[Equest-users] Fwd: Fw: Mandatory Provisions 5.4
Bobby Sy
rsg4999 at gmail.com
Tue Feb 7 18:22:31 PST 2012
Hi Ty / Nick / eQuest users,
I also have a question about the mandatory provisions with international
projects (Climate-1), a tropical country where heating is not applicable
and wall insulation is not typically being used. Though insulation helps
improve the energy savings a little bit, it's always been a problem for the
owners to agree because of the additional cost for a very minimal effect
(usually <1%).
With the envelope mandatory provisions, using the Performance Rating Method
is it necessary to follow the required insulations / U-values in Table
5.5-1 or does LEED accept some kind of explanation or Local Code stating
that insulation or SC / U-value is really not regulated to show envelope
mandatory compliance?
Does anyone have the same experience for international project?
- Bob
On Tue, Feb 7, 2012 at 11:21 PM, Nick Caton <ncaton at smithboucher.com> wrote:
> Hi Ty,****
>
> ** **
>
> Here’s a paraphrase:****
>
> ** **
>
> “Where you are required to have insulation, you must install it per
> section 5.8.1.1-9.”****
>
> ** **
>
> Turning that around:****
>
> ** **
>
> “Where you are not required to have insulation, 5.8.1.1-9 does not come
> into play.”****
>
> ** **
>
> I don’t believe this is a “follow either A or B” statement – more like “if
> A, then B.”****
>
> ** **
>
> ~Nick**
>
> * *
>
> [image: cid:489575314 at 22072009-0ABB]**
>
> *NICK CATON, P.E.***
>
> SENIOR ENGINEER****
>
> ** **
>
> Smith & Boucher Engineers****
>
> 25501 west valley parkway, suite 200****
>
> olathe, ks 66061****
>
> direct 913.344.0036****
>
> fax 913.345.0617****
>
> www.smithboucher.com* *****
>
> ** **
>
> *From:* equest-users-bounces at lists.onebuilding.org [mailto:
> equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Ty Law
> *Sent:* Tuesday, February 07, 2012 2:28 AM
> *To:* equest-users at lists.onebuilding.org
> *Subject:* [Equest-users] Fwd: Fw: Mandatory Provisions 5.4****
>
> ** **
>
> Hi Everyone,****
>
> ****
>
> I am quite confused between what the ASHRAE 90.1 and the user’s manual
> tell us about Building Envelope Mandatory Provisions:****
>
> ****
>
> *5.4 Mandatory Provisions*****
>
> *“5.4.1 Insulation.** Where insulation is required in Section*****
>
> *5.5 or 5.6, it shall comply with the requirements found in Sections*****
>
> *5.8.1.1 through 5.8.1.9.” - ASHRAE 90.1-2007*****
>
> * *****
>
> ****
>
> *Insulation (§ 5.8.1)*****
>
> *“**The first set of mandatory requirements*****
>
> *addresses the proper installation and*****
>
> *protection of insulation materials. Issues*****
>
> *that are covered include compression of*****
>
> *insulation, installing insulation on sloping*****
>
> *ceilings and around recessed equipment,*****
>
> *and protecting insulation from physical or*****
>
> *moisture damage.”- ASHRAE 90.1-2007-User’s Manual*****
>
> * *****
>
> ****
>
> Does this mean that we could use insulation that is not as efficient as
> indicated in Table 5.5-1 through 5.5-8 as long as it complies with Section
> 5.8.1.1 through 5.8.1.9?****
>
> ****
>
> Your thoughts are highly appreciated.****
>
> ** **
>
> ** **
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120208/92081856/attachment.htm>
More information about the Equest-users
mailing list