Aru,
I may be reading the question wrong but the proposed case system does NOT dictate baseline case ERV requirements. If the autosized baseline case systems meet the characteristics outlined in 90.1-2007(?) Section G3.1.2.10, then an ERV must be included on that system unless one of the exceptions apply.
Anthony Hardman, PE, BEAP, LEED AP BD+C
Senior Building Performance Analyst
The Green Engineer, Inc.
(978) 610-2801
From: Darryl Kasun via Equest-users [mailto:equest-users at lists.onebuilding.org]
Sent: Monday, November 28, 2016 10:12 PM
To: Arunabha Sau
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] ER Wheel in Baseline
Hi Aru,
Yes you are correct - you have to create an exhaust air heat recovery with at least 50% effectiveness in your baseline bldg. Check out section 6.5.6.1 of ASHRAE 90.1 for further guidance.
Darryl Kasun, P. Eng,
Interior Engineering
On Mon, Nov 28, 2016 at 6:58 PM, Arunabha Sau via Equest-users <equest-users at lists.onebuilding.org> wrote:
Hello there,
In a 5A climate zone, I am working with a Proposed model with a RTU (30,000 CFM, 100% OA) with exhaust air ER wheel in it. I am kinda sure that I've to create a ER wheel for the 90.1 Baseline (as per G3.1.2.10). Just want to make sure if I am correct?
Help please. Thanks
Best,
Aru Sau
Architectural Sustainability | Energy Analyst
analyzing the ROI of your sustainable initiatives...
c: 678-467-7934, Ann Arbor, MI
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20161129/80f02bfd/attachment-0001.htm>
More information about the Equest-users
mailing list