[Equest-users] order of magnitude low for results
PKConsulting via Equest-users
equest-users at lists.onebuilding.org
Wed Aug 3 15:48:43 PDT 2016
Thanks John & Nick, I appreciate the feedback. Yes the climate is fairly moderate and temperate in characteristics, but I had really expected to see a more significant EUI for the baseline model. Maybe I was expecting too much!
Your general feedback and time gives me more confidence that I'm not as far off as I initially thought.
Thanks! I hope I can return the favor sometime!
Pasha
Ph: 308-763-1593
> On Aug 3, 2016, at 3:55 PM, <Nicholas.Caton at schneider-electric.com> <Nicholas.Caton at schneider-electric.com> wrote:
>
> A few observations:
> · Don’t equate GLASS-CONDUCTANCE with assembly U-value (see the associated help entry) à fixing this will bump up your solar conductive gains a bit
> · Site EUI is ~40 – not bonkers low… see next point.
> · I was not familiar with the climate in Tel Aviv, so worth a check. Visualizing drybulb from the provided weather file demonstrates really decent annual temperatures – you don’t ever stray very far from 70-75. In fact through the dead of summer 75 looks like the 24 hour average between day and night temps:
> <image005.jpg>
> · This weather data also looks to be in general agreement with some cursory googling, so not terribly suspect:
> <image006.png>
> Give yourself some moderate internal loads (lighting/plug load densities look in line with 90.1-2007), and this should probably be a cooling-dominated building on an annual basis, with heating/cooling enduses not playing a dominant role.
>
> All of that is reflected in the present outputs:
> <image008.jpg>
>
> I performed a few other cursory spot-checks, and I didn’t find anything seriously awry in terms of baseline hydronic efficiencies or related calculations (you’ll want to revisit tower and pumping power inputs before finishing, but they’re in the right ballpark now).
>
> You might find a helpful swing in fan energies after doing your Pfan calcs, but be sure to document / seek out any fan static pressure credits you can claim (I observe fans are user-defaulted to 4” static at present).
>
> From there you might find it beneficial to dig deeper into not missing any process loads (i.e. elevator banks & garage ventilation are probably in play for this case).
>
> Altogether, this doesn’t look like a climate conducive to relatively bad baseline EUI’s (if that makes sense)!
>
> ~Nick
>
> <image003.png>
> Nick Caton, P.E.
> Senior Energy Engineer
> Energy and Sustainability Services
> Schneider Electric
> D 913.564.6361
> M 785.410.3317
> E nicholas.caton at schneider-electric.com
> F 913.564.6380
> 15200 Santa Fe Trail Drive
> Suite 204
> Lenexa, KS 66219
> United States
> <image004.png>
>
>
> From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of John Aulbach via Equest-users
> Sent: Wednesday, August 03, 2016 3:53 PM
> To: Pasha Korber-Gonzalez; eQUEST Users List
> Subject: Re: [Equest-users] order of magnitude low for results
>
> And you are only cooling to 76 DegF, and not on weekends.
>
> Again, try these to help you.
>
> JOhn
>
>
> On Wednesday, August 3, 2016 1:26 PM, Pasha Korber-Gonzalez via Equest-users <equest-users at lists.onebuilding.org> wrote:
>
>
> Hi eQuesters...
>
> I'm now running the latest 3.65 version and I have a new model (baseline) that is showing results that seem very low in order of magnitude. My baseline file is producing 11 kWh/ft2.
>
> All throttling range hours are in check for the time being. I'd like if someone could give my model a 'second pair of eyes' and see if there is something that I've input, or haven't input that is causing this low order of magnitude on results.
>
> This is an office building, quite large, and approximately 80% glass.
>
> I've attached the files and the weather file. If anyone has a bit of time to take a look.
>
> My phone number is 308-763-1593 if it is easier to give me a call if you'd like.
>
> I appreciate any comments or time anyone can offer.
>
> Thanks!
> Pasha
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>
> ______________________________________________________________________
> This email has been scanned by the Symantec Email Security.cloud service.
> ______________________________________________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160803/906aca94/attachment-0002.htm>
More information about the Equest-users
mailing list