[Equest-users] Chiller sequencing

Nicholas Caton ncaton at catonenergy.com
Fri Aug 21 11:37:56 PDT 2015


Of particular interest, I think your exact situation is covered nicely by:



Volume 3: Topics > Central Plant Components > LOAD-MANAGEMENT and
EQUIP-CTRL > Examples of EQUIP-CTRL and LOAD-MANAGEMENT Sequences > Example
1:  Chiller Staging



That said, after you’ve reviewed the literature, you might first set up
some hourly reporting (assigned load for each chiller) before messing with
EQUIP-CTRL settings at all.  If you have two identical chillers, I am 99%
certain they will behave exactly as you’ve described.  That is, chiller A
will handle the first 400 tons of load, then for hours with 401 tons and
upwards the two chillers will share the load 50/50.  The only nuance to add
is that, again assuming they are identical, the chiller that is engaged
first will be determined by the which occurs first in the .inp.



Best regards,



~Nick





*NICK CATON, P.E.*
*Owner*



*Caton Energy Consulting*
  306 N Ferrel

  Olathe, KS  66061

  office:  785.410.3317

www.catonenergy.com



*From:* Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] *On
Behalf Of *Jones, Christopher
*Sent:* Friday, August 21, 2015 7:49 AM
*To:* 'Sambhav Tiwari'; equest-users
*Subject:* Re: [Equest-users] Chiller sequencing



Sambhav,

I suggest reviewing the DOE22 Manuals.  DOE33Vol3-Topics contains a
detailed section on load management and equipment sequencing.



The manuals can be downloaded at http://doe2.com/download/doe-22/



Download the latest versions of the pdf files.





[image: cid:image003.png at 01D09C46.E75BA0D0]

*Christopher Jones,* P.Eng.
Senior Engineer



*WSP Canada Inc.*

2300 Yonge Street, Suite 2300

Toronto, ON M4P 1E4
T +1 416-644-4226

F +1 416-487-9766

C +1 416-697-0065



www.wspgroup.com



*From:* Equest-users [mailto:equest-users-bounces at lists.onebuilding.org
<equest-users-bounces at lists.onebuilding.org>] *On Behalf Of *Sambhav Tiwari
*Sent:* Friday, August 21, 2015 6:12 AM
*To:* equest-users
*Subject:* [Equest-users] Chiller sequencing



Dear Equesters,





I have a building with 800TR load and 2 chillers of 400TR each . In actual
design the chiller sequencing is in such way that



for 0 to 400TR chiller 1 will operate



for load between 400TR to 800TR  both chillers will run under 50% of total
building load ie the building load is say 500TR so chillers wil operate
like 250TR for each 1&2. not like 400TR for chiller 1 and 100TR for chiller
2.



How can i do such sequencing in equipment control.



I shall wait for your valuable response.



Regards

Sambhav Tiwari
------------------------------


You are receiving this communication because you are listed as a current
WSP contact. Should you have any questions regarding WSP’s electronic
communications policy, please consult our Anti-Spam Commitment
www.wspgroup.com/casl. For any concern or if you believe you should not be
receiving this message, please forward this message to us at
caslcompliance at wspgroup.com so that we can promptly address your request.
This message is intended only for the use of the individual or entity to
which it is addressed, and may contain information which is privileged,
confidential, proprietary or exempt from disclosure under applicable law.
If you are not the intended recipient or the person responsible for
delivering the message to the intended recipient, you are strictly
prohibited from disclosing, distributing, copying or in any way using this
message. If you have received this communication in error, please notify
the sender, and destroy and delete any copies you may have received.

WSP provides professional land surveying services through the following
entities: WSP Surveys (AB) Limited Partnership and WSP Surveys (BC) Limited
Partnership
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150821/a8e1ca5d/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 6574 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150821/a8e1ca5d/attachment-0002.png>


More information about the Equest-users mailing list