Rehana,
Estimating the energy consumption of a pool heater can be very tricky. The dominant mode of heat loss is generally evaporation. Some major influences include activity level of people using the pool (splashing/stirring increases evaporation), wind speeds, and the use of a pool cover. The US DOE has some material on the subject: http://energy.gov/energysaver/gas-swimming-pool-heaters There is a table on this page which I have used to back calculate and extrapolate heating requirements for a specific project as a sanity check.
Also, ASHRAE HVAC Applications 2015 addresses pool heat loss starting on page 5.6. The discussion is helpful and provides sound calculation methods, but they are more easily applied to indoor pools than outdoor pools.
That’s all I have at the moment; hopefully you can find some additional resources.
Good luck,
Christian
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Sunayana Jain
Sent: Monday, March 28, 2016 8:23 AM
To: Rehana Jiffrey; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Outdoor swimming pool and heater
Rehana,
You can model pool heater load on electric meter (see image below) with winter months schedule:
Thanks,
Sunayana Jain CEM, LEED AP BD+C
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Rehana Jiffrey
Sent: Saturday, March 26, 2016 11:21 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Outdoor swimming pool and heater
Dear All,
I'm trying to model an outdoor swimming pool located at the roof top of a residential building. Pool heater (45Kw) operates from December to March (4 months).
I was wondering if anyone could help me how to model this scenario, and where to input these consumption values.
FYI, this is my first time modeling an outdoor pool and pool heater.
Thank you,
Rehana.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160328/7eae48ac/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 27726 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160328/7eae48ac/attachment-0002.jpeg>
More information about the Equest-users
mailing list