eQUEST Users List <equest-users at lists.onebuilding.org>
Subject: [Equest-users] Supply Air Temp Reset Interpretation Please...?
Hello--- I received this note from a fellow energy model reviewer (non-LEED review comment) regarding my Baseline energy model that is supposed to be compliant with Appendix G. I disagree with what they are saying. I appreciate your feedback please and verification if in fact I am wrong in how I am interpreting Section G3.1.3.12.
"We believe TEMP-FIRST supply air reset control strategy is not the correct interpretation of G3.1.3.12 – rather, AIRFLOW-FIRST should be used."
Thanks!
Pasha
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170420/d4324d4f/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1848 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170420/d4324d4f/attachment-0002.jpg>
More information about the Equest-users
mailing list