[Equest-users] Interior Space Temperature
Rob Hudson
rdh4176 at gmail.com
Wed Apr 18 13:02:07 PDT 2012
If you leave the thermostats in the space as undefined and the fan schedule
in the HVAC tab, the results should show that the HVAC never turns on, and
give you the results you are wishing to see.
Hope this helps,
Rob
On Wed, Apr 18, 2012 at 3:08 PM, <bfountain at greensim.com> wrote:
> If the fan schedule is off (and fan control isn't cycle at night) eQUEST
> doesn't really look at space temp.
>
> My inclination would be to create a psz system serving your space with
> very small cooling capacity (e.g. 1 BTU/hr -- 0 will cause it to autosize)
> an an 'always on' fan schedule. Fan volume would depend on whether you
> wanted to introduce OA.
> Brian Fountain
> bfountain at greensim.com
>
> -----Original Message-----
> From: Ekaterina Tzekova <ekaterina.tzekova at mail.utoronto.ca>
> Sender: equest-users-bounces at lists.onebuilding.orgDate: Wed, 18 Apr 2012
> 18:38:35
> To: equest-users at lists.onebuilding.org<equest-users at lists.onebuilding.org>
> Subject: [Equest-users] Interior Space Temperature
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
--
Rob Hudson
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20120418/a6af96e5/attachment.htm>
More information about the Equest-users
mailing list