[Equest-users] infiltration levels

Rob Hudson rdh4176 at gmail.com
Wed May 4 11:44:26 PDT 2011


I would not input the ACH at 50 Pa into eQuest, as your infiltration will be
incredibly huge (made mistake myself in the past).  The wizard has a good
approximation for "average" buildings programed into it, and i recall it was
around 0.038 cfm/sqft of exterior wall area.  We like to use exterior wall
area rather than total ACH rate.  This usually works out to around 0.005 to
0.04 cfm/sqft of floor area, depending on the space and its exposure.

Hope this helps a little.  there are lots of documents online that can help
further explain "normal" values to use in the model, which can then be
translated into eQuest inputs later.

Rob

On Wed, May 4, 2011 at 1:27 PM, Shalini Modi <shalinimodi at msn.com> wrote:

>  Dear all,
>
> I would really appreciate some insight on infiltration with respect to
> eQUEST.
>
> The air change rate of the building at a pressure difference of 50 Pa
> indicates the level of air tightness. eQUEST allows entering the number of
> infiltration caused air changes per hour at a reference speed of 4.47 m/s.
> In that case, do we just enter the ach at 50 Pa in eQUEST, then how does the
> wind factor effect? Am kind of confused.
>
> Also, I would highly appreciate if anyone could share what are the ballpark
> infiltration levels in commercial (small) buildings in US and Canada.
>
> Thanks,
>
> Shalini
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>


-- 
Rob Hudson
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110504/352fd1c2/attachment.htm>


More information about the Equest-users mailing list