[Equest-users] WSHP System with PS-H Report Circulation Loop Overload
Lapierre, Patrick
plapierre at bpa.ca
Mon Jan 25 04:45:36 PST 2016
I pretty sure I read somewhere in one of DOE's manual that the overload is the part of load that goes over capacity.
In your report, you see the heating capacity of the loop is 575 kBtu/h which is roughly equal to the net heating peak load of your loop. When the heat load exceeds that capacity, it goes in overload and must be treated the following hour.
If you look at hourlies, you'll see that it matches.
[cid:image002.jpg at 01D15744.23696F40]
Patrick Lapierre_ing.
plapierre at bpa.ca
De : Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] De la part de Kathryn Kerns
Envoyé : 22 janvier 2016 15:10
À : equest-users at lists.onebuilding.org
Objet : [Equest-users] WSHP System with PS-H Report Circulation Loop Overload
Everyone, I made an energy model of a building being served by water source heat pumps attached to a typical water loop with a fluid cooler and a boiler. I let eQuest size all the equipment including the boiler and water source heat pumps. The PS-H Water Loop report showed the following:
[cid:image003.png at 01D15744.23696F40]
Notice that in January, the peak heating load is -991.9 kbtu/hr, the peak net load is -576.1 kbtu/hr, and the peak over load is -355.6 kbtu/hr. eQuest sized the water loop boiler to be -576.1 kbtu/hr. I believe these numbers are correct and the boiler size is correct but I cannot find an explanation in a document telling me how net load and over load is calculated and what they mean. I can explain how eQuest develops the heat load, but not the other two loads. I know a typical hot water coil system has heat load peaks equal to net load peaks and the over loads are usually zero. I am pretty sure the over load value is related to the heat pump COP, but I would like to be able to point to a written piece of documentation explaining this. Anybody know where to look?
Thanks.
P.S. the energy model ran successfully with less than 10 heating hours out of throttling range.
Kathryn Kerns
Systems Specialist
BCE Engineers, Inc.
| Ph: 253.922.0446 | Fx: 253.922.0896 |
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160125/1f8b3a6e/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 1728 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160125/1f8b3a6e/attachment-0002.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 36163 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160125/1f8b3a6e/attachment-0002.png>
More information about the Equest-users
mailing list