[Equest-users] DOAS+DCV+ERV problems - no dummy zone heat recovery
Javed Iqbal
eee.javed at gmail.com
Thu Feb 4 20:06:08 PST 2016
There was a very nice post by Mr. James Hess on DOAS Modeling procedure in
eQuest posted on 2nd March 2013. It was explained very well in spite of its
own complexity. You can find the same in Quest archives.
Regards,
On Thu, Feb 4, 2016 at 9:43 PM, Bishop, Bill <bbishop at pathfinder-ea.com>
wrote:
> As far as I know (AFAIK), no one has posted to equest-users to describe a
> way to accurately model heat recovery using an OA-FROM-SYSTEM DOAS assigned
> to a dummy zone. The main problem being that the OA-FROM-SYSTEM uses the
> dummy zone temperature as the return air temperature to the ERV.
> In the case of this particular model, I think a more reasonable workaround
> would be to model energy recovery at each of the VAV units instead of
> modeling a dedicated DOAS. Model each VAV system with SELF-CONTAINED
> ERV-FANS and distribute the DOAS fan power amongst the VAV systems.
>
> Regards,
> ~Bill
>
> William Bishop, PE, BEMP, BEAP, CEM, LEED AP | Pathfinder Engineers &
> Architects LLP
> Senior Energy Engineer
> 134 South Fitzhugh Street Rochester, NY 14608
> T: (585) 698-1956 F: (585) 325-6005
> bbishop at pathfinder-ea.com www.pathfinder-ea.com
> Carbon Fee and Dividend - simple, effective, and market-based.
>
> -----Original Message-----
> From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On
> Behalf Of jacob goodman
> Sent: Thursday, February 04, 2016 10:32 AM
> To: Jones, Christopher <Christopher.r.Jones at wspgroup.com>;
> equest-users at lists.onebuilding.org
> Subject: Re: [Equest-users] DOAS+DCV+ERV problems
>
> Chris,
> Thanks mucho!!! Switching from "Fixed Setpoint" to "Mixed Air Reset"
> seems to have totally cleared up the problem. The model now shows
> reasonable savings without any unmet hours. I have had many models run with
> no problem using the Fixed Setpoint controls, but not this one. I agree
> that Float almost always causes issues.
> Thank you so much, you truly saved my day, Jacob
>
>
> On 2/4/2016 8:13 AM, Jones, Christopher wrote:
> > Quoting Brian Fountain's response of January 28:
> >
> > "The default settings for heat recovery control is'float' which always
> maximizes heat recovery, even if it reduces free cooling. Changing this to
> 'mixed air reset' will help.
> >
> > Also, on the 2nd heat recovery tab, the default is 1" of static added to
> the supply fan (on top of whatever you have on the fan tab) to account for
> the added fan power to push the air through the heat recovery device. "
> >
> > I changed your model to 'mixed air reset' and the cooling energy dropped
> significantly.
> >
> > Christopher Jones, P.Eng.
> > Senior Engineer
> >
> > WSP Canada Inc.
> > 2300 Yonge Street, Suite 2300
> > Toronto, ON M4P 1E4
> > T +1 416-644-4226
> > F +1 416-487-9766
> > C +1 416-697-0056
> >
> > www.wspgroup.com
> >
> > -----Original Message-----
> > From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org]
> > On Behalf Of jacob goodman
> > Sent: Thursday, February 04, 2016 9:50 AM
> > To: equest-users at lists.onebuilding.org
> > Subject: [Equest-users] DOAS+DCV+ERV problems
> >
> > Dear Community,
> > I am working on a model of a 33 story building served by separate VAV
> system for core and perimeter zones. Core zones with VAV terminal units and
> perimeter with fan powered boxes. All areas are served by DOAS via the
> dummy zone/"OA from system" work around. I have added DCV return sensor to
> the non-DOAS systems only. These systems showed appropriate savings from
> this before I added the DOAS and seem ok after as well. The problem comes
> when I add the ERV to the two DOAS systems. I am using ERV settings and
> controls that are well tested and have worked in similar models. That is
> Enthalpy wheel, 56% Sen.&Lat. effectiveness, OA Exhaust DT at 5deg, fixed
> set point controls and 0.5inH2O pressure drop with premium fans.
> >
> > The issues is that as soon as I activate on the ERV the heating energy
> drops by ~90% and cooling/pumps/fans triple or more. This creates 4,000+
> unmet hours and overall building energy use is up 40%.
> >
> > It seems like a massive heat load is being added to the system because
> of the ERV, but I cant see why or how. I checked fan kW sizing and that
> does not go up. Neither does supply air flow.
> >
> > I would work on debugging this for as long as needed, but the deadline
> looms! Attached is the model for reference. Simply turn "Recover Exhaust?"
> to No to see the difference.
> > Jacob
> >
> > ________________________________
> >
> >
> > You are receiving this communication because you are listed as a current
> WSP contact. Should you have any questions regarding WSP’s electronic
> communications policy, please consult our Anti-Spam Commitment
> www.wspgroup.com/casl. For any concern or if you believe you should not
> be receiving this message, please forward this message to us at
> caslcompliance at wspgroup.com<mailto:caslcompliance at wspgroup.com> so that
> we can promptly address your request. This message is intended only for the
> use of the individual or entity to which it is addressed, and may contain
> information which is privileged, confidential, proprietary or exempt from
> disclosure under applicable law. If you are not the intended recipient or
> the person responsible for delivering the message to the intended
> recipient, you are strictly prohibited from disclosing, distributing,
> copying or in any way using this message. If you have received this
> communication in error, please notify the sender, and destroy and delete
> any copies you may have received.
> >
> > WSP provides professional land surveying services through the
> > following entities: WSP Surveys (AB) Limited Partnership and WSP
> > Surveys (BC) Limited Partnership
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
--
Javed Iqbal, LEED AP, CEA
Sr. Energy Analyst
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160205/75be4b10/attachment-0005.htm>
More information about the Equest-users
mailing list