[Equest-users] Boiler Fuel Type / Hot Water Pipe Properties

David Berty via Equest-users equest-users at lists.onebuilding.org
Tue Jun 7 07:03:18 PDT 2016


I don't personally know the answer to your question on the fuel source coal
vs. natural gas.

Regarding the 2nd question on simulation of piping pressure and thermal
losses; these modelling software programs do not model these energy losses.
They don't "care" where your central utility plant is physically located in
relation to your load. They make the assumption that you have properly
sized pipelines, insulation etc. EQuest is only attempting to estimate the
fuel consumption of meeting the building's heating and cooling load, not
assess the pipe sizing and insulation condition.

David Berty, P.E.
Baseline Energy Consulting
317.220.9272
On Jun 7, 2016 9:18 AM, "Tuğçin Kırant" <equest-users at lists.onebuilding.org>
wrote:

> Hi everyone :)
>
> I am a new user and modelling a district heating system. Probably my
> questions are easy, but i couldnt solve the problems.
>
> 1- I define boiler but the fuel type must be coal. However, Equest doesnt
> let me get the results for coal. It simulates as natural gas. Even i create
> new fuel meter for coal and select it on boil properties. How can i get the
> results for coal? (Maybe it is related to pic1. But there is no other
> choice except Natural Gas )
>
>
>
>  2- As i mentioned before, this is a district heating system and there
> are 6 residential villas. Combined Heat Power Plant supplies the hot
> water and it is located very far away. I wanna see the effect of pipe
> lenght, dimension and insulataion material of the hot water pipes. So,  how
> can i enter the pipes and their properties?
>
>
> Sincerely.
>
> H. Tuğçin KIRANT
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160607/1178d06a/attachment-0005.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: pic1.png
Type: image/png
Size: 98330 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160607/1178d06a/attachment-0005.png>


More information about the Equest-users mailing list