[Equest-users] Load Reports
Saif A via Equest-users
equest-users at lists.onebuilding.org
Tue Aug 16 09:05:12 PDT 2016
what I am looking at in the PS-C report is the peak load which
is 2852.1 KBTU/HR, while the chiller size in the PV-A report is 5.09
MBTU/HR for some reason eQUEST is over sizing the chiller capacity by two
times. Also it does not allow me to input the chiller capacity manually in
the detailed mode.
Thank you,
Saif
On Tue, Aug 16, 2016 at 6:43 AM, Sharad Kumar via Equest-users <
equest-users at lists.onebuilding.org> wrote:
> Hi Saif,
>
>
> I will like to mention that PS-C is equipment load reports and PV-A is
> chiller plant design parameters based cooling capacity. So if there is some
> relation then there can be some connections in hours to be multiplied with
> the equipment loads to get the cooling capacity of the plant loads as the
> units are in MBtu and MBtuh.
>
>
> But the real PV-A report analyses is like it is the auto-sized parameter
> based and with the input of flow and the temperature difference of cooling
> plant configuration based cooling capacity, the cooling capacity is
> determined. The formula can be 500 X GPM X delta T. GPM is the cooling
> plant water flow and delta T is loop design temperature difference. The
> default temperature difference is 10 °F.
>
>
> I don't have any sort-ful idea of PS-C analyses.It can be TR of the
> chillers.
>
>
> *Thanks,*
> Sharad.
>
>
> ---------- Forwarded message ----------
> From: Saif A via Equest-users <equest-users at lists.onebuilding.org>
> To: equest-users at lists.onebuilding.org
> Cc:
> Date: Mon, 15 Aug 2016 10:56:20 -0500
> Subject: [Equest-users] Load Reports
> Good morning guys,
>
> After I ran the simulation for the building I am working on I found the
> chiller size and plant loads does not match in reports PS-C and PV-A the
> difference is almost double is that normal? Also when I try to input the
> chiller capacity in detailed mode the results in the reports does not
> change is there a way to fix this?
>
> Thank you,
>
> Saif
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160816/c976393b/attachment-0002.htm>
More information about the Equest-users
mailing list