I would not input the ACH at 50 Pa into eQuest, as your infiltration will be incredibly huge (made mistake myself in the past). The wizard has a good approximation for "average" buildings programed into it, and i recall it was around 0.038 cfm/sqft of exterior wall area. We like to use exterior wall area rather than total ACH rate. This usually works out to around 0.005 to 0.04 cfm/sqft of floor area, depending on the space and its exposure.<div>
<br></div><div>Hope this helps a little. there are lots of documents online that can help further explain "normal" values to use in the model, which can then be translated into eQuest inputs later.</div><div><br>
</div><div>Rob<br><br><div class="gmail_quote">On Wed, May 4, 2011 at 1:27 PM, Shalini Modi <span dir="ltr"><<a href="mailto:shalinimodi@msn.com">shalinimodi@msn.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex;">
<div>
<span style="font-size:12pt;line-height:115%">Dear all,<br><br>I would really appreciate some insight on infiltration with respect to eQUEST.<br><br>The
air change rate of the building at a pressure difference of 50 Pa indicates the
level of air tightness. </span><span style="font-size:12pt;line-height:115%">eQUEST
allows entering the number of infiltration caused air changes per hour at a
reference speed of 4.47 m/s. In that case, do we just enter the ach at 50 Pa in eQUEST, then how does the wind factor effect? Am kind of confused.<br><br>Also, I would highly appreciate if anyone could share what are the ballpark infiltration levels in commercial (small) buildings in US and Canada.<br>
<br>Thanks,<br><br>Shalini<br></span> </div>
<br>_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br><br clear="all"><br>-- <br>Rob Hudson<br>
</div>