Michael,
First, you're under 300 hours so indeed it's a minor problem.
I've only looked at your model very briefly but:
- HW loop operation is set to "SNAP" at OA of 60°F. This is causing some
minor underheating in shoulder season.
- You have local exhaust fan with makeup = infiltration. Basically
equest ignores this added infiltration during the sizing, so you have to
trick it to take it into account by having a different schedule for sizing
(heating AND cooling design days). I've put together my findings on the
subject on Unmet Hours here
<https://unmethours.com/question/3102/how-do-you-model-exhaust-fans-in-equest/>
in some kind of tutorial that I hope is helpful.
Do the above and your unmet hours disappear.
Additionally:
- Throttle range of 0.3°R seems pretty aggressive to me.
- when you use baseboards and want to oversize, use the system's sizing
ratio
Hope this helps,
Julien
--
Julien Marrec, EBCP, BPI MFBA
Energy&Sustainability Engineer
T: +33 6 95 14 42 13
LinkedIn (en) : www.linkedin.com/in/julienmarrec
LinkedIn (fr) : www.linkedin.com/in/julienmarrec/fr
<http://www.linkedin.com/in/julienmarrec>
2015-10-15 16:30 GMT+02:00 Michael Campbell <mcamp1206 at gmail.com>:
> I mistakenly attached the PRD file instead of PD2. Correct files are
> attached.
>
> On Thu, Oct 15, 2015 at 10:16 AM, Michael Campbell <mcamp1206 at gmail.com>
> wrote:
>
>> Hello,
>>
>> I'm having what appears to be a minor issue with unmet hours in a model
>> that I've inherited. My INP and PD2 files are attached. I've tried
>> adjusting the cool sizing ratio and and adjusted infiltration rates and
>> equipment loads with no real effects. Anybody have any ideas?
>>
>> Thanks,
>> Mike Campbell
>>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20151015/4c24f68b/attachment-0002.htm>
More information about the Equest-users
mailing list