[Equest-users] Multiple Heating Hot Water Loops
    Jeremy McClanathan 
    jmcclanathan at CDiengineers.com
       
    Thu Sep 15 09:14:43 PDT 2011
    
    
  
eQuest allows you to create secondary loops with different design temperatures.  Right click on project, create a new circulation loop of type Hot Water, choose secondary subtype, select the primary loop and specify your design temperatures.  It will use a 3-way valve to mix down the temperature you specify.  There may be a couple steps I'm forgetting, but this is the general direction I head in.
Jeremy
___________________________________________
Jeremy McClanathan, P.E., BEMP, HFDP, LEED(r) AP BD+C
[cid:image001.jpg at 01CC7382.B220AB90]
4200 194th St SW, Ste 200, Lynnwood, WA 98036
P 425-672-1071 | F 425-778-8769
P Please consider the environment before printing this email.
From: Eric Hethcoat [mailto:EHethcoat at lsapa.com]
Sent: Thursday, September 15, 2011 7:51 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Multiple Heating Hot Water Loops
How do you model multiple temperatures for various heating HW loops such as radiant slab (120/constant temp) vs. HW loop (160/based on OA reset) for any type system if they are all coming from the same boiler plant?
Do you provide a heat exchanger on the peripheral loop to account for the different temperature?
Eric Hethcoat, P.E.
Partner
Latimer, Sommers & Associates, P.A.
3639 SW Summerfield Dr., Suite A
Topeka, KS  66614
c.  913.481.3256
w.  785.233.3232
f.  785.233.0647
ehethcoat at lsapa.com<mailto:ehethcoat at lsapa.com>
This message and any attachments included here-in, are solely for the intended recipient and may contain confidential or privileged information.  If you are not the intended recipient, any review, disclosure, copying, use, forwarding, or distribution of the information included in this message and any attachments is prohibited.  If you have received this communication in error, please notify the sender by reply e-mail and immediately and permanently delete this message and any attachments.  Thank you.
This email message, including any attachments, is for the sole use of the intended recipient and may contain confidential, proprietary, and/or privileged information, as well as content subject to copyright and other intellectual laws.  If you are not the intended recipient, you may not disclose, use, copy, or distribute the email message or its attachments.  If you believe you have received this email message in error, please contact the sender by reply email, immediately delete this email and destroy copies.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110915/ba98c3f2/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1232 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110915/ba98c3f2/attachment.jpg>
    
    
More information about the Equest-users
mailing list