Also – do you have an airside economizer? If so – you might be running in economizer mode which will show up on your fans, but not space cooling.
Vikram Sami
BEMP, LEED BD+C
Associate Partner
ZGF ARCHITECTS LLP
T 206.521.3509 E vikram.sami at zgf.com
925 Fourth Avenue, Suite 2400
Seattle, WA 98104
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Nick Caton
Sent: Thursday, November 14, 2013 9:20 AM
To: František Bartoš; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] eQuest - Electricity consumption for cooling in winter
Hi Frantisek,
A few shotgun thoughts:
·         Does that space have unmet hours (see airside tab summary report after a simulation)?
·         Does the corresponding zone have a cooling thermostat schedule?  Not defining one means the zone won’t call for cooling.
·         Is the zone defined as “conditioned” and not “unconditioned” or “plenum?”
·         Are the other spaces sucking all the internal heat gains out through the partitions?
·         Is there exterior exposure (envelope) incident on the space doing the same?
This all assumes you’ve actually defined your computer server room as a distinct zone… If you only defined a percentage activity allocation for the server area within a larger zone (in wizards), your model likely isn’t detailed enough to capture a simultaneous call for heating and cooling between the different zones/systems.
If none of this helps, you might consider uploading your files to the mailing list to allow others to take a look.  I suggest doing a File --> Save As… into a new directory, then attaching the few files resulting.  Also be mindful to specify which version of eQuest you’re using.
Best of luck!
~Nick
[cid:489575314 at 22072009-0ABB]
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of František Bartoš
Sent: Thursday, November 14, 2013 10:19 AM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] eQuest - Electricity consumption for cooling in winter
Hello,
I have a question about eQuest modeling - I created a model of quite simple rectangle Office building, but in results I have no consumption of electricity for cooling during winter (november - march) although in area specification I have 6 % of floor area specified as a Computer server room (data centre) with 100 % plug load in occupied and unoccupied times.
The building is in Prague (Czech republic) and from my experiences based on real dates from existing building there´s always consumption of cooling energy for data server rooms in winter in this location.
Do you know,  where the problem can? What parameter could I insert wrongly?
Thanks for advices.
Frantisek
--
František Bartoš
Energetika a certifikace budov
Enerfis s.r.o.
Tel.: +420 222 766 952
Fax: +420 222 766 959
Mob: +420 607 965 265
E-mail: bartos at enerfis.cz<mailto:bartos at enerfis.cz>
________________________________
The contents of this email and any attachments to it contain confidential and/or legally privileged information from Zimmer Gunsul Frasca Architects LLP or its affiliates. If you are not the intended recipient, or an employee or agent responsible for delivering this message to the intended recipient, be aware that any disclosure, copying, distribution, or use of the information contained herein is strictly prohibited. If you received this transmission in error, please contact the sender and destroy the material in its entirety, whether in electronic or hard copy format.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20131114/0697c15f/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20131114/0697c15f/attachment.jpg>
    
    
More information about the Equest-users
mailing list