[Equest-users] How do you think about the no electricity Eco-Coolers from Bangladesh
冷面寒枪 via Equest-users
equest-users at lists.onebuilding.org
Thu Jul 14 19:22:16 PDT 2016
Recently,I read the news about the zero air cooler,which is made with re-purposed plastic bottles.And the new claims that it helps reduce indoor temperature by 5 degrees centigrade.
The making process is shown as following:
I dout that very much.
the Joule-Thomson Coefficient for air (mostly nitrogen) at 300K (27°C/80°F) is about 0.36K/bar. This means that at 300K a 1bar change in pressure equates to a 0.22K. The change in pressure required to get the 5°C (5K) reduction would therefore be:
5 / 0.22 = 22.7bar
So I think it is impossible the temperature drop will be up to 5 degrees centigrade after the air through the bottle.
What do you think?
------------------
Yongqing Zhao
Changsha Green Building & Energy Saving Technology CO.,LTD
NO.438,Shaoshan Road,Changsha,Hunan,China
Telephone:13574805636
Email:zhaoyongqing1987 at 126.com
503271081 at qq.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160715/c55412d4/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 106626 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160715/c55412d4/attachment-0003.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 109500 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160715/c55412d4/attachment-0004.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 157349 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160715/c55412d4/attachment-0005.jpeg>
More information about the Equest-users
mailing list