[Equest-users] Ground Water/chilled water loop error(s)
Dave Bastow
dbastow at mcclure-engineering.com
Tue Oct 18 14:39:03 PDT 2011
Travis,
If nothing else you can model it as a regular chiller with an open cooling
tower and just use KW/efficiency factors & curves for the various components
so that it equals what you would get from energy used by your well pumps or
what have you. Also, using temperatures that relate to your well water
temperatures for the chilled water temperatures. I did this once, modeling
an existing large office building that was cooled by well water, that varied
from 50 degrees F. in winter to 60 degrees F. in the late summer. Once I
got all the inputs and curves and all set up correctly then it modeled very
closely to what the actual energy use had been from all of our historical
recorded data.
David A. Bastow
McClure Engineering, Inc.
507 Main Avenue West
Post Office Box 1404
Twin Falls, Idaho 83303-1404
PH. (208) 734-9015
FAX (208) 734-9016
Cell (208) 308-1152
E-Mail: <mailto:dbastow at mcclure-engineering.com>
dbastow at mcclure-engineering.com
Web Site: <http://www.mcclure-engineering.com/>
www.mcclure-engineering.com
From: Travis Miller [mailto:tmiller at dcengineering.net]
Sent: Tuesday, October 18, 2011 9:28 AM
To: Dahlstrom, Aaron; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Ground Water/chilled water loop error(s)
Thanks Aaron I did that and now the error reads:
Description: C:\Users\tmiller\Desktop\Capture1.PNG
So I went and gave the chilled water loop the same process load, but that
did not fix the problem. Below is a screenshot on how the loops are tied
together. Ignore the heat pump loop that is for a different system in the
same building. Any other thoughts would be appreciated. Thanks
Description: C:\Users\tmiller\Desktop\Capture.PNG
From: Dahlstrom, Aaron [mailto:ADahlstrom at in-posse.com]
Sent: Monday, October 17, 2011 5:18 PM
To: Travis Miller; equest-users at lists.onebuilding.org
Subject: RE: Ground Water/chilled water loop error(s)
Travis sometimes this error can be addressed by putting a nominal process
load on the offending loop say 0.000001 Mbtu/hr, with a minimal schedule.
There may be a more comprehensive or elegant solution, but this might just
get you going.
AD
Aaron Dahlstrom , PE, LEED® AP
In Posse A subsidiary of AKF| 1500 Walnut Street, Suite 1414,
Philadelphia, PA 19102
d: 215-282-6753| m: 267-507-5470| In Posse: 215-282-6800| AKF: 215-735-7290
e: ADahlstrom at in-posse.com | in posse web: www.in-posse.com
<http://www.in-posse.com/> | akf web: www.akfgroup.com
<http://www.akfgroup.com/>
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Travis
Miller
Sent: Monday, October 17, 2011 5:45 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Ground Water/chilled water loop error(s)
Hello all:
I have a system that is using well water direct to the cooling coils (no
heat exchanger to protect the cooling coils) at multiple air handlers in the
building. I set it up with the condenser water loop tied to a ground water
heat exchanger. This condenser loop then is tied to another heat exchanger
on the chilled water loop to the coils. This approach has given me an error
on the condenser water loop that it has no design flow. I have been playing
with the primary/secondary loop designations, even putting some made up flow
values into the loops/pumps etc. but have had no luck. Any ideas?
I would like to eliminate heat exchangers all together and just model the
50° well water directly into the chilled water loop any advice on how to
do this? I already changed the effectiveness of the heat exchanger to 1.0.
Thanks
Travis Miller, PE
DC Engineering
123 W. Spruce St.
Missoula, MT 59802
P: (406)829-8828x209
F: (406)829-8829
This e-mail may contain information that is confidential, privileged or
otherwise protected from disclosure. If you are not an intended recipient of
this e-mail, do not duplicate or redistribute it by any means. Please delete
it and any attachments and notify the sender that you have received it in
error. Unintended recipients are prohibited from taking action on the basis
of information in this e-mail. E-mail messages may contain computer viruses
or other defects, may not be accurately replicated on other systems, or may
be intercepted, deleted or interfered without the knowledge of the sender or
the intended recipient. If you are not comfortable with the risks associated
with e-mail messages, you may decide not to use e-mail to communicate with
In Posse.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111018/5fe024a9/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 26778 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111018/5fe024a9/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 20500 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111018/5fe024a9/attachment-0001.png>
More information about the Equest-users
mailing list