[Equest-users] Evaporative Media on Air-cooled Chiller
    Kevin McGaffigan 
    kmcgaffigan at dmiinc.com
       
    Fri May  1 13:23:08 PDT 2015
    
    
  
Kusum,
 
I just took a look at your PRD file and it looks like you changed the condenser type to remote evaporatively cooled without updating the chiller EIR or the fan/pump EIR associated with the remote condenser.  For an air-cooled chiller, the condenser fan power is built into the chiller EIR value but once you set the condenser type to remote, eQuest calculates the condenser fan and condenser pump energy separately based on the EIR you specify (default in this case).  You might try either removing the fan energy from the chiller EIR or zeroing out the condenser fan and pump EIR values.  
 
You could also look into changing the minimum condensing temperature.  The default is 80°F but you might be able to reduce that by a few degrees to increase savings.
 
Kevin
From: Kusum Sekhalia [mailto:skusum3 at gmail.com] 
Sent: Thursday, April 30, 2015 7:19 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Evaporative Media on Air-cooled Chiller
 
Hi all,
 
I am working on this project where I am proposing a measure to install evaporative media on the air-cooled chiller. When I am changing the condenser type in parametric runs from air-cooled to evaporative cooled, its giving me negative savings. Can anyone help me figure out what the issue is. I have attached the model.
 
Thanks!
 
Kusum
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150501/23b71668/attachment-0005.htm>
    
    
More information about the Equest-users
mailing list