[Equest-users] system type workaround dilemma
R B
slv3sat at gmail.com
Fri May 4 08:45:00 PDT 2012
Use PIU - in detailed mode change the cooling source to DX. Set the
terminal units to parallel or series, or standard vav. Zone heat source to
electric, the ahu heat source to furnace. Seems straightforward unless I am
missing something in the question.
-Rohini
.On Fri, May 4, 2012 at 10:28 AM, Ramana Koti <ramana.koti at gmail.com> wrote:
> Dear All,
>
> I'm starting to build a LEED energy model. Its a small university
> classroom building around 5000 sf. The proposed mechanical design is as
> follows:
>
> Packaged VAV RTU with DX cooling and natural gas heating. Twelve PIU
> terminals with electric heating coils.
>
> For the proposed design model, I'm unable to select a system type or think
> of an equivalent/workaround in eQUEST. Any ideas on how best to go about it
> or if it is doable in eQUEST at all?
>
> Thanks,
> Ramana Koti.
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120504/491213e3/attachment.htm>
More information about the Equest-users
mailing list