If the fan schedule is off (and fan control isn't cycle at night) eQUEST doesn't really look at space temp.

My inclination would be to create a psz system serving your space with very small cooling capacity (e.g. 1 BTU/hr -- 0 will cause it to autosize) an an 'always on' fan schedule. Fan volume would depend on whether you wanted to introduce OA. 