[Equest-users] Fwd: Fw: Mandatory Provisions 5.4
Nick Caton
ncaton at smithboucher.com
Tue Feb 7 07:21:36 PST 2012
Hi Ty,
Here's a paraphrase:
"Where you are required to have insulation, you must install it per section 5.8.1.1-9."
Turning that around:
"Where you are not required to have insulation, 5.8.1.1-9 does not come into play."
I don't believe this is a "follow either A or B" statement - more like "if A, then B."
~Nick
[cid:489575314 at 22072009-0ABB]
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Ty Law
Sent: Tuesday, February 07, 2012 2:28 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Fwd: Fw: Mandatory Provisions 5.4
Hi Everyone,
I am quite confused between what the ASHRAE 90.1 and the user's manual tell us about Building Envelope Mandatory Provisions:
5.4 Mandatory Provisions
"5.4.1 Insulation. Where insulation is required in Section
5.5 or 5.6, it shall comply with the requirements found in Sections
5.8.1.1 through 5.8.1.9." - ASHRAE 90.1-2007
Insulation (§ 5.8.1)
"The first set of mandatory requirements
addresses the proper installation and
protection of insulation materials. Issues
that are covered include compression of
insulation, installing insulation on sloping
ceilings and around recessed equipment,
and protecting insulation from physical or
moisture damage."- ASHRAE 90.1-2007-User's Manual
Does this mean that we could use insulation that is not as efficient as indicated in Table 5.5-1 through 5.5-8 as long as it complies with Section 5.8.1.1 through 5.8.1.9?
Your thoughts are highly appreciated.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120207/ee4d8c0c/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120207/ee4d8c0c/attachment.jpg>
More information about the Equest-users
mailing list