[Equest-users] Using an Equip-Control as a Parametric Run

Jones, Christopher Christopher.r.Jones at wspgroup.com
Sun Jun 28 16:59:00 PDT 2015


John,
You can use an EQUIP-CTRL and LOAD-MANAGEMENT schedule of type SCHEDULED.  It’s fairly straight forward in eQuest.


[cid:image003.png at 01D09C46.E75BA0D0]
Christopher Jones, P.Eng.
Senior Engineer

WSP Canada Inc.
2300 Yonge Street, Suite 2300
Toronto, ON M4P 1E4
T +1 416-644-4226
F +1 416-487-9766
C +1 416-697-0065

www.wspgroup.com<http://www.wspgroup.com/>

From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of John Aulbach
Sent: Sunday, June 28, 2015 11:21 AM
To: Equest-users
Subject: [Equest-users] Using an Equip-Control as a Parametric Run

To the Royal order of eQuesters (and other such people):

I am trying to show savings from basically setting back a perimeter double duct system after hours. I believe I have it figures that I actually need to reset the Heat-Set-T, as a single fan DD system seems to only react to that set-point. I must then figure out how to shut off ther boiler on a nightly basis.

This of course would use the Equipment-Control and Load-Management. But what parameters within would be my change elements? The Flags? Has anyone ever set this up?

Thanks.

John R. Aulbach, PE
________________________________

You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSP’s electronic communications policy, please consult our Anti-Spam Commitment www.wspgroup.com/casl. For any concern or if you believe you should not be receiving this message, please forward this message to us at caslcompliance at wspgroup.com<mailto:caslcompliance at wspgroup.com> so that we can promptly address your request. This message is intended only for the use of the individual or entity to which it is addressed, and may contain information which is privileged, confidential, proprietary or exempt from disclosure under applicable law. If you are not the intended recipient or the person responsible for delivering the message to the intended recipient, you are strictly prohibited from disclosing, distributing, copying or in any way using this message. If you have received this communication in error, please notify the sender, and destroy and delete any copies you may have received.

WSP provides professional land surveying services through the following entities: WSP Surveys (AB) Limited Partnership and WSP Surveys (BC) Limited Partnership
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150628/e0872f26/attachment-0005.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 6574 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150628/e0872f26/attachment-0005.png>


More information about the Equest-users mailing list