Jeremy:
My space is subject to the requirements to model a cooling system in the
baseline.
This is where I am a bit confused. The office area has a specified cooling
and heating system (RTU) but the warehouse area only has a heating system -
15 unit heaters plus a ventilation system. The building is only one level
- so do I model just one cooling and heating system (system 5) or can I
model 2 systems? - one for the office and one for the warehouse?
If so how do I treat the fan energy from the unit heaters and the need to
model a boiler and hot water pumps, when no such system exists?
In a message dated 3/3/2011 4:13:10 P.M. Eastern Standard Time,
Jeremy.Poling at transwestern.net writes:
Richard,
First check against the definitions of “space” on page 13. If the rated
capacity of the heating units for the space is between 3.4 Btuh/SF and the
value in Table 3.1 for your climate zone, then your warehouse space is
considered a semi-heated space and is not subject to the requirement to model
a cooling system in the baseline.
For the question on number of systems, what you’re looking is under
G3.1.1: “For systems 5, 6, 7, and 8, each floor shall be modeled with a separate
HVAC system.” That would mean a single system for the entire warehouse
portion of the building and the offices (unless you claim an exemption for the
offices due to G3.1.1.a, G3.1.1.b, G3.1.1.c, or G3.1.1.d). Then note any
requirements for system 5 from the latter portions of appendix G.
Jeremy R. Poling, PE, LEED AP+BDC
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of RJTHEACMAN at aol.com
Sent: Thursday, March 03, 2011 11:48 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Fedx
I am modeling a 110,000 sf. Fedex sorting facility for LEED and the
building has a small office area that is heated and cooled by rooftop units and
the remainder of the warehouse is only heated.
In accordance with ASHRAE 90.1 2007 if no cooling system exists the
cooling system shall be identical to the system modeled in the baseline building
design.
That system is a system 5 packaged vav with reheat, which includes a hot
water boiler.
We have (15) gas-fired unit heaters that provide heat to the warehouse.
My question is do I set up my heating system with 15 hot water boilers,
the same heating capacity as the unit heaters?
For the fan energy, do I set my air quantity the same as my unit heaters?
How do I address the VAV portion of the system as well as the hot water
pumps?
I have my model setup with (2) separate HVAC systems (1) Packaged VAV with
Reheat and (2) Packaged rooftop DX units with a gas furnace.
Any help will be greatly appreciated.
Richard Dominick, P.E.
TEC Engineers, LLC.