<div><br>Use PIU - in detailed mode change the cooling source to DX. Set the terminal units to parallel or series, or standard vav. Zone heat source to electric, the ahu heat source to furnace. Seems straightforward unless I am missing something in the question.</div>
<div>-Rohini</div><div> </div><div class="gmail_quote">.On Fri, May 4, 2012 at 10:28 AM, Ramana Koti <span dir="ltr"><<a href="mailto:ramana.koti@gmail.com" target="_blank">ramana.koti@gmail.com</a>></span> wrote:<br>
</div><blockquote style="margin:0px 0px 0px 0.8ex;padding-left:1ex;border-left-color:rgb(204,204,204);border-left-width:1px;border-left-style:solid" class="gmail_quote"><div>Dear All,</div><div> </div><div>I'm starting to build a LEED energy model. Its a small university classroom building around 5000 sf. The proposed mechanical design is as follows: </div>
<div> </div><div>Packaged VAV RTU with DX cooling and natural gas heating. Twelve PIU terminals with electric heating coils. </div>
<div> </div><div>For the proposed design model, I'm unable to select a system type or think of an equivalent/workaround in eQUEST. Any ideas on how best to go about it or if it is doable in eQUEST at all?</div><div> </div>

<div>Thanks,</div><div>Ramana Koti.</div>
<br>_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote><br>